Vented or Unvented Attic?
The Approach to the Attic Depends on Whether It's Going to Be a Living Space
UPDATED 11/18/2011
Bird's-Eye View
Determine whether to insulate the floor or the roof
Utilizing the attic as a living area is a good, green way to take full advantage of the available floorspace for a given house footprint. Why let a whole floor go to waste when the alternative might require building a bigger foundation?
An attic's intended use determines where and how it should be insulated and air sealed. There are basic principles involved, and within each, there are variations. (Isn't that what makes green building so much fun?)
See below for:
ABOUT ROOF VENTING
UNCONDITIONED ATTICS
CONDITIONED ATTICS
INSULATING AND AIR BARRIERS
Key Materials
Open-cell vs. closed-cell polyurethane foam
Roofs above conditioned attics are usually insulated with spray polyurethane foam. Builders can choose either closed-cell (2-pound) foam or open-cell (1/2-pound) foam.
Closed-cell foam. When typically installed, closed-cell foam is a vapor retarder as well as an air barrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both.. When sprayed on the underside of roof sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. , it prevents any interior moisture from reaching the cold roof sheathing.
Open-cell foam, on the other hand, is vapor permeable. When used in a cold climate, the interior face of the foam should be covered with a vapor retarder to prevent interior moisture from diffusing through the foam and condensing against the cold roof sheathing. Some installers spray a vapor-retarder paint on the inside face of cured open-cell foam.
Many building inspectors require that spray polyurethane foam installed in a conditioned attic be protected by a layer of 1/2-inch drywall or an equivalent thermal barrier. The requirement applies both to open- and closed-cell foam.
Design Notes
Batts don't work well between rafters
As long as an air barrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both. is in place, almost any type of insulation can be installed on an attic floor. Many types of insulation, including fiberglass batts and cellulose, perform poorly between rafters, however.
Problems arise when interior air or water vapor has access to cold roof sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. , leading to condensation. These problems are difficult to prevent with fiberglass batts or cellulose insulationThermal insulation made from recycled newspaper or other wastepaper; often treated with borates for fire and insect protection..
The best way to insulate rafter bays is with spray polyurethane foam. This creates an air barrier between the attic and the roof sheathing.
In new construction, a conditioned attic can also be created by using structural insulated panels (SIPs) in the roof installation. Similarly, a conventionally framed roof can be insulated from above with rigid foam.
Builder Tips
Air-barrier continuity is crucial
One of the biggest challenges builders face when completing an attic is getting the air-barrier details right. When a conditioned attic is insulated with spray polyurethane foam, most air leakage problems are addressed by the insulation. However, builders should ensure air-barrier continuity at the attic perimeter and at chimneys. For more on the topic, see "Air BarrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both. Details" below.
The Code
Venting, insulation, critters, and R-values
Requirements for unvented conditioned attics are found in Section R806.4 of the IRCInternational Residential Code. The one- and two-family dwelling model building code copyrighted by the International Code Council. The IRC is meant to be a stand-alone code compatible with the three national building codes—the Building Officials and Code Administrators (BOCA) National code, the Southern Building Code Congress International (SBCCI) code and the International Conference of Building Officials (ICBO) code.. Insulation installed in direct contact with the underside of the roof sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. must be air impermeable.
Attic venting
Sections 806, 1101, and 1102 of the IRC relate to ventilation and energy efficiency details. All code references are to the IRC unless otherwise specified.
Ventilation
Venting needs to reach all air spaces above attic insulation [806.1] and have an area greater than 1/150 of the attic square footage [806.2]. This area can drop to 1/300 if 80-50% of the venting is 3 ft. above the eave vents or if a less than 1 perm vapor barrier is on the warm-in-winter side of the ceiling [806.2]. Keep critters out of your vents with 1/8 to 1/4 in. screening [806.1].
Insulation
Installers need to post a certificate of R-value if it isn't clearly marked on the insulation [1101.4]. In the warmest climates, attic insulation needs to be R-30, but in most cases it's best to have a considerably higher R-value [1102.1]. Whether you enclose recessed lights in an airtight, insulated box, or use properly sealed IC-rated fixtures, inside air shouldn't leak into your attic [1102.43].
Illustration: from Code Check Building 2nd Edition. click to buy .
OTHER CONSIDERATIONS
Complex roofs are special cases.
Effective roof ventilation becomes a problem with complex roof shapes. Ridge or soffit vents may be sources of water intrusion in coastal areas. It may be easier to move the insulation and air barrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both. up to the roof sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. , making the attic a conditioned spaceInsulated, air-sealed part of a building that is actively heated and/or cooled for occupant comfort. . This can be done whether or not the attic is tall enough to be used as living space.
MORE INSULATION IS ALWAYS BETTER
Recommended R-values for attic insulation vary by region and climate, ranging upward to R-49 in colder areas of the country, according to U.S. Department of Energy guidelines. More insulation, however, is usually a good investment. Many cold-climate builders now insulate attics to R-60.
AVOID POWERED ATTIC VENTILATORS
Powered attic ventilators should never be used because they cause more problems than they solve. Unless they are PVPhotovoltaics. Generation of electricity directly from sunlight. A photovoltaic (PV) cell has no moving parts; electrons are energized by sunlight and result in current flow.-powered, they require energy to run. By depressurizing the attic space, they can suck conditioned air out of a house through ceiling cracks, increasing energy costs for heating and air conditioning. Some powered attic ventilators are powerful enough to depressurize a home's interior and cause gas water heaters to backdraft.
DRAWING LIBRARY CONSTRUCTION DETAILS
Roof-Section Details
Vented Roof Details
GREEN POINTS
LEED-H Conditioned spaceInsulated, air-sealed part of a building that is actively heated and/or cooled for occupant comfort. that also meets requirements for habitable space is counted in the floor area to determine the award thresholds. A conditioned attic may have adverse scoring implications (based on the LEED for HomesLeadership in Energy and Environmental Design. LEED for Homes is the residential green building program from the United States Green Building Council (USGBC). While this program is primarily designed for and applicable to new home projects, major gut rehabs can qualify. score adjustments,which are themselved based on home size).
NGBSNational Green Building Standard Based on the NAHB Model Green Home Building Guidelines and passed through ANSI. This standard can be applied to both new homes, remodeling projects, and additions. Under Chapter 7, "Energy Efficiency": up to 3 points for Energy StarLabeling system sponsored by the Environmental Protection Agency and the US Department of Energy for labeling the most energy-efficient products on the market; applies to a wide range of products, from computers and office equipment to refrigerators and air conditioners. thermal bypass checklist items that apply to attics (703.2.1.4).
ABOUT ATTICS
To vent or not to vent, that is the question.
In the broadest sense, an attic is simply a space between a pitched roof deck and the rest of the house. Depending on how the house has been framed, an attic can be anything from a valuable storage or living area to a space just large enough for heating and ventilating ducts.
When an attic is conditioned, the thermal and air barriers are located in the roof; in an unconditioned attic, insulation and air barriers are in the ceiling that separates the house from the attic. Conditioning an attic raises questions about the type of venting, so these two components need an integrated approach for high performance.
If your pitched roof creates a decent-sized space, why not use it? Detailing the insulation of a roof can be tricky and expensive, but the resulting space can make good sense — economically and environmentally.
In many parts of the country, builders put HVAC(Heating, ventilation, and air conditioning). Collectively, the mechanical systems that heat, ventilate, and cool a building. or plumbing systems in the attic rather than in the living space, where they belong. If these components must go into the attic, then the air barrier and insulation should be moved up to the roof line, making the attic unvented and semi-conditioned. Conditioned or semi-conditioned attics use a little more energy than unconditioned attics, but the amount is insignificant compared to heat loss through ducts and pipes in a vented, unconditioned attic.
About roof venting
By convention, the minimum amount of ventilation is described as a ratio of vent space to ceiling area. Building codes usually require 1 sq. ft. of vent space for every 150 sq. ft. of insulated ceiling; the ratio can be adjusted depending on several factors.
Why vent?
In an unconditioned attic, ventilation serves a number of purposes. The flow of cold air beneath the roof deck in winter helps prevent ice dams and remove moisture that works its way up through the ceiling and insulation. During the summer, vents help carry away the hot air that accumulates under the roof deck, lowering cooling costs in the conditioned spaceInsulated, air-sealed part of a building that is actively heated and/or cooled for occupant comfort. below.
Soffit and ridge vents
The usual way to vent a roof is with continuous soffit vents acting as air inlets and a continuous ridge vent to act as an air outlet. In most cases, ventilation takes place beneath the roof deck. Builders using this method must install vent channels in each rafter bay before insulation is installed.
Insulation should not be allowed to block the flow of air beneath the roof deck. Above the top plates of exterior walls, ventilation chutes should be installed in each rafter bay to keep insulation away from the sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. . In most cases, a vertical wind dam should be installed at the base of each ventilation chute.
If the insulation is spray foam, it's important to choose rafter baffles that are sturdy enough to resist the forces created by the expanding foam. Many builders prefer to make site-built channels using 1"x1" battens and narrow pieces of rigid foam.
Venting above the sheathing
Vent channels can also be built above the roof sheathing. Builders following this method usually install several layers of rigid foam above the roof sheathing, followed by parallel lengths of 2x4s installed above the foam, each positioned above a rafter. A second layer of roof sheathing is then installed above the 2x4s.
ABOUT UNCONDITIONED ATTICS
Thick insulation is easier if the attic is unconditioned
Laying down unfaced fiberglass batts or, better yet, blowing cellulose between the joists in an unfinished attic can be the fastest, easiest, and most affordable way to achieve high R-values. As long as a house is designed with an uncomplicated roof, the best way to detail the attic is as vented unconditioned space.
Go to the top of an old farmhouse and what you will almost certainly find is an open attic, its rafters and roof sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. in plain view. Ventilation could take the form of operable windows or louvered vents in the gable-end walls. Any insulation would be in the floor that divides the attic from the rest of the house.
This is essentially how many houses are built today. The space immediately beneath the roof is “unconditioned.” Whether the attic has enough headroom for storage or is too low to be of any practical use, these houses have one common feature: the attic and the living space below are separated by insulation and an air barrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both..
The two most common problems with unconditioned attics are air leaks at the ceiling plane and not enough insulation, which can result in ice dams in colder climates. It's especially critical to seal air leaks and install adequate insulation at the attic perimeter, where ice damming problems begin. But this is also important in hot climates, where attics can get extremely hot; piles of insulation can make it a lot easier to keep a house cool.
To ensure that there is enough room for insulation at the attic perimeter, use raised-heel trusses or raised plate framing details. If design issues limit the available space for insulation, spray foam may be required at the attic perimeter.
Unconditioned attics are cheap and easy
In an unconditioned attic, it's much less expensive to install a thick layer of insulation on the attic floor than between the rafters, and it's easier to ventilate the roof. Perhaps the biggest bonus of all is that it's a lot easier to pinpoint a roof leak when the roof sheathing isn't hidden by insulation.
ABOUT CONDITIONED ATTICS
Keep roof lines simple
When the attic has headroom for living space, it may be worth it to condition it and insulate the roof. If mechanical equipment and ductwork are located in the attic, it's smart to seal the vents and treat it as semi-conditioned spaceInsulated, air-sealed part of a building that is actively heated and/or cooled for occupant comfort. — insulated but not heated.
Some people argue that if we don't ventilate wall cavities, why do we need to ventilate roof cavities? Aren't roofs just like walls that are leaning? The answer is, well, sort of.
Conditioned roof assemblies are becoming more common because they are being allowed by local building officials more often. To keep these assemblies dry, they must be airtight because moisture that gets in has a tough time getting out.
A better understanding of how heat and moisture move through building materials, in combination with more sophisticated building products, have cleared the way for successful designs that can be adapted to all climate zones. Just like walls, unvented roof designs should be based on climate. Where temperatures dip low enough to cause condensation, either moisture must be kept away from the sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. or the sheathing temperature must be kept high enough to prevent condensation. Exterior rigid foam above the roof sheathing or closed-cell foam insulation under the roof deck can achieve this in all climates.
Unvented roofs can perform well as long as they are properly detailed to limit moisture transfer from the interior. Construction details vary depending on climate, but closed-cell spray polyurethane foam (specifically allowed by Section R806.4 of the International Residential Code) can be used anywhere.
Closed-cell spray foam to the rescue
Spraying closed-cell polyurethane foam directly onto the underside of the roof deck to form an air, vapor, and thermal barrier, is a foolproof but expensive way to insulate cathedral ceilings or conditioned attics. Closed-cell foam is denser and heavier than open-cell foams and also has higher R-values. According to a description of this technique by the Building Science Corp., a minimum of 1 inch of closed-cell foam acts as an air barrierBuilding assembly components that work as a system to restrict air flow through the building envelope. Air barriers may or may not act as a vapor barrier. The air barrier can be on the exterior, the interior of the assembly, or both., while a minimum of 2 inches creates a vapor retarder.
The foam sticks tenaciously to the roof deck and expands to fill cracks and voids that in a cold climate might allow warm, humid air to reach the back of the roof deck and condense. In a hot climate, the foam blocks humid air from entering the house, where it could condense on cooler surfaces.
Closed-cell foam can be combined with other types of insulation, such as fiberglass or cellulose, to get the benefits of an air or vapor barrier and to meet local energy guidelines at a lower cost.
One criticism of unvented roofs insulated with spray foam is that roof leaks are difficult to detect and could cause extensive roof sheathing rot before the homeowner notices any problems.
ABOUT INSULATION AND AIR BARRIERS
An air barrier between the living space and the attic prevents the escape of conditioned air and interior moisture into the attic.
In cold climates, some builders use a continuous layer of plastic at the ceiling line as a combination air barrier and vapor retarder. Those using the airtight drywall approach install ceiling drywall with gaskets. In either case, penetrations through the attic floor must be carefully sealed with caulk or spray foam, and attic access hatches must be weatherstripped.
Maintaining this air barrier can be difficult when the ceiling is punctured by recessed lighting fixtures or heating and cooling ducts.
A home's air barrier should always be contiguous with its thermal barrier. In a home with a conditioned attic, the air barrier follows the slope of the rafters. As long as the rafters are filled with spray foam insulation, it's fairly easy to achieve a high-quality air barrier.
Houses with unconditioned attics use a variety of insulation materials. Unless the attic floor is being insulated with spray foam, the integrity of the air barrier must be verified before attic insulation is installed. Most of this air barrier work is performed from the attic. Steps will vary depending on the home's construction details, but may include:
  • Installation of site-built boxes around recessed can fixtures. These can be built from scraps of rigid foam, using canned foam as an adhesive.
  • Installation of caulk or spray foam to seal the cracks between partition top plates and drywall.
  • Sealing oversized holes for plumbing vent pipes and electrical wires.
  • Sealing gaps around chimneys.
  • Sealing the tops of vertical chases enclosing plumbing pipes, ducts, or flues.
  • Before the insulation is installed, these steps may also be required:
  • Installing insulation dams around the attic access hatch.
  • Installing vent baffles and dams above the top plate of exterior walls to protect insulation from wind-washing.
  • FURTHER RESOURCES
    How to Build an Insulated Cathedral Ceiling
    Creating a Conditioned Attic
    BuildingScience.com: Understanding Attic Ventilation
    A Vent on Venting by Joseph Lstiburek, P. Eng.
    Unvented Roof Systems
    Image Credits:
    1. Don Mannes/Fine Homebuilding #190
    2. Daniel Morrison
    Tags: , , , , , ,
    8.
    Tue, 12/27/2011 - 11:46
    Re: Ice Dams & Icicles with Closed Attic Assemblies
    by Kevin Kane
    Martin, I agree... I have not had a water leak in a closed attic assembly due to ice dams caused by the sun (or at all for that matter)... only massive icicles growing from the eaves on the sunny side. I built a 2-story energy star certified home last year with a closed attic assembly under an 8/12 & 12/12 pitch roof. This house is so tight the guys doing the blower door test thought their equipment was malfunctioning at first. There is 7" of open cell spray foam on the bottom side of the roof deck that encapsulates the top cord of the roof trusses. A manual J calc and HERS rating shows this thickness of foam to be more than adequate here in Iowa. The owner is amazed at how easily the house heats and cools. Snow easily blankets the roof until the sun finds a patch of exposed asphalt shingles. I believe the sun is able to quickly warm the shingles where the roof deck is insulated on the bottom side. Since the eaves of this house are not insulated I believe they remain below freezing. In essence we end up with a warm roof above the attic (when the sun shines) and cold eaves (because they are cooled from the bottom by ambient air temps) which recreates the very conditions we have been trying to prevent all these years. I have another home being built right now and I think I will spray foam the eaves and porches to make the roof construction consistent from the ridge cap to the drip edge. Perhaps this will allow the eaves to warm up and melt off when the sun hits them rather than refreeze the snowmelt from above. Worst case scenario is I install an electric ice melt system along the eaves, gutters, and downspouts. Overall a foam insulated home is amazingly energy efficient and quiet. I have to admit the icicles surprised me, but I really do not think it is due to heat loss through the foam. If we get a good snow here in Iowa followed by some sunshine I will have a perfect test subject since the home I am currently building is not yet heated. The roof deck is entirely foamed minus the eaves and porches at this time. If I get massive icicles on a sunny day it will reinforce my theory. Then I will insulate the eaves and see what happens. Strangely we have only had about 1" of snow in Iowa so far this season... very odd, but great for construction. Thanks for your input on this subject.
    7.
    Tue, 12/27/2011 - 07:47
    Response to Kevin
    Kevin,
    Yes, sunshine can definitely contribute to ice dams, especially if there is a shady portion of the roof or a valley below the sunny portion of the roof. It's rare for sunshine to cause ice dam problems resulting in leaky ceilings, however, if the house is well detailed (that is, equipped with an effective air barrier and adequate ceiling insulation).
    If there is a detached unheated garage next to a heated house, it's valuable to compare the ice dams, if any, on the two buildings. Any icicles on the garage are usually caused by sunshine, while the icicles and ice dams on the house can be caused by many factors, included heat loss due to air leakage or thin insulation.
    For more information on ice dams, see Prevent Ice Dams With Air Sealing and Insulation.
    6.
    Tue, 12/27/2011 - 02:59
    by Kevin Kane
    Could it be possible (as Chet mentioned) that the sun is warming the roofing materials and causing the snowmelt? I believe this can happen on any type of roof but perhaps more so on a closed attic assembly with spray foam applied directly to the bottom side of the roof sheathing. Perhaps the sun can more easily warm the insulated roofing materials since they are not being cooled from the bottom side by cold winter air. I have only noticed icicles on the sunny side of these roofs. The snowmelt only occurs when the sun is shining (or when the air temp is high enough). If the snowmelt were due to heat loss through the foam insulation it would happen at night and on cloudy days, but it only seems to happen when the sun shines. I believe the ice dams then form on shaded and/or un-insulated portions of the roof deck such as un-insulated overhangs and porches. I think ice dams and icicles could be reduced or eliminated by insulating the overhangs and porches to allow them to warm up like the rest of the roof when exposed to direct sunlight. Insulation may even help when the overhangs are shaded by allowing the melted snow to warm the roofing materials more easily. Thoughts?
    5.
    Mon, 10/11/2010 - 16:19
    Causes of Ice Dam Formation
    by Chet
    Thanks for the info on ice dams. I believe I have a different situation that causes ice dams at my location in the San Luis Valley of Colorado ( a very cold and snowy location).
    I have a roof that is hipped and that gets lots of southwest sun that melts the snow on two faces. They drain onto some lower sections that face away from the sun and have valleys that are always shaded from the sun. The the snow does not melt in the shade but the ice from the water above freezes in the valleys. My ice dam forms near a vertical wall along such a valley. The house is pretty well insulated and sealed with at least 8" of closed cell foam on the roof sheathing. I've inspected the attic penetrations and fixed all I could find but that has not stopped the ice dams.
    Cheers
    Chet
    4.
    Wed, 09/08/2010 - 13:20
    Response to Sean Wiens
    Sean Wiens,
    Then install metal roofing over the foam. No top layer of sheathing is required, just 1x3 or 2x4 strapping over the foam.
    3.
    Wed, 09/08/2010 - 13:09
    Roof Leaks
    by Sean Wiens
    Thanks Martin - I just personally do not like the wasted material of a dbl roof deck
    2.
    Wed, 09/08/2010 - 05:25
    Sean Wiens,
    I don't agree with you that spraying foam on the underside of the roof sheathing is the "best" way to create a conditioned attic or cathedral ceiling. Here are two better ways:
    1. Install thick layers of rigid foam board on the exterior side (the top) of the roof sheathing.
    2. Create site-built ventilation channels under the roof sheathing using 1x1 sticks in the corners of the rafter bays and rigid material like Thermoply, OSB, Masonite, or rigid foam board. Then install closed-cell spray foam on the underside of the material that was used to create the ventilation channel.
    3. The "danger of roof leaks" will never go away. Builders have to choose a system that allows them to sleep at night. If you want an easy way to regularly inspect the underside of your roof system for leaks, then the best choice is an unconditioned attic. Once you switch to a conditioned attic or a cathedral ceiling, you really can't inspect the roof sheathing. Pin-pointing roof leaks becomes difficult.
    1.
    Wed, 09/08/2010 - 01:37
    Roof Leaks
    by Sean Wiens
    It appears that if you are going to have a conditioned attic or a cathedral ceiling, that closed cell foam sprayed right to the underside of the roof sheathing in thicknesses enough to form both an air and vapour barrier is best.
    But how do you address the added danger in this system that roof leaks represent. Is there an effective way at mitigating this issue?