0 Helpful?

Insulating at Steel Beam

Good evening,

This question is for a new construction home, climate zone 4A, with north being to the right in the attached PDF. I was planning on using OC spray foam directly under the roof sheathing and in the walls, but I changed my mind during construction after reading accounts of problems with the foam installations, particularly during the winter. I now am now using dense packed cellulose in the walls and using loose fill cellulose on the ceilings.

I have attached a bit of a tricky (non-ideal) detail for everyone's review and comment. My plan is to fill in the web of the W8 steel beam with tapered rigid insulation, foam/seal the rigid to the steel beam, and then provide a 2" bead of foam to the wood members to provide an air seal. The beam will be "warm" in the winter and "cold" in the summer. Unfortunately, the contractor ordered the beam 1.5" too long, so I can only get 1/2" of insulation at the end of the beam adjacent to the exterior wall. I will either foam in this gap or push in a piece of 1/2" rigid insulation. Any thoughts, suggestions, or obvious issues I may be missing?

Thank you to all,
David

Beam Insulation.pdf32.31 KB
Asked by David Baca
Posted Jan 15, 2013 7:57 PM ET
Edited Jan 15, 2013 7:58 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
0 Helpful?

David,
It looks like the steel beam is well insulated -- except, perhaps, at the ends.

One comment: if your contractor ordered the beam 1.5 inch too long, it's within your rights to tell him to cut it shorter -- at his expense.

Answered by Martin Holladay, GBA Advisor
Posted Jan 16, 2013 9:12 AM ET

Other Questions in Plans Review

Why is it so trendy to hate on radiant in-floor heat?

In Mechanicals | Asked by Josh Jipson | Mar 1, 15

Best way to have a wood fireplace?

In Energy efficiency and durability | Asked by Clara Kim | Feb 22, 15

Adding wall R-value in a historic retrofit

In Green building techniques | Asked by alok khuntia | Feb 28, 15

Insulating a low-slope EPDM roof from the ceiling below

In General questions | Asked by joseph moore | Feb 26, 15

Dense packing cellulose - height of cavity

In General questions | Asked by Graham Fisher | Feb 28, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!