We are trying to determine if there are any issues with using standard firestop sealants such as STI LCI-305 or Hilti CP606 to air seal the exterior of electrical outlets. Looks like the stuff will shrink but is it enough to compromise the air seal ? Can anyone suggest an alternative product or method for air sealing outlets in a min. 1-hr rated partition wall ? The Hilti 601 product is elastomeric but costs a fortune, there must be an alternative. Thanks !

Asked by Greg Xikes | Feb 16

Tags:

6 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Have you considered intumescent putty, such as STI's SSP? They even make a putty pad specifically for electrical boxes. Applied by hand, stays flexible. Rated for up to 3 hour fire walls.
http://www.stifirestop.com/product_information/product_selector/ssp_putt...

Answered by Robert Riversong - Feb 16 10

2.

We looked at the putty pads but felt they would not create a good seal at the front of the box and to the back of the drywall.

Answered by Greg Xikes - Feb 17 10

3.

I don't know if it will satisfy your fire code, but for air sealing outlets I've always used Lessco polypans (as part of the air-tight drywall system). Then sealant is required only where the cables penetrate the pan, which can be filled with fire-resistant mineral-fiber or cellulose insulation.
http://www.lessco-airtight.com/

Answered by Robert Riversong - Feb 17 10

4.

Nutek makes airtight switch boxes with a built in drywall gaskets...2 hour fire rating.

Answered by Garth Sproule - Feb 17 10

5.

On my own house I used the regular intumescent fire caulk and, after inspection, covered it with regular duct mastic to hold it in place long term, cheap except for the time and attention to detail required.

For my clients I just use the intumescent fire caulk and airtight drywall detailing.

Answered by Michael Chandler, GBA Advisor - Feb 17 10

6.

I used the Airfoil boxes in my exterior walls. http://www.airfoilinc.com/index.html They have been really easy to work with and seal. I've been using spray foam but I would think a fire rated sealant would also work in these if the boxes meet your code.

Answered by Donald Lintner - Feb 17 10

Post new answer

The content of this field is kept private and will not be shown publicly.
Discussion policy: The editorial staff at GreenBuildingAdvisor.com does review user submissions. Please be respectful of others. Inappropriate content will be removed.
  • Web page addresses and e-mail addresses turn into links automatically.
  • Allowed HTML tags: <a> <em> <strong> <cite> <code> <ul> <ol> <li> <dl> <dt> <dd> <blockquote>
  • Lines and paragraphs break automatically.

* required fields

Other Questions in Green building techniques

In Energy efficiency and durability | Asked by Hunter Dendy | Jul 30, 10
In Mechanicals | Asked by sheri | Jul 28, 10
In General questions | Asked by Susie Harrington | Jul 26, 10
In Green products and materials | Asked by Jesse Thompson | Jul 30, 10
In Green building techniques | Asked by Sandra Heiser | Jul 27, 10