GBA Logo horizontal Facebook LinkedIn Email Pinterest Twitter X Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Plus Icon Minus Icon Picture icon Hamburger Icon Close Icon Sorted
Building Science

What Is the Building Leakage Curve?

How a blower-door test can estimate a home's pressure under normal operating conditions

The building leakage curve, a product of a blower-door test, shows expected leakage rates of a structure at specific pressures. We’ll get into how this can be helpful in a bit. Automated blower-door testing using software from a blower-door manufacturer (either Minneapolis Blower Door or Retrotec) will calculate the building leakage curve. Previous generations of the tool required manual inputs and calculations to produce the graph.

The most accurate, and in my opinion, easiest method to create the building leakage curve is by conducting a multipoint blower-door test. This type of blower-door test collects data at several different pressures during the test, as compared to the single-point test, which only collects data at one pressure (usually 50 Pascals). The multipoint tests used with the software are standardized test methods, typically the ANSI/RESNET/ICC 380 standard, or ASTM E779 standard. Both standards, plus ASTM E1827, are accepted by International Residential Code (R402.4.1.2) as air-leakage testing methods. Canadians might use the CGSB testing standard, which also has a multipoint test option. (An interesting footnote to the single vs. multipoint test using the 380 standard is that if you choose to only perform a single-point test for code-compliance blower-door testing, 10% must be added to the final blower-door test result. If the final result is above 2.72 ACH50 and the person performing the test uses a single-point test method, the test fails for areas requiring a maximum of 3 ACH50.)

For this discussion, we will go over the ANSI/RESNET/ICC 380 multipoint airtightness method. The 380 standard requires the multipoint test pressures to be a 10-second average (typically more than 100 data points are collected during the 10 seconds of data recording) of five equally spaced pressure points between 10 and 60 Pascals (Pa). Software I’ve used will take the pressure readings at 10 Pa, 23 Pa, 35…

GBA Prime

This article is only available to GBA Prime Members

Sign up for a free trial and get instant access to this article as well as GBA’s complete library of premium articles and construction details.

Start Free Trial

3 Comments

  1. user-723121 | | #1

    Randy, This is good information, certainly from a safety standpoint when changing anything related to pressures in a home. Did not know about this.

    "(An interesting footnote to the single vs. multipoint test using the 380 standard is that if you choose to only perform a single-point test for code-compliance blower-door testing, 10% must be added to the final blower-door test result. If the final result is above 2.72 ACH50 and the person performing the test uses a single-point test method, the test fails for areas requiring a maximum of 3 ACH50.)

    Will be interesting to watch as Canada adopts their Step Code (by 2030?) and how builders respond to what I understand will ultimately be 1 ACH50 required for new homes. This level of airtightness takes a good bit of effort but is certainly achievable.

    Doug

  2. GBA Editor
    RANDY WILLIAMS | | #2

    Hi Doug, I agree. 1 ACH50 isn't too difficult on a simple design, but when you add a bunch of inside/outside corners and convoluted roofs, that air tightness level becomes much more difficult.

  3. GBA Editor
    MALCOLM TAYLOR | | #3

    Randy,

    Interesting blog - and worth reading in conjunction with your related earlier one on Natural ACH: https://building-performance.org/bpa-journal/ach50-achnat/