Wall detail for vertical siding

I am building a 2-story cottage in NH. It is 2x6 framing on 24 inch centers. Covered with 1/2 sheathing grade plywood. Then covered with Tyvek (seams taped). I plan on covering this with 1 1/2 foam board, then using horizontal furring strips on 24 in centers fastened over the foam board into the wall studs.

I will then fasten 1x12 shiplap siding to the furring strips. This will also create an air space behind the siding to allow for moisture control. Any opinions on this detail would be much appreciated.

I have attached a copy of the detail that I downloaded from this site. I will be using the recommended detail to flash around all windows and doors. I think my main concern is the horizontal furring strips allowing for drainage past them. Thanks for your time.

vertical siding detail.pdf55.32 KB
Asked by Raymond Klinger
Posted Jan 8, 2013 9:56 PM ET
Edited Jan 9, 2013 7:12 AM ET

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
0 Helpful?

Not all that relevant, but I just did a similar wall in NH but with vertical furring and horizontal fake vinyl shake siding.. Used rough sawn reclaimed corners to make it look like a camp. A camp that I will never paint. Wish I had staggerd two layers of foam rather than just depending on 2in with taped seams... Don't know where you are in NH, but you might want to up your rvalue in foam to keep that sheathing warmer.

Answered by stephen edge
Posted Jan 9, 2013 4:42 AM ET
Edited Jan 9, 2013 4:49 AM ET.

2.
0 Helpful?

The building is off of exit 32 (Lincoln). About 10 mi. west of the exit. Yes, I have read about increasing the r value to 10 on the foam board to keep the wall from having condensation. Plus staggering the seams is a great idea. Thanks for the advice. What brand of vinyl shakes did you use? Are you satisfied with them?

Answered by Raymond Klinger
Posted Jan 9, 2013 6:55 AM ET

3.
0 Helpful?

Raymond,
Your question about horizontal furring strips has been discussed on GBA before. See these pages:

What’s the Best Approach for a Rainscreen?

Rainscreen behind cedar shingles

Rigid Insulation - Cedar Sidewall

Wood shingles nailed through 1-1/2" Styrofoam

I don't think it's necessary to notch the back side of your horizontal furring strips with saw kerfs. However, if you want the notches, you can buy notched battens at some roofing supply stores.

Answered by Martin Holladay, GBA Advisor
Posted Jan 9, 2013 7:09 AM ET
Edited Jan 9, 2013 7:10 AM ET.

4.
0 Helpful?

I went with foundry shingles only because they were cheap on craigslist. I like they way they look and they were easy to work with. My place is down in Sandwich. Trying to attach pic.. If you ever want to compare notes, let me know..

Answered by stephen edge
Posted Jan 9, 2013 9:51 AM ET

Other Questions in Green building techniques

Do screws through exterior insulation reduce the wall R-value?

In General questions | Asked by brad hardie | Mar 1, 15

Trombe wall (non-vented) with exterior moveable mode of insulation?

In GBA Pro help | Asked by Thomas Tricarico | Mar 1, 15

What is the correct climate zone?

In Building Code Questions | Asked by william dempsey | Mar 1, 15

Should engineered wood flooring be glued to a concrete slab?

In Green products and materials | Asked by Christina Griffin | Mar 2, 15

Biggest bang for your buck?

In Energy efficiency and durability | Asked by Justin Murphy | Mar 1, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!