I have tried several free software packages to calculate the heat load of my 3,100 sq ft home near Boulder Colorado. The numbers from the software (and websites) all vary a lot. So I started thinking why not measure the actual load?
My design heating temperature is 0°F for my area. My gas furnace is 98.7% efficient.
This coming winter when our temperature will drop to 0°F for at least a few hours during the night why not measure the therms used during those hours to keep my house warm and then subtract the 1.3% because my furnace is not 100% efficient?
For instance if the temp is a 0°F outside between the hours of 1AM – 3AM (no solar heat gain) and I measure 1.5 therms during those hours:
1.5 therms X .987 = 1.4805 therms (Furnace efficiency)
1.4805 is 148,014.659 BTU
148,014.6 BTU / 2 hours = 74,007 BTU Heat Load
Does that seem right?
GBA Detail Library
A collection of one thousand construction details organized by climate and house part
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb1.png)
![](https://www.greenbuildingadvisor.com/app/themes/greenbuildingadvisor/dist/img/modules/detail-library/thumb2.png)
Replies
That's exactly right but you don't need to wait until the coldest morning of this winter if you have last winter's data.
https://www.greenbuildingadvisor.com/article/out-with-the-old-in-with-the-new
From there, you can add a heat pump and gain some real efficiency!
Paul thanks for the link to that article.
I collected lots of hourly data for months. A linear fit to outdoor temp vs furnace on-time using a few weeks of night (no solar gain, wind should average out) values should provide a more accurate design day heat load than a monthly fuel use derived value.
I expect much less data would be more accurate than the typical Manual J. So for new construction, temporary electric heaters for a few nights might be a viable Man J alternative.