Is a 16 SEER air conditioning system worth it over a 14 SEER in Houston, TX?

Building a new house, 1.5 story and looking to get the most bang for my buck. Doing 2x6 walls with polyseal spray and cellulose insulation. Will a 16 Seer be worth the addition $3-4 k I have been quoted? Energy prices here are currently 10-12 cents per kw hour, but do rise occasionally. I am most concerned about home comfort though and have been told by some folks that higher seer units in this humidity are not worth it. Any thoughts?

The house is appx 3500 sq ft with 2700 down and 800 up. I am looking at two units, a 4 Tom down and a 2 ton up.

I am also interested on thoughts on the necessity of a fresh air inlet. I am not using spray foam and will have an unconditioned attic, but I am using the polyseal and spray foam at all windows and joints and using the airtight can lights. I am trying to get as tight as I can for less cost. Not sure if that is tight enough to need a fresh air duct in AC. I don't think the environments for living homes are doing this and they are using similar sealing methods.

Thanks!!

Asked by Dustin Gohmert
Posted Wed, 01/16/2013 - 22:58
Edited Thu, 01/17/2013 - 04:56

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Answered by Armando Cobo
Posted Thu, 01/17/2013 - 00:25

2.
Helpful? 0

Thank you for the links. I think I may have further confused myself. Looking up the model numbers, the vendor has quoted for the low end quote a Trane XB14 series. However when I look it up, it claims "up to 16 SEER". The high end unit he quoted was a Trane XR16i that claims up to 17.5 SEER. Is the "up to" rating something to be wary of? I know installation highly matters, but if installed properly with the proper coil, do I get a 16 SEER unit out of the XB14?

I guess then I also wonder if I need the dual stage compressor of the XR16i? I have heard warning against them for lack of reliability.

There is a series in between these two that I want to look into because they seem more like what I am after in terms of efficiency, cost, and noise levels.

Answered by Dustin Gohmert
Posted Thu, 01/17/2013 - 00:33

3.
Helpful? 0

Dustin,
I'm not sure what you mean by "Polyseal spray." There is an insulation company in Alaska called Polyseal Insulation, but I don't think that's the company. There is a company in Plano, Texas called Polyseal Coating -- they seem to make industrial paints. So please describe what you mean by Polyseal.

You wrote, "I am not using spray foam and will have an unconditioned attic." I certainly hope that you don't plan to have any ductwork in your unconditioned attic. If you do have ducts there, then your questions concerning 14 SEER versus 16 SEER -- or 16 SEER vesus 17.5 SEER -- are totally off base.

The type of equipment is irrelevant if your ductwork is outdoors. If you are considering spending $3,000 to $4,000 to upgrade your equipment, spend the money instead on bringing your ductwork inside your house.

Answered by Martin Holladay, GBA Advisor
Posted Thu, 01/17/2013 - 04:55

Other Questions in Mechanicals

Grid-tied without independence … what’s the point?

In General questions | Asked by flitch plate | Sep 29, 14

Windows for my Pretty Good House

In Green products and materials | Asked by Matt Mesa | Sep 29, 14

Please tell me why I have to put so much insulation / outsulation at the roof/celing?

In Energy efficiency and durability | Asked by leo kloop | Sep 30, 14

Is continuous polyiso over plywood and concrete wall OK?

In Plans Review | Asked by Jamie Malcolm-Brown | Sep 30, 14

How to handle SE/SW orientation? And any experiences with Richlin windows?

In PassivHaus | Asked by Ryan Griffin | Sep 30, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!