Condo walls don’t have insulation so smells and airborne sounds travel easily between units. There are gas appliances so can’t get it too tight. However if there is a leak in one unit, you know pretty quickly. Condo in zone 4a. What is the best insulation for the walls to remedy this situation? Dense pack cellulose? JM Spider dense pack insulation? Thanks.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Sam,
    To reduce the transfer of smells from on unit to another, insulation is irrelevant. What you need to do is to seal air leaks between units. If that isn't enough, you can install a supply air ventilation system that pressurizes your unit; that will reduce the chance that smells will migrate inward.

    The fact that you have gas appliances doesn't mean that you have to live in a leaky home. Most gas appliances should be properly vented. If you have a gas stove for cooking, make sure that you have a range hood equipped with an exhaust fan, and use it when you cook.

    The techniques used for reducing sound transmission are different from those used to reduce smell transmission. Among the possible details to consider: installing mineral wool insulation between the studs (the denser the better); installing drywall on resilient channel; and installing two layers of drywall.

  2. samyork | | #2

    Thanks for the response. Doesn't the supply air ventilation system require the supply air flow to be higher than the leakage airflow in order to create positive pressure? If so, will it work without insulation in the walls? Tearing out walls to install insulation between the studs is not an option which is why I asked about the blown-in insulation.

  3. Expert Member
    Dana Dorsett | | #3

    Air sealing is primary for sound reduction.

    Blown in low-density cellulose insulation (not "dense packed") will improve the air tightness and reduce sound transfer, and dramatically reduce the amount of air that will move through those cavities via convective forces. If you dense-pack it the mechanical coupling from one side to the other goes up and more sound passes through.

    If you get to the point of ripping the walls open, mid-density rock wool batts that aren't thick enough to fully span the depth of the cavity will do more for sound reduction than full-depth batts, but unless it's air-tight you'd still have the smells issue.

    A second layer of wallboard attached with Green Glue (tm) also has a measurable benefit on the sound reduction.

    The Canadian National Research Council has spent a lot of time researching soundproofing, and is something of the Gold Standard on the issue. They have developed lots of tools & methods, and published tons of research, much of which is available online. Try surfing through some of their mateirial to find what's most relevant to your situation:

    http://www.nrc-cnrc.gc.ca/ctu-sc/category/st

    I haven't played with their acoustic design web-tool, so I'm not sure whether it would be of use to you, but I believe use is gratis if you want to register:

    http://www.nrc-cnrc.gc.ca/eng/solutions/advisory/soundpaths/index.html

  4. samyork | | #4

    I should also mention that sounds and smells tend to travel up and down rather than side to side. Maybe firewalls help prevent side to side transfer. Not sure. Thanks.

  5. Expert Member
    MALCOLM TAYLOR | | #5

    Sam,
    I second Dana's recommendation to look at the NRC's work on sound attenuation. It is very helpful and practical.

  6. GBA Editor
    Martin Holladay | | #6

    Sam,
    Q. "Doesn't the supply air ventilation system require the supply air flow to be higher than the leakage airflow in order to create positive pressure?"

    A. Yes, more or less -- although any supply air flow should reduce the chance that migrating smells will easily enter your home. Obviously, the more air tightening work you can do, the more effective a supply air system would be -- and the more likely this solution would work with a smaller fan.

    Q. "If so, will it work without insulation in the walls?"

    A. Yes. You can make a wall airtight even if the wall is uninsulated. But the insulation is definitely useful to reduce sound transmission.