Can an ASHP have higher MBH at 40F than 47F

markmac | Posted in General Questions on

While graphing the MBH of our York heatpump, I noted the table suggests a higher MHB and COP at 40F than 47F.

Is this possible?  I looked at the specs for the 2, 3 and 5 ton and none of those show any increase in MBH as Outside temp decreases.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. relztes | | #1

    I see the higher MBH, but lower COP and higher input power. If the controller boosts the compressor to a higher speed below a certain temperature, I don't see any problem with the numbers.

    Edit: OK, I'm changing my mind. 47 °F for the 4 ton unit is the only condition where input power goes down with increasing indoor temperature. That is awfully weird.

    Plus, it's just a two-stage compressor. There's something about a variable outdoor fan speed, but I don't understand how it could produce that result.

  2. moe_wilensky | | #2

    Id very much defer to someone with an better understanding of what exactly makes a heat pump a Cold Climate Heat Pump, but I think I heard recently that they can be optimized in such a way as to perform (a bit) worse above rated conditions than just under them.

    When I heard this it kind of made sense to me as there’s always trade offs.

    Something to do with vapour injection??..

    1. moe_wilensky | | #3

      (I should mention I did not look at any of the specifics of the heat pump above)

      Edit:

      I did however go and look up vapour injection for fun:

      “This is a technology used to achieve a broader operating temperature range and increase low-ambient temperature efficiency, which refers to how well HVAC systems function in cold climate conditions below typical heat pump operating ranges. A small amount of refrigerant is passed through a separate expansion valve and heat-exchanger before re-injection at warmer temperature back into the compressor. This technology sacrifices some peak efficiency to improve overall average efficiency.”

      From: https://smartenergy.illinois.edu/cold-climate-heat-pumps-work/

  3. markmac | | #4

    It seems odd. Especially when it’s only in the 4-ton unit. None of the other sizes see a jump a sudden increase as outside temp drops. I may contact York for clarification as it could just be incorrect in the table.