Duct Insulation in a Conditioned Attic

garet_denise | Posted in Mechanicals on

We’re planning to build a new 2,200sf house in Phoenix, climate zone 2B. The single story flat roof will have 1″ spray foam roofing on top and 10″ of open-cell foam underneath. A conventional air-source heat pump will be located in an interior, conditioned mechanical room. Ductwork will all be within the open-web truss cavity between the ceiling and roof-deck insulation.

Since the ductwork will be completely within the thermal envelope, I don’t see a benefit to installing duct insulation. But the architect is insisting on R6 duct insulation w/ vapor barrier facing.

Questions:
1) Is duct insulation needed?
2) Would duct insulation in this circumstance provide a benefit?
3) Is condensation on uninsulated ducts likely to be an issue in this climate?

Since the IEEC minimum ceiling insulation requirements will go up to R49 in the next code cycle, it seems like it would make more sense to spend money on additional roof-deck insulation rather than duct insulation.

One related question:
4) The specs also say that exhaust ducts “shall not be” insulated. Why? Since the exhaust damper will be at the fan, the air inside the exhaust duct will basically be “outside” air. It seems like we would want insulation between that and the conditioned ceiling cavity.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. garet_denise | | #1

    Bump - Anyone?

  2. walta100 | | #2

    The way I see it insulating ductwork in a conditioned space is cheap insurance against water damage. Understand this insulation will not lower your operating costs or improve your comfort.

    What it may do is prevent water from condensing on the ductwork from dripping on your drywall and staining the ceiling.

    It seems to me condensation is not much of a problem Phoenix.

    You are paying for expert advice hopefully better than free internet advice. LOL I say ask the architect to explain the choice to you and listen to his answer. If the answers is something like that how we always do it ask him to try again. I think it would be a mistake to overrule the architect.

    Walta

  3. user-2310254 | | #3

    Just make sure the truss openings are big enough for the ducts you need to use. Sometimes it's better to use a plenum truss.