Building Science

The Most Neglected Part of HVAC Design

Good HVAC design doesn't start at the beginning—it starts at the end

Placement and sizing of supply registers is critical to occupant comfort. ACCA Manual T explains how to do it properly

My book (A House Needs to Breathe … Or Does It?) has three sections. The two that take up most of the book are on the building enclosure and the mechanical systems. But the one that I lead with is called “Start at the End.” Unfortunately, many people start with what’s right in front of them and don’t think about the results they’re trying to get.

The problem with starting at the beginning

We see it all the time in our HVAC design work at Energy Vanguard. Potential clients tell us they’re looking to get a heating and cooling load calculation so they’ll know what size system to install. But the load calculation is just the first part of the design process. The Air Conditioning Contractors of America (ACCA) has a set of manuals that lay out the whole process. The residential load calculation protocol is in Manual J.

But to determine the proper size of the system, there’s Manual S. And that’s not the end either. You can put in a perfectly sized piece of equipment to do all the heating and cooling, but how does it get distributed? For forced-air equipment, you need a duct system. That’s Manual D.

But wait! There’s more

Ducts designed using Manual D, when applied skillfully, will move the air efficiently and quietly to the rooms where you need heating and cooling. But what if the air goes into one corner of the room and just hangs out there? Or what if you have a vent blowing the air out right on someone sitting at their desk so they’re never comfortable?

These are some of the issues that you solve by applying the most neglected part of HVAC design: selection, sizing, and placement of the inlet and outlet coverings. That’s what ACCA Manual T is for.

T is for termination(?)

Once you get the conditioned air to the room, you’ve got to put it into the room properly. But what does that mean? Here are a few of the things Manual T helps you with:

  • Comfort – This is a result of blowing the air into the right places and not the wrong places.
  • Quiet – Sizing the registers and designing the central return are critical to keep the noise down.
  • Uniformity – By choosing the right type of supply outlet, putting it in the right place, and sizing it for the right velocity, you’ll get good mixing of the conditioned air from the ducts with the air already in the room.
  • Condensation control – Sometimes you need supply air blowing on the windows to reduce the condensation that occurs.
Condensation on the main window
Indoor window condensation can be reduced by blowing heated air across the window

I don’t know if the T in “Manual T” really stands for “termination,” but it makes sense. It’s all about what you do with the end of the supply and return ducts.

  • What part of the room should you put them in?
  • Should they be in the ceiling, wall, or floor?
  • What type should you use?
  • How big should they be?

To answer those questions properly, you need to know Manual T, and you need to dig into the engineering data of the terminations (registers, diffusers, and grilles) you plan to use.

Manual T terminology

There’s a lot of great info in Manual T, and it comes with some new terminology. First, let’s talk about the special components that you put at the end of those supply and return duct runs.

  • Vent – I use this term as a generic word that includes all of the more specific terms below.
  • Supply outlet covering – This includes the various types of terminations you put at the end of supply ducts.
  • Return inlet covering – This is usually just a grille, but it could be one that also has space for a filter. And that would make it a  “filter grille.”
  • Grille – This is just a covering with fixed louvers. The term is used for return inlets and occasionally supply outlets.
  • Register – A grille with adjustable louvers, this is the most common type of supply-outlet covering used in homes.
  • Diffuser – This is a special type of supply-outlet covering made for higher-velocity air. It’s most often used in ceilings and not so often in homes.

There are a bunch of other terms that Manual T throws at you (😁), many of which have to do with airflow patterns. Throw and spread are two important ones, and the diagram below makes it clear what they mean.  If you have a supply vent at the end of a long narrow room, you want a register that will give you good throw. If the register is aiming its air across a short, wide room, you want more spread.

Throw and spread illustrated
Throw and spread illustrated

Some other good terms in Manual T include primary air, secondary air, entrainment, Coanda effect (also called surface effect), and face velocity.

Manual T has the answer to a Manual D misconception

Some HVAC pros have a misunderstanding about the velocity of air moving in ducts. I’ve talked with contractors, installers, and techs who think you’ve got to keep a high air velocity in the duct so you’ll get enough throw once the air enters the room. But it’s not the velocity in the duct that matters. It’s the velocity when it enters the room.

Throw from a supply outlet depends on the covering, not the velocity in the duct
Throw from a supply outlet depends on the covering, not the velocity in the duct

It’s the same principle you use when you’re spraying water from a garden hose and want it to go farther. You put your thumb over the end. That makes the water come out faster and travel farther. Low velocity is perfectly fine inside a duct. In fact, it’s better for airflow because it reduces the resistance felt by the air. Manual D even addresses this issue in an appendix:

There are scores of things to worry about when designing and installing a comfort system. Low velocity through a duct airway is not one of them.

What happens in the real world?

Go into a typical home and take a look at the supply outlets. Installers often like to use a limited number of sizes. The 6-in. by 10-in. supply register seems to be a favorite, at least here in the Atlanta area. The problem with many supply registers is that they’re too big. A larger register means lower velocity and less throw. And that can result in reduced comfort.

You should see already that there’s quite a bit to know about air distribution after the conditioned air comes out of the supply outlets.  Manual T has many of the answers. Even though it’s the oldest and thinnest of the four main HVAC design manuals, it’s just as important as the others.

Even better, ACCA did with Manual T what I did with my book: started at the end. The first chapter is titled “What Makes People Comfortable?” And one of the most important things they say is that you can’t solve comfort problems with mechanical systems alone.  Thermal comfort depends on much more than air temperature. And they discuss the important concept of mean radiant temperature on the second page. Unlike my take on that subject, though, Manual T does NOT include photos of naked people jumping on a bed.

3 great Manual T resources:  The first, of course, is ACCA Manual T itself. The other two are from the HVAC School. One is an article by Matt Bruner, and the other is a podcast with Bryan Orr and Ed Janowiak.


Allison A. Bailes III, PhD, is a speaker, writer, building science consultant, and the founder of Energy Vanguard in Decatur, Georgia.  He has a doctorate in physics and is the author of a bestselling book on building science. He also writes the Energy Vanguard Blog.  For more updates, you can follow Allison on LinkedIn and subscribe to Energy Vanguard’s weekly newsletter and YouTube channel.

5 Comments

  1. charlie_sullivan | | #1

    I think it's worth also noting that the importance of all the Manual T stuff decreases if you have an excellent envelope. With triple-pane low-e, argon windows, R-40 walls, and low air leakage, you wouldn't be able to maintain a significant temperature difference across a room if you tried, so you now longer need to worry about throw and spread.

    1. alexdorf | | #5

      This is my understanding as well.

  2. Piniuze | | #2

    So many times I’ve seen people throw in a system and hope for comfort, without realizing it's not just about the load, it's where and how the air enters the room. I learned the hard way that poor vent placement can ruin a perfectly sized system. Same lesson I learned with customer service, like when I had to find the earthbreeze phone number through https://earthbreeze.pissedconsumer.com/customer-service.html . Comfort (and help!) depends on where things end up, not just where they start.

  3. bvillebound | | #3

    Dear Allison: What a great article - focusing on key issues many people never consider! "Where does the hot/cool air go?"

    When I rebuilt our little beach house, there were lots of these problems to consider. For example: (1) The dining room addition, which had a metal (uninsulated) HVAC pipe running to one register, hanging out in the crawlspace during the very cold winter / hot summer. (2) A room that was once a deck, turned into a '4 season' room with the best windows and views in the house! With NO HVAC duct! This was a refrigerator in winter. (Massachusetts) (3) One supply duct to the bedrooms, with no 'return'. This required lots of changes to ducts and registers, with insulation and air-sealing all around. I also found that insulate flex duct significantly reduces air handler noise, compared to hard metal ducts. So use flex for all straight runs, with metal for all angles/connections. And ALWAYS use metal HVAC tape - NEVER silver fabric 'duct' tape. For example, Nashua foil tape: https://www.homedepot.com/p/Nashua-Tape-1-89-in-x-50-yd-322-Multi-Purpose-HVAC-Foil-Sealer-Duct-Tape-1906075/100030120

    I hope this is helpful

  4. southface | | #4

    Great article!
    A few things I have learned over the years:
    1. Never use the word "vent" without a modifier as it means different things to different people - supply vent, return vent, crawlspace vent, eave vent, ridge vent, flue vent.
    2. @bvillebound, don't use anything but mastic or mastic tape to seal ducts!