Latest Science on Asphalt Roof Underlayment with spray foam under decking
![](https://secure.gravatar.com/avatar/13190394b7dcaa4efb7a2a17c73c6b6e?s=52&d=https%3A%2F%2Fimages.greenbuildingadvisor.com%2Fapp%2Favatars%2F200x200%2Fm.png&r=g)
Hello all,
Getting ready to pull the trigger on some home energy upgrades and want to check with experts on products to use to ensure a durable outcome.
Climate zone 5. Syracuse, NY.
Going to use 2lb closed cell spray foam on underside of roof decking at 4”.
Going to replace the roof/asphalt shingles/repair decking prior to the spray foam.
Question 1: what is the best product I can use as an underlayment for the shingles? Multiple products suggested?
Question 2: should I replace existing sheathing along the ridge to close up existing ridge vent?
Question 3: any other best practices I should be aware of?
Thank you in advance,
Matt
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb1.png)
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb2.png)
Replies
Matt,
1. With closed cell foam directly under the sheathing, a permeable synthetic sheet underlay will give you a bit of drying though the shingles. I'm sorry - I can't make a specific recommendation as I have always used impermeable ones.
2. Yes. Although if the gap is very small you can probably get away with just covering it with the cap shingles.
3. Use drip-edge flashing on both the eaves and rakes.
Thanks Malcolm!
Will this be your only roof insulation? Despite what spray foam salespeople tell you regarding R-value, over time it will drop to around R-5.6/in, so a 4" layer is really R-22.4, a little more than a 6" fiberglass batt. You can boost the performance by using a flash-and-batt or flash-and-fill approach. In climate zone 5, current codes require R-60, but I would aim for at least R-38.
Closed cell foam often separates from the framing, leaving a gap directly from interior to exterior, which will lead to condensation at the sheathing and eventually rot. I don't recommend relying on spray foam to be a perfect air and vapor barrier.
Closed cell foam sometimes doesn't cure properly, leading to horrible situations for the homeowner. Those cases are rare but common enough that I avoid foam when possible.
Asphalt shingles are impervious to water vapor so having a permeable underlayment has no benefit. The important thing is to have a waterproof underlayment.
Mike,
Really trying to find a balance in what isn’t going to be our “forever home”.
House needs a new roof, new siding. As it stands now, leaky as a could be 1961 built split level colonial.
Original plan was for rigid insulation above the roof deck. Engineer poo-pooed it with the current 2x6 roof rafters 16” on center without sistering all 200+ of them. He thumbs upped spray foam without any modifications.
In a further attempt to save weight and create a more durable end state, now leaning towards a metal roof with sharkskin vented underlayment on top of sheathing.
Seems to me batts with the sistered joists would be a PITA to install w/ a ton of waste. Do you disagree?