Heating system sizing.

Is it possible to calculate the size of a heating system based on past energy usage? I'm working with a customer that I think their heating system is much larger than it should be. The average hourly BTU usage of the home was 28,000 BTU's for the time period of December 27th thru January 26. He has an electric boiler rated at 27 KW, producing around 92,000 BTU's. Weather data for this time period was 1810 heating degree days, average mean temp of 6 degrees. The location is zone 7, northern Minnesota. I believe the design temp for my area is -19.

Asked by Randy Williams
Posted Mar 8, 2018 5:06 PM ET

Tags:

7 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

"Is it possible to calculate the size of a heating system based on past energy usage?"

Yep! But it's not about the average hourly use, it's about what it needs at the coldest hours, using a linear approximation.

See:

http://www.greenbuildingadvisor.com/blogs/dept/guest-blogs/out-old-new

Answered by Dana Dorsett
Posted Mar 8, 2018 5:13 PM ET

2.

Using 28,000 BTU/hr at a mean temp of +6F, which is (65F-6F=) 59F below the presumptive base 65F balance point is a linear constant of (28,000 / 59=) ~ 475 BTU/degree-hour, give or take.

-19F (is this near Hibbing?) would be (65F- -19F =) 84F heating-degrees...

...x 475 BTU/degree-hour is an implied heat load of 39,900 BTU/hr @ -19F.

Heat load isn't EXACTLY linear with temperature- window losses are extremely non-linear, but that would be the right range.

So that's less than half the capacity of his electric boiler. ASHRAE recommends 1.4x oversizing as the compromise (that gets you through Polar Vortex coolth without suffering, but not ridiculously oversized), which for a ~40K load would be 56,000 BTU/hr, or 16kw.

That's the gist of it, but run your kwh/HDD numbers carefully, and use both base 60F and base 65F linear approximations to bracket it.

Is the electric boiler sub-metered, or was that the entire power use on the premises, including outdoor lights, hot water that ended up going down the drain, etc?

Answered by Dana Dorsett
Posted Mar 8, 2018 5:25 PM ET

3.

Thanks Dana, that was exactly what I was looking for.

Answered by Randy Williams
Posted Mar 8, 2018 5:37 PM ET

4.

The boiler is sub-metered at a rate of $.0765 per KW. Total usage for the time period was 5890 KW. A high bill complaint brought me to his house. He usually heats with an outdoor wood boiler. Your close on the location, about a half hour west of Hibbing.

Answered by Randy Williams
Posted Mar 8, 2018 5:41 PM ET

5.

A smaller electric boiler isn't going to be cheaper to run than an oversized electric boiler- the effieincy is the same either way.

If using this data to size some other heating equipment it has to be a period where auxiliary heat from the wood boiler wasn't in use.

Answered by Dana Dorsett
Posted Mar 8, 2018 5:48 PM ET

6.

Got it, thanks again.

Answered by Randy Williams
Posted Mar 8, 2018 6:23 PM ET

7.

> Heat load isn't EXACTLY linear with temperature

It can can get fairly in-exact when wind variation is factored in.

Answered by Jon R
Posted Mar 8, 2018 9:39 PM ET

Other Questions in Mechanicals

Conventional heat pumps with mini-split low temp efficiency?

In Mechanicals | Asked by Mai Tai | Jun 22, 18

Fastening Exterior pine trim to an ICF home

In Green building techniques | Asked by Wayde | Jun 23, 18

Dirty electric from minisplit ductless heat and air conditioning

In General questions | Asked by Arleendv | May 30, 18

Bubble-wrap air space 2" below in-joist radiant floor heating

In Energy efficiency and durability | Asked by user-6765846 | Jun 23, 18

Tyvek reinvent battens

In Green building techniques | Asked by user-7088022 | Jun 23, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!