2″ Air Gap (consistent) between R-10 Rigid Foam and 2×4 wall w/Roxul

VTLiving | Posted in General Questions on

Hello,

We were anticipating using 4″ of EPS rigid foam around the interior perimeter of our basement wall and then framing an empty 2×4 wall in front of that.  Turns out 4″ of EPS does not (quite) meet the R-20 continuous exterior insulation code (I should connected those dots but didn’t — too many balls in the air), so we are now looking into other options.  The complicating factor is that our contractor put 4″ of foam around our concrete slab, and it sticks up above the concrete in various heights around the perimeter (we were going to foam that gap where the foam pieces came together).   We do not have exterior insulation.

If we go with 2″ of XPS up against the concrete, and then frame our 2×4 wall in the expected location (which also conveniently lines up with the underside of the floor joists) we meet the code a different way.  However, we then have a continuous 2″ gap between our insulated framed walls and the rigid foam board.  I’ve done a lot of looking and most air gap questions are for small sections of wall, so this is a bit different.

One concern I can think of is that the tape for the perimeter foam board might come undone over time, allowing moisture to seep through.  We could push the Roxul batts back up against the rigid foam, leaving only 2″ gaps behind the studs themselves.

I would appreciate any thoughts you might all have about this approach, or if this is setting us up for badness in the future.

We can go with 4″ XPS around the outside, it just is a couple thousand extra dollars which we would like to use elsewhere, but not at the expense of moisture concerns down the road.

Thanks so much!!!

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    BILL WICHERS | | #1

    4" of EPS is going to give you just shy of R17. You might try 3.5" of polyiso, which would give you R22, or you could use a 2" layer of EPS (R8.4) plus a 2" layer of polyiso, which would bring you up to a total of R21.4. My preference would be to not use XPS here, because it's not as green as EPS or polyiso, and it doesn't perform as well as polyiso.

    I would not use batts, rockwool or otherwise, in the framed wall. Batts in basements is always risky, even though your proposed assembly would likely be OK. Note that you can also save some space by framing the wall differently -- you can use 2x3s "on the flat" tight to the rigid foam, then 1.5" deep 4" square electrical boxes for electricals, along with mudrings to bring the devices (receptacles and switches) up flush to the finished drywall surface. It's not necassary to frame a regular 2x4 wall here, since you don't need a structural wall.

    Bill