Can TrueFoam Foundation Plus Type 2 rigid foam be used as a vapor barrier?

I am finishing the exterior basement walls in my new home. My plan is adhere rigid to the foundation walls, after that I'll be putting down dricore subfloor, then studding up 2X4 walls on top of the dricore. There will be an air gap between the rigid and the 2X4's as I am laying in R-20 "2X6" batts. Plastic vapor barrier will complete the system before the drywall.

My question is about the rigid foam. I've been told that as long as it's not type 1 EPS, it will act as a vapor barrier and protect against moisture. My local building supplier ensured me the Type 2 Foundation Plus by TrueFoam was the stuff I was looking for, and no vapor barrier between it and the foundation would be necessary.

I'm skeptical of this after looking further into the product. It claims "breathability" and the perfect rigid foam for EXTERIOR applications. However mentions nothing about its use in finishing interior basement walls.

Any help would be greatly appreciated. It's in my garage already purchased and I just have a feeling like it may not be what I need. Thanks for the help.

Asked by Mark McKenzie
Posted Sep 1, 2014 5:49 PM ET
Edited Sep 2, 2014 7:13 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Mark,
First of all, the vapor permeance of the rigid foam installed in this location isn't that important. A wide range of rigid foam products can be successfully installed on the interior side of a basement wall -- ranging from rigid foam that is somewhat vapor-permeable to rigid foam that is vapor-impermeable. All of these products are in an acceptable permeance range. There is no need to have what you call a vapor barrier at this location.

For more information on this issue, see How to Insulate a Basement Wall.

The product under discussion -- TrueFoam Foundation Plus -- is simply one brand of EPS insulation. It will work just fine in your application.

I strongly advise you to omit the plastic vapor barrier that you plan to install on the interior side of the 2x4 studs. This polyethylene layer can potentially trap moisture, leading to mold and rot. When you install insulation on the interior side of a basement wall, the assembly should never include polyethylene.

Answered by Martin Holladay, GBA Advisor
Posted Sep 2, 2014 7:20 AM ET

Other Questions in Green building techniques

Should I air seal and insulate above the ceiling of my attached garage?

In Energy efficiency and durability | Asked by Nathaniel G | Mar 30, 15

New home buyer — metal roof in Maine with no sheathing

In General questions | Asked by dimitrios maniatakos | Mar 28, 15

2 questions: Rigid foam in attic space

In Energy efficiency and durability | Asked by Jeremy M | Mar 30, 15

Unvented slanted roof with radiant cooling and NO polyurethane in 4C

In GBA Pro help | Asked by Jan Verschuren | Mar 11, 15

Review of insulation/air sealing retrofit plan...

In Energy efficiency and durability | Asked by Howard Gentler | Mar 28, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!