I’m going to have a blower door test done eventually. Do they have a cheap, repeatable way to block flapper dampers, used to provide makeup air for bathroom fans and a whole house fan during an blower door tests? My house is a bit experimental in using several large ones for the a whole house fan. They will have custom insulated plugs that block them off in winter, so this is more of a general question and not for my house specifically.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Eric,
    The usual way that openings are sealed for a blower-door test is with ordinary 6-mil polyethylene and tape (for example, duct tape).

  2. exeric | | #2

    Thanks Martin