Loose-pack versus dense-pack cellulose for a flat roof

Loose-pack cellulose has been recommended for the cockloft of our row house. The roof has a slight grade so that the cockloft height goes from about 1 foot to 2 feet (including the roof joists). We will have a vapor permeable air barrier below it. Is loose fill a better choice here than dense pack? If so, why?
Daniel

Asked by Daniel Herskowitz
Posted Wed, 12/11/2013 - 00:11
Edited Wed, 12/11/2013 - 07:59

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Daniel,
To read my recommendations for insulating this type of roof, see Insulating Low-Slope Residential Roofs.

Your attic isn't high enough for a vented approach, so you will need to create an unvented roof assembly.

Unvented roof assemblies require either rigid foam on top of the roof sheathing (an approach that requires you to install new roofing) or spray foam insulation on the underside of the roof sheathing. All of the necessary details for a successful unvented roof assembly are described in my article.

Don't forget to insulate your attic walls.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 12/11/2013 - 07:21

2.
Helpful? 0

Local climate affects the answer- where are you?

Answered by Dana Dorsett
Posted Wed, 12/11/2013 - 14:24

Other Questions in Green building techniques

In Mechanicals | Asked by Kent Jeffery | Apr 16, 14
In Mechanicals | Asked by Peter L | Apr 19, 14
In Energy efficiency and durability | Asked by maggie wilbur | Apr 19, 14
In Energy efficiency and durability | Asked by Erik Schmitt | Apr 19, 14
In General questions | Asked by Lisa MArtin | Apr 15, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!