0 Helpful?

Fixing undersized ductwork - best approach for difficult section?

I've just uncovered some ductwork in my house that needs to be addressed. It is a 1400 square foot two storey brick house, no wall insulation, in climate zone 5. It's a narrow and tall Victorian house and the ductwork in question feeds the rear of the house on both storeys - kitchen on the first floor and a bedroom on the second. These rooms have been poorly heated ever since I've lived here but last winter, which was particularly testing, the rear bedroom was basically uninhabitable without backup electric heat.

The ductwork runs from a 14x8 duct out of the plenum 8' where it breaks off into two 6" round ducts which are routed between the floor joists to the exterior wall. From there, one flex duct serves a register in the kitchen and the other sheet metal duct continues to the rear of the house where it serves one register in the kitchen and one in the bedroom above. The vertical duct reaching upstairs is 6x10 sheet metal.

I'm no HVAC expert but my gut tells me this ductwork is a little small - considering it serves the rooms furthest away from the furnace and with the most heat loss. Airflow feels extremely weak out of all 3 registers. The other side of the house has an 18x8 trunk so I figure that's where the air prefers to go. Comfort levels in the house bear out these assumptions.

My question is how to best deal with this span of ductwork replacing everything from the 14x8 trunk to the 6x10 at the far corner, i.e. replacing the round 6" section.

Based on the numbers - 1400 square foot house, zone 5, no wall insulation, R40 attic, 75,000BTU furnace, would 14x8 duct likely get the job done or do I need to go back further and use bigger duct? Total length is about 30' from furnace to second floor register. I intend to seal / insulate all the basement ductwork and install balancing dampers as part of this project.

There are a lot of elbows required to turn the duct up through the floor joists and down and around again adding lots of equivalent length to this already long duct. There's not much room to put them so the elbows that would fit best are the crappiest ones for airflow. What is the best approach to fittings? Should I have transitions custom manufactured or could I combine stock fittings to do what's required with reasonable efficiency?

Is it reasonable to maintain this headspace in the basement by running the duct through the joists, or should I abandon it and just have a duct to duck under to get to the basement room?

Thanks again for the always helpful answers.

IMG_0837.jpg1.45 MB
IMG_0838.JPG1.38 MB
IMG_0839.jpg355.36 KB
Asked by Jonathan Dalton
Posted Jul 10, 2014 3:40 PM ET
Edited Jul 11, 2014 7:35 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Jonathan,
Duct design is a complicated topic -- more than can be easily covered here. The short answer is that the correct solution to your problems requires an experienced engineer or HVAC contractor who knows how to perform room-by-room Manual J calculations and Manual D calculations. That's how duct systems are designed.

For a longer answer and some useful rules of thumb, see the section titled "Designing a duct system" in the following article: All About Furnaces and Duct Systems.

Answered by Martin Holladay
Posted Jul 11, 2014 7:42 AM ET
Edited Jul 11, 2014 7:50 AM ET.

Other Questions in Mechanicals

Water cooled refrigerator coils

In Mechanicals | Asked by LT.Son | May 19, 18

Fasteners for concrete, brick, and CMUs

In General questions | Asked by Martin Holladay | May 23, 18

Spray foam questions

In General questions | Asked by Stanger133 | May 20, 18

1 1/2 story farmhouse in British Columbia

In Plans Review | Asked by Michael Blake | May 22, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!