I’ve been trying to learn about HRV and ERV systems and have found some payback analyses for larger commercial systems, and am wondering if they ever pay for themselves in a single family house with ~22,000 cuft living space (including the finished portion of the basement), or if it would be cheaper to just run a small ventilation fan occasionally, or crack a window?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. MartinHolladay | | #1

    Artisan,
    The answer can be found in my article, "Are HRVs Cost-Effective?"

    1. artisanfarms | | #2

      Thanks for the link.

  2. Expert Member
    Michael Maines | | #3

    A Pretty Good House is relatively airtight--ideally no more than 1-2 ACH50, so mechanical ventilation is required--both by most building codes and by common sense. The question is whether you need balanced ventilation, exhaust-only, or supply-only. Ten years of crowd-sourcing information and opinions for what makes a PGH says that balanced ventilation is required, whether or not it has an attractive payback period.

    While exhaust-only ventilation systems can work, they also depressurize the home's interior, leading to things like increased radon infiltration, makeup air entering through random gaps and cracks rather than through a known filtration system, water infiltration and backdrafting of combustion equipment. There are work-arounds to all of those, but with what we now know about the importance of indoor air quality, and the availability of many good balanced ventilation options, if you're building a Pretty Good House, you should include an ERV or HRV, even if it's not the most cost-effective option.

    1. artisanfarms | | #5

      I'm not trying to be difficult, but what's wrong with cracking a window and running a small exhaust fan when you're in the house vs. spending thousands for a HRV or ERV?

      1. Expert Member
        Joshua Salinger | | #8

        An E/HRV has a number of functions. Building durability is one of the most important. By balancing the pressures between indoors and out, it reduces in/exfiltration of moist air into the assemblies. This can lead to moisture build up and biological growth-- which is a health issue. It also filters the air, which opening a window can't do. If there is high pollen, uncomfortable temps, noise, high/low humidity, rain/snow nearby traffic, etc., cracking a window is not helpful. This is also a health issue. Running an exhaust fan with an open window causes infiltration, poor comfort and energy losses. E/HRV's can also take stale air from 'dirty' places such as kitchens and baths and supply fresh air to living and bedroom areas where the people are. Opening a window is random ventilation, a balanced ventilation system is a strategic ventilation strategy. The short answer is that an E/HRV should not be, first and foremost, an economic return question, rather a durability, health and comfort concern. For instance, I have a son who has bad allergies. I couldn't care less about how quick the ROI of my economic investment is. Everyone has different but equally important issues and one needs to view the E/HRV question through this lens vs. just an economic one.

  3. walta100 | | #4

    My opinion is maybe in zone 6 & 7 where you will see very differentials between the indoor maybe 100° at times then yes, I think a dollar return on investment is possible.

    In zones 1 & 2 absolutely no way to see a dollar return on investment with a 30° differential.

    Walta

  4. Expert Member
    Akos | | #6

    The math on this is pretty easy.

    For example, I'm at 7200 heating degree days. A typical house will need around 100CFM of ventilation.

    Exhaust only ventilation the cost of providing this is:
    7200 HDD *24 hours * 100CFM * 1.08 (btu/cfm)=186 Therms.

    With an 80% efficient HRV/ERV that drops to:

    7200 HDD *24 hours * 100CFM * 1.08 (btu/cfm) *(1 - 80%)=37 Therms.

    So it definitely saves a fair bit of energy, even when heating with a heat pump, that adds up.

    The question is does a $20k ERV setup make sense? I would have a hard time justifying that, ROI is pretty much never. There are some ancillary benefits to a fancy ERV, so for some that might be worth the cost.

    Instead of a top of the line install, getting a higher efficiency ERV installed using simplified or hybrid ducting to the air handler return should be a reasonable ROI in colder climates.

  5. Walterwilkinson | | #7

    An HRV or ERV can pay for itself in a well-insulated, energy-efficient house by improving air quality while reducing heating and cooling costs. However, the payback period depends on factors like your climate, energy rates, and usage. For a house with 22,000 cuft of living space, these systems can be more cost-effective than relying on a small ventilation fan or opening windows, which may lead to heat loss or increased energy consumption. For managing your finances while considering home upgrades, check out https://thecashappapk.com/cash-app-apk-for-ios/, a great alternative to PayPal and Payoneer for saving and managing digital currency, including crypto.