Toilet vent pipe placement

Is there a way to vent the toilet pipe out through the wall and up instead of piercing the roof?

Asked by Matthew Michaud
Posted Sun, 02/24/2013 - 12:53

Tags:

7 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Not a direct answer to your question, I know, but have you considered using an air admittance valve instead of a traditional drain waste vent? That way, you need no building envelope penetrations at all.

Answered by Jacob Weel
Posted Sun, 02/24/2013 - 18:25

2.
Helpful? 0

and where does it fit in the system? FYI, i will not have an attack space.

Answered by Matthew Michaud
Posted Sun, 02/24/2013 - 18:28

3.
Helpful? 0

This can get you started on AAV's, but be aware that they are illegal in some areas. http://www.studor.net/ Check their legality with your local building department before you even look at AAV's. If they are illegal, see a local, reputable plumbing business who will know your codes for proper sewer venting.

Answered by John Klingel
Posted Mon, 02/25/2013 - 01:57

4.
Helpful? 0

You need a plumbing stack that vent out the top. Sewer gas need a way to vent. An AAV is not a vent. It is closed in 1 direction in the it doesnt let sewer gas in to the home but does allow air in the system to allow a fixture to drain.

A good use of an AAV would be for a sink in a kitchen island. You dont have a vent going up but you still need to let air in to facilitate drainage.

Answered by Robert Hronek
Posted Mon, 02/25/2013 - 13:05

5.
Helpful? 0

You need a plumbing stack that vent out the top. Sewer gas need a way to vent. An AAV is not a vent. It is closed in 1 direction in the it doesnt let sewer gas in to the home but does allow air in the system to allow a fixture to drain.

A good use of an AAV would be for a sink in a kitchen island. You dont have a vent going up but you still need to let air in to facilitate drainage.

Answered by Robert Hronek
Posted Mon, 02/25/2013 - 13:05

6.
Helpful? 0

Matthew, There may be some rare exceptions, but I've never heard of a building or plumbing code that allowed air admittance valves to be used when a conventional alternative was available. They have prescribed limited uses in islands and renovations. Certainly for new construction vents are required. What was your rational for trying to avoid plumbing vents?

Answered by Malcolm Taylor
Posted Mon, 02/25/2013 - 22:37
Edited Mon, 02/25/2013 - 23:19.

7.
Helpful? 1

Don't know what code you're under, but per the 2009 and 2012 IRC you do not have to go through the roof, you can go through a wall, see http://publicecodes.cyberregs.com/icod/irc/2012/icod_irc_2012_31_par015.htm

Answered by David Meiland
Posted Mon, 02/25/2013 - 23:02
Edited Mon, 02/25/2013 - 23:03.

Other Questions in Green building techniques

Double wythe CMU vs. Thermomass

In Green building techniques | Asked by leo kloop | Oct 22, 14

Window U-value comparison to wall R-value and window replacement

In General questions | Asked by Keith Miller | Oct 20, 14

Insulation in old home repair

In Energy efficiency and durability | Asked by Tom Ives | Oct 21, 14

Sealing meeting point of brick wall and asphalt driveway

In General questions | Asked by Jon Haque | Oct 22, 14

Spray foam over XPS on external wall

In Energy efficiency and durability | Asked by Jeff M | Oct 22, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!