Indoor dryer vent kit?

Does anyone have any feedback on indoor dryer vent kits? Are they a good idea/bad idea? I have a electric dryer for our new house we're building in New Hampshire, but would like to avoid putting an additional hole in the wall if I could. If I didn't already have a dryer, I would likely have gotten a condensing dryer that doesn't require venting.

Asked by Scott McCullough
Posted Nov 13, 2012 5:54 PM ET

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

In a NH climate they're always a BAD idea, even if you filter the heck out of them, especially on a house as tight as you'd LIKE to be able to have. Dumping the humidity indoors adds a latent load to the summer AC and could lead to mold conditions even during the shoulder seasons, even with an HRV running a pretty good duty cycle.

In high-dry locations (say, at 8000' in AZ) the additional moisture load is of little consequence, but you;d still have issues with suspended particles (and VOCs, with some laundry products) adding to the indoor air pollution burden.

Another hole in the wall, with a better than average backdraft preventer on the dryer vent (eg: http://store.dryerbox.com/Dryer-Vent-Closure-for-Wall_p_29.html or similar ) would be the way to go in NH.

Answered by Dana Dorsett
Posted Nov 13, 2012 6:04 PM ET

2.

Scott,
Q. "Does anyone have any feedback on indoor dryer vent kits? Are they a good idea/bad idea?"

A. Bad idea.

If you are tempted to ignore my advice and install one anyway, be aware that they are particularly dangerous if you have a gas dryer. If you install one on a gas dryer, you will not only be helping to destroy your house (as you would with an electric dryer), you will also be destroying your health (because of the combustion byproducts).

Answered by Martin Holladay
Posted Nov 14, 2012 7:25 AM ET

3.

Thanks for the feedback. As I said, it's an electric dryer, though it seems like the 'dryerbox' that Dana suggested is the way to go. I'll try to find one that is less of an eyesore or figure out a way to disguise it. Thanks again.

Answered by Scott McCullough
Posted Nov 14, 2012 9:42 AM ET

4.

Less of an eyesore: http://www.seiho.com/product/sfb/sfb.html

I use these on every job.

Answered by David Meiland
Posted Nov 14, 2012 10:48 AM ET

Other Questions in Mechanicals

ERV and flex duct

In Mechanicals | Asked by William Costello | Mar 22, 17

Insulating floor of an old barn

In Energy efficiency and durability | Asked by Michael Stelts | Mar 22, 17

PV panels on the roof or in the yard?

In General questions | Asked by user-6801629 | Mar 24, 17

2 layers vs 1 of outsulation?

In Energy efficiency and durability | Asked by Adam Fuller | Mar 24, 17

Another Question over Spray foaming Cathedral Attic

In Green building techniques | Asked by uberaustin | Mar 24, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!