Musings of an Energy Nerd
European vs. U.S.–Manufactured Windows
It's impossible to compare European window U-factors to American window U-factors
This triple-glazed window is manufactured in Austria by Optiwin. [Illustration credit: Fine Homebuilding]
If you’ve ever shopped for windows in the U.S., you’ve probably noticed that most windows come with a National Fenestration Rating Council (NFRC) label listing energy performance numbers. Before the NFRC developed a standardized method of reporting U-factor and solar heat gain coefficient (SHGC) ratings for windows, manufacturers’ reporting methods were inconsistent. The establishment of the NFRC standard benefited window buyers by allowing for comparison shopping.
As long as windows have an NFRC label—most major U.S. brands do—window buyers can compare the performance specifications of windows from different manufacturers. (For more information on U-factor and solar heat gain coefficient, see “All About Glazing Options.”)
Europe is different
Unsurprisingly, European window manufacturers test their windows according to different standards than American manufacturers. That means buyers can’t directly compare window performance claims made by European manufacturers to the claims of U.S. manufacturers—unless the European manufacturer has gone to the trouble of getting NFRC labels for their windows. (Most haven’t, because getting the laboratory testing done to obtain NFRC certification is expensive.)
Several GBA articles and Q&A threads explain how European window manufacturers differ from U.S. window manufacturers when it comes to reporting U-factors and solar heat gain coefficient. (Many of these articles are listed in the “Related Articles” sidebar at left.) I think it’s time to collect the most important information from all of these articles and Q&A threads together in one spot.
The table below attempts to summarize some of the differences between the North American approach and the European approach when it comes to window design and window energy performance reporting.
26 Comments
    Michael Maines | | #1
    Excellent overview, Martin. It's unfortunate that there is really no way to correlate the different ways of calculating the window U-factor. In Passive House software, each part of the window is input separately so it's custom-calculated but time-consuming to do so.
  2. pjpfeiff | | #2
    It must also be the case that there is a standard size window used for ratings. Do the two rating systems at least use about the same size window?
    1. MartinHolladay | | #3
      Pipfeiff,
      The NFRC rating system is accurate for the window size you are purchasing. Software is used to adjust the U-factor as needed for differently sized windows. This software requires inputs of frame characteristics, the width of the frame, and the shape of the window. It uses extensive historical testing data of the performance of windows of different sizes and shapes.
      1. pjpfeiff | | #4
        Thanks, that's cool. Now if they could just validate their models to where they could provide U-factor as a function of delta-T (or at least the outside T while keeping the inside fixed) we'd be all set.
        1. enteecee | | #11
          It's cool except during design if you're cutting it close on U-Factor requirements (code or otherwise) because the characteristics of each window with all its specific options isn't readily available. Turns out this window needs to be 6" narrower for structure, or that one can be enlarged now that there's a better location in the room for a TV? Either way could be a call to the manufacturer to figure out whether the spec needs to be changed to meet goals.
          On balance I'm glad for the specificity, but it would be great to know there's always enough wiggle between product and spec to not sweat it so much. Since windows are inherently the thermal weak spots in any good wall, though, I don't think we'll get that. Performance will have to increase a great deal before standards stop rising to meet them.
  3. charlie_sullivan | | #5
    It seems like we have sufficient computer power now that we could list windows with a climate-specific U-factor rating. You look up the window, put in your zip code, and get a rating for your situation, calculated for the center of glass from the specifics of the spacing, gas, and coatings used, and then adjusted for the framing.
    1. enteecee | | #12
      As best I can tell from working with the manufacturers, the trick is really data entry and management for a product that has so many variables in each instance. beyond the obvious like double or triple glazing, changing the gas or coating or true lites in any window of a given size changes the whole rating. Multiply that over the material and cladding options, and the stock sizes, and the scale of data management comes into focus - then add custom sizing to the mix!
  4. jollygreenshortguy | | #6
    Excellent article that covers all the important points.
    I'll just mention, I'm an American, living in France. The window in the illustration I would characterize as better than average for what is installed in the new homes here. Like in the USA, there are plenty of builders ready to put in the lowest quality they can get away with that looks good on the surface. That's why it's so important that we have a regulatory authority to set a minimum standard. Unfortunately, minimum standard is the best an uninformed homebuyer can expect to get when buying a new home.
  5. entropic | | #7
    Very helpful article and collection of other similar article links on this topic. Thanks, Martin.
    Is there any source of air tightness measurements for comparing North American to European windows? Since the dogma generally prioritizes air control layer over thermal control layer, I’m wondering if air tightness should be used when selecting windows. Or, maybe manufacturers targeting high performance building have all figured out air tightness equally well that it’s a moot point? I’m assuming this article is not aimed at comparing Andersen/Marvin/Pella windows with PHI-certified European made windows.
    1. MartinHolladay | | #8
      Entropic,
      For information on airtightness testing of U.S. windows, see this thread in the Q&A section: "Window NFRC ratings and airtightness."
      I invite GBA readers who are familiar with European test protocols for windows to comment on how air leakage testing and reporting is done in Europe.
  6. sukhoi | | #9
    You can buy European (Smartwin) windows made in the Kansas from Advantage Architectural Woodwork. No relation to the company other than buying some windows from them last year, but they do good work.
    1. MartinHolladay | | #10
      Sukhoi,
      Your comment raises many questions.
      1. If Advantage Architectural Woodwork windows are made in Kansas, what makes the windows "European"?
      2. I wonder whether Advantage Architectural Woodwork has gone to the trouble of getting NFRC labels for their windows. I see no mention of NFRC ratings on the company's web site.
      1. sukhoi | | #20
        1. I suppose that's a fair point... they are designed in the EU, I think Bob pays Smartwin (https://www.passivhausfenster.com/en/homeowners/products/smartwin) for the design, but not too sure about the specifics.
        2. No NFRC stickers on the windows I bought, just "passive house certification" and "equivalent" U value - thanks for sharing the issues with that.
        1. user-1020940 | | #25
          I'm using AAW HSHG windows on an EnerPhit project in NE Kansas; Bob gets his IGU's and hardware from the EU. He builds, assembles and finishes the windows in his facility. The AAW facility looks like a CNC shop, but they are milling wood (Hemlock/others) instead of metal. The time, talent and precision he puts into his windows and doors is worldclass. During my CPHT training, we reviewed leading US/EU passive house windows, and his product was the best. We are also using the Warema (www.warema.com) external blinds, sourced through AAW as well. Our PHPP modeling and projected performance outcomes using his windows is outstanding.
  7. Nathan_Kipnis_FAIA | | #13
    I've never understood why window manufacturers use 'U' value and not 'R' value. I've never been given a good answer for this. Wouldn't it be more consistent to keep everything as an 'R' value?
    1. MartinHolladay | | #14
      Nathan,
      U-factor is a technically useful factor -- literally a factor that can be multiplied in certain heat loss calculations. It predates the invention of R-value, which is a marketing term, not a technical term.
      Engineers all prefer U-factor, but insulation manufacturers wanted to invent a number that worked in a "bigger is better" manner. They promoted R-value -- the inverse of U-factor -- so that American shoppers wouldn't have to deal with the "lower numbers are better" confusion.
      More information is available here: "All About U-Factor."
      During the development of the NFRC label, certain window manufacturers were embarrassed that they were selling R-2 or R-3 windows while fiberglass manufacturers were selling R-13 or R-26 batts. The number was small. To avoid comparison with walls, which perform better, they stuck with U-factor.
      In America, it's all about marketing.
      1. Nathan_Kipnis_FAIA | | #17
        That's the first response I've heard that makes sense. I guess the lower score with golfing is a rarity ; )
        MALCOLM TAYLOR | | #18
        Martin,
        Ever tried to convince a customer 24 gauge flashing was better than 29? It may have been marketing, or maybe it was just an acknowledgment of how slow the average consumer is.
  8. dburgoyne | | #15
    Would be interesting to know recommendations for windows in cooling-dominated regions. We have hot summers frequently exceeding 100 degrees F, and our winters rarely get below 30 degrees F. Do the same guidelines apply? Most of the year we are more interested in blocking rather than absorbing solar radiation. Is Low-E glass enough or should we be looking for more?
    1. MartinHolladay | | #16
      D. Burgoyne,
      Low-e glass can either have a low solar heat gain coefficient (SHGC) or a high solar heat gain coefficient. You're looking for a window with a low SHGC, so low-e is no guarantee for your climate.
      For more information, see "All About Glazing Options."
  9. rwsac | | #19
    A couple other items of which to be aware: We did a project in Ohio with European windows that did not have an NFRC rating. The Plans examiner would not accept any calculations for the energy code compliance using converted European U Values, which I understand for the reasons in the article. We had to use code default U values of .55 for our triple pane windows. (This is the default for double pane, there is no code default for triple pane.) We were still able to pass the energy code, because the overall U of the envelope was still ok. There are some European manufacturers that have gone through the NFRC process, I think it is worth it to use one of them. Secondly, many European windows do not come with an etched safety glazing mark. This can also be an item of contention for inspectors and examiners. Make sure to get backup information from the manufacturer regarding the safety testing performed. Often, European safety windows are laminated rather than tempered, which is actually safer in my opinion, but many inspectors are only used to seeing tempered units and take some convincing to accept laminated.
  10. user-1072251 | | #21
    My understanding is that several American window manufacturers buy the European Tilt Turn frames and hardware from European companies with warehouses in North America, assemble the windows and install the glass. Best of both worlds; great European windows made in America.
  11. [email protected] | | #22
    Great article Martin!! I have read through it several times, and really enjoyed the read. Also some really good questions and answers to backup the original blog. Obviously a subject that I have a great deal of interest in, and some knowledge of...
    I think something that is semi-overlooked, but brought up in the blog, and by default is kind of a given, is that when people talk about "European windows" they are referring to tilt/turns. The terms European Window and tilt/turn have become synonymous in many (if not most) discussions about windows from either side of the pond,.
    One aspect of comparisons of the tilt/turn style window to US window companies is that it's a comparison of a single style to companies who might offer a half-dozen (or more) different style windows with several different lines of different quality and affordability levels. And yes, double hungs are much less efficient than are tilt/turns from Europe...and also tilt/turns from US or Canadian manufacturers as well.
    There are tilt/turns manufactured in North America that are every bit as good as units from Europe. As mentioned previously, the North American built tilt/turns use European hardware and often, if vinyl (not saying uPVC is intentional), then it's common that the PVC lineals come from Europe as well, but not always.
    If you buy a tilt/turn window then the hardware in that window probably(?)* comes from Germany or German owned companies no matter if the finished window comes from Canada, Poland, US, Czech, Belarus, Austria, or Germany.
    *It's possible (maybe likely?) that all tilt/turn hardware comes from Germany (or at least German-owned), it used to be that way, and I have heard it still is, but being retired I haven't paid attention recently, so it's possible that there are now other suppliers for tilt/turn hardware that aren't German. And for the record I ignore Chinese suppliers of windows, glass, hardware, etc. when making broad statements about windows, glass, hardware, etc.
    Companies building tilt/turns in North America are a split of local companies and European companies with factories or subsidiaries on this side of the pond. And while these companies all use Euro hardware, and often vinyl lineals from Europe, they almost always are using glass from Cardinal, Guardian, or Vitro in their windows. In the case of Cardinal, IG's as well.
    As Martin pointed out, European window companies and their advocates point out the superiority of Euro windows energy performance by publishing center of glass and not whole window U factor. By definition center of glass is the entire glass area outside of 2 1/2" from the edge, which is edge of glass. Center of glass is valuable when comparing glass package performance to glass package performance and should never be used for discussing window performance.
    In addition, Europeans use glass-only visible transmittance and SHGC while NFRC is a whole window performance scale, and since whole window includes frame, the euro windows have apparently significantly better performance data in those areas as well.
    I do know of at least one US tilt/turn manufacturer called LuxView who uses Guardian's Ultra Clear low iron glass in their windows. This is a high end / luxury level window company and looks it.
    Pertaining to safety concerns, laminated glass is more widely used in Europe for home safety glazing applications, but you might need to be careful with a direct comparison because European and North American laminating standards are slightly different in that Europeans typically use .38mm (.015") thick as go-to for safety glass, while US manufacturers use .76mm (.030").
    Using .38mm in North America is acceptable in glass smaller than 9 sqft meets code as a category 1 product, but anything over 9 sqft has to use .76mm to meet cat 2 requirements.
    1. tdbaugha | | #24
      It appears to me that Luxview is using rebranded Reynaers SL38 line, just like Kolbe Vistalux AL is. European extrusions and hardware. Most likely getting their IGUs from Garibaldi who to my knowledge is the only North American mfg making similarly large IGUs as compared to European offerings. Garibaldi uses Guardian glass…
      Another thing, the “best” center of glass Garibaldi offers in their “standard” triple glazed IGU is 0.123. That’s two double silver low e coated surfaces. I did not ask about their low iron offerings since the price was already over $50/sqft for just the glass. Any more layers of silver or additional surfaces with low e starts to push the VT too low for my liking.
  12. [email protected] | | #23
    "...safety windows are laminated rather than tempered, which is actually safer in my opinion, but many inspectors are only used to seeing tempered units and take some convincing to accept laminated."
    Prior to my retirement I dealt with building code folks a fair bit on safety glass, and laminated glass versus tempered glass was something I had to deal with a number of times. I don't know how often I heard "it has to say tempered to be safety glass", when in fact the word "tempered" isn't actually required as part of the safety logo, but that's a different topic.
    Worse was when the laminated glass was impact rated (which technically isn't a thing, but we still called it that), and it's even many times stronger than regular laminated glass, but inspectors would sometimes still insist on seeing "tempered glass" in the logo, having no idea what they were actually dealing with.
  13. NoelScott | | #26
    I am an Irish contractor , based north of Boston. When I visit my family in Ireland , I am perpetually impressed by the quality of the windows in their homes . As such, I consistently urge clients to consider European windows , with modest success. I source European windows and doors from OKO windows , who are conveniently located. Aside from technical details, I respect the quality of construction , functionality and the locking mechanisms.