Low slope roof options with I-Joists

Chris_in_NC | Posted in General Questions on

Planning a garage/shop, looking for options if part of the roof is 2:12 monopitch with i-joists.  CZ3a.  Design phase; I have not boxed myself into any corners…yet.  Metal roof, standing seam.  I can abandon the 2:12 idea if needed, but it does solve some wall height problems.

Looking at the span tables, 11 7/8″ I-joists should be no problem. With R-38 high density fiberglass batts (10.25″?), that only leaves 1 5/8″ for venting (not including any vent chute thickness), which sounds risky for 2:12 pitch.

Bumping up to a 14″ I-joist is an option for additional venting (no structural need), would then be 3.5″ baffle with a R-38 fiberglass batt.  Making/installing a deeper baffle (that attaches somewhere other than the 1.5 inch flange) seems like a lot of work.  Probably not much price difference between 11 7/8 and 14 inch from the same series, but does weigh more when I’m wrangling them into position, and there will be a change in wall or ceiling height obviously.

Are either of those vented options feasible?  The low-slope vent gap recommendations are all over the place for depth, and most don’t mention whether the recommendations include a baffle (some imply the insulation is open to the vent cavity).

I know I could do un-vented, but that seems like an expensive way to address a very simple roof plane if there’s a vented option.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    MALCOLM TAYLOR | | #1

    Chris,

    From Martin's article https://www.greenbuildingadvisor.com/article/insulating-low-slope-residential-roofs
    "What’s a low-slope roof? It’s a roof that is flat or almost flat. While some sources define a low-slope roof as one with a pitch that is less than 3 in 12, ASTM (in Standard E 1918-97) defines a low-slope roof as one that has a pitch that is less than 2 in 12."

    3/12 is more forgiving, but my take is that in most climates, with good interior air-barrier with few penetrations, you should have no problems going to 2/12 with the shallower I-joists - especially for a building where the interior humidity should be lower than in a house.

  2. Chris_in_NC | | #2

    Sounds good, thanks. I may opt for the 14 inch if I can ignore the wall height, as it occurred to me that I could move to 24 inch OC if I did that (I can't go 24 OC with the 11 7/8, and I don't want to mess with insulating a 19.2 inch OC or whatever that actually is).

    1. Expert Member
      MALCOLM TAYLOR | | #3

      Chris,

      A deeper vent space moves it into the roof assemblies I'd categorize as risk-free.