Insulated headers

I am in the Chicago area (CZ 5) and we are using a modified version of IECC 2012. Our exterior wall is a masonry veneer wall and we are using 2x6 wall studs for framing, allowing R-21 insulation in the stud cavities. Structurally, the wall could be built with 2x4 studs but it was decided that going with 2x6 and R-21 would be more cost effective than using 2x4s with 2" of rigid on the outside.

Some of the headers in this wall only need a double Microllam (3-1/2"), and the rest of the space can be filled with 2" rigid insulation. Where is the best place to put this insulation? I've seen some details that show the rigid sandwiched between the two 1-3/4" Microllams. This would support both sides of the 2x6 wall above and prevent twisting. But I think the double Microllam has more structural integrity when the two are nailed together, then putting the rigid on one side or the other. SInce the floor joists only need 3-1/2" of bearing, I don't think twisting is a concern. So is it better to put the rigid on the interior side or exterior side of the wall. My inclination is to put the Microllams to the outside, to provide additional support at that side, since that is where the windows/doors in the opening have their nailing flange.

Does this make sense, or are there other considerations I should be factoring in?

Asked by David Wytmar
Posted Fri, 01/31/2014 - 11:10
Edited Mon, 02/03/2014 - 08:40

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

That's what I would do. You will also need a furring strip on the inside of the header, at the bottom, to fasten the drywall.

Answered by David Meiland
Posted Fri, 01/31/2014 - 11:14

2.
Helpful? 0

I'm just a DIYer but I did a few replacement headers recently. I put the foam board in the center and used RSS lag screws from both sides. The screws from both sides suck the headers together.

You'd have to show some video or science for me to believe that the two spaced headers would separate somehow. It's common to see 2x6s, 2x12s etc in older homes assembled this way with blocking. A nailer on both sides is helpful, yes?

I do think this is a question for your engineer however as you will be changing the depth of the bearing end of the truss or joist if you place the foam to the interior. (ie the trusses/joists will bear on 3.5" instead of 5.25").

There is a discussion here that might help:
http://forums.jlconline.com/forums/showthread.php?15564-Headers-2X6-walls

Answered by Keith H
Posted Mon, 02/03/2014 - 02:57

Other Questions in Green building techniques

In Green building techniques | Asked by Eric Stear | Jul 31, 14
In General questions | Asked by mark mahon | Aug 1, 14
In Energy efficiency and durability | Asked by Brett Sichello | Jul 31, 14
In Interior design | Asked by Adam Lawrence | Aug 1, 14
In General questions | Asked by Chuck Jensen | Aug 1, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!