Seeking Guidance on Heating Options for 1890s Farmhouse Renovation
I’m in the process of renovating a gutted 1890s farmhouse and need advice on heating options. Initially we planned to use ducted mini-splits, but we’ve heard concerns about their performance during extremely cold days and potential challenges with generator compatibility (power outages are occasional in our area).
We’re now considering hydronic baseboards but this would shift us toward relying on propane – and make furniture placement more tricky.
Our goal was to make the house primarily electric to transition to solar in the future. Additionally, if we go with hydronic baseboards, we would likely need to add ductless mini-splits for air conditioning at some point.
On the plus, side if we go with hydronic baseboards – we would get a nice Navien combi boiler with on-demand hot water.
Could you outline which option would be safer (the house is for an elderly couple), more efficient (it will be insulated mainly with Rockwool), and environmentally friendly? We keep going back and forth on this decision.
Any advice would be greatly appreciated!
My opinion hydronic heating is a poor fit for your long-term goals.
In that fueling a hydronic distribution from an electric source leaves you with few good options. One an electric resistance boiler the are very expensive to operate. Two an air to water heat pump that is a rare emerging technology that is poorly supported and overpriced. Three ground source to water heat pump generally the install costs are so high that they never pay off.
The other problem with hydronic is that a separate cooling system is required that doubles your HVAC budget on top of the perineum price tag hydronic systems command.
I say make this a tight well insulated house with a good air to air heat pump.
The sad thing is if you made a detailed list of all your planed improvements with a budget number for each it would be less expensive to bulldoze the foundation and rebuild something that looks the same that will be more energy efficient than the retrofit ever could hope to be.
I think propane is the most expensive possible way to heat a home
“ I think propane is the most expensive possible way to heat a home”
This is very dependent on where you are located and not necessarily true. For example, in CA the cost of a gal of propane right now is 2.57. The cost of a khw is about $.36.
For a heat pump with a cop of 3, that works out to about 28353 btu/$1.
For propane, assuming .95 efficiency boiler, you get 33822 btu/$1
The worst thing about propane is that it is total unregulated by most state governments unlike natural gas, and electricity where prices are fixed by regulation. Should supply and or demand change tomorrow, the price of propane could easily exceed $7.00 a gallon again in a matter of days.
Who owns the tank also changes the price per gallon a lot. If you own the tank you can shop for the best price. If a supplier provides a “free” tank you pay whatever they chouse to charge or freeze to death.
Yes this is probably true and I don't think propane is a good long term solution to our energy needs. But until we all have solar or fusion energy is realized, It is not as bad as it gets made to be from a financial perspective. Also considering 60% of grid energy is from fossil fuels and there are aprox 30% energy loss from generation to house hold I think it is also not as bad in regard to carbon emission.
Also even if it goes to $7 a gallon it will still be cheaper than resistance electric in the above scenario as you will lose that 3 cop.
Thanks Walta. I hadn't considered either air to air or air to water. I was thinking that if we went with the hydronic baseboard, it would be propane. I'm going to look into it, appreciate the feedback.
If you took what I said as a recommendation for air to water or ground to water heat pump systems, I totally failed in my post.
I would do both. In rural areas (and really any cold climate) I think it’s worth the peace of mind to have multiple heating options in case of power failure. I have used a navien in conjunction with wall radiators and it worked great. It will definitely add upfront cost, though the combi gets you a pretty good deal considering it also does dhw. As far as the mini split goes, you could then either size it for cooling and still use it in a heating environment by just setting its thermostat higher than your hydronic so that it is basically always running and the hydronic kicks in as supplemental.
With the navien system its zone controller annoyingly does not supply 24v to the thermostats so you need to run a standard 4 wire thermostat cable and splice into a 24v transformer. They sell them specifically for this but it’s just annoying if that is not identified at time of rough in wires. Or else you can get a battery thermostat but that is annoying with today’s smart thermostats.
As far as cost to run, depending on your gas and electric cost the differential is not that great, it has more to do with reducing greenhouse gas emissions, and depending on your utility, it may be the same at the current time.
Thanks for the advice. That's a great idea, we're in the northeast so it makes sense to do both. I have a Navien combi for my radiant floor & water and it's great. The old farmhouse reno is for an elderly couple and we want to make sure that it's safe for them, environmentally responsible, but also so that they don't have to worry about losing heat during a power outage. They want to convert to solar ultimately but it would gives us peace of mind to have some backup/propane in the meantime.
You don't mention the location or climate zone, which would improve the responses quite a bit. ;)
If you are running ductwork (I'm assuming there was no original ductwork, maybe https://rheiacomfort.com/ would be helpful?), then I'd consider something like a Mitsubishi Intelliheat dual fuel air-to-air heatpump. You can use their hyperheat outdoor units (MKZ series), combined with a small gas furnace (I think these can be jetted for propane, but haven't confirmed that). They will run as a heatpump in virtually all conditions, but can light up the gas furnace in low temperatures or manually if you were running on generator. They can be set for economic cutover, which would maybe be in 30F sort of range with your quoted propane prices, or capacity cutover, which would be more in the 0F range.
That would let you heat and cool from the more efficient heatpump, but have gas/propane backup if you really deem it necessary.
They hydronic baseboards really feel like you'd be painting yourself into a corner for future options. Propane is cheap now but won't always be, and there just aren't a lot of other US options for that system now.
Good point! The build is in zone 6a, Damascus PA.
Interesting, I don't know there are dual fuel air-to-air heatpump. I'm going to dig into it a bit more but sounds like they can do aircon as well which is a bonus. The house is completely gutted so we're at a point where we can add ductwork and run anything it through the attic and crawl space.
It seems like the best option for us is to have two sources - one more sustainable (air to air, air to water, electric) as well as a secondary or backup gas/propane.
Thanks for the suggestion!
I’m currently sitting in an 1800’s farmhouse of my own. It’s -3 outside at the moment, and our mini splits are keeping things a balmy 68. I put in baseboard resistance heaters also for an emergency backup, and have only run them one time when it dropped to -23. And even then, they were only a supplement.
Sounds good, thanks!
I have a basic 1980 house (1500 sq ft main floor and 1200 sq ft finished basement) in zone 5 with oil boiler and baseboard. I just stuck three one ton Fujitsu hyper heat mini splits in: two in the main living/dining/kitchen area and one in the finished basement. The bedrooms get heat down the hallway from the main rooms as we do not close our bedroom door. I did a little air sealing in the attic and added some insulation, but otherwise it is a standard 1980's era house. I keep the mini splits blasting all winter and the oil baseboard occassionally kicks on to heat the bedrooms when the temps drop below 5F or so. I also installed a heat pump hot water heater. My oil usage went from around 700-800 gallons a year to 100 or so gallons this year. Meanwhile I estimate I used 9,000 -10,000 kwh of additional electricity at 11 cents a kwh for heat and hot water.
The problem with all electric heat is that you will lose electricity in winter storms. The electric grid in the North East will get worse before it gets better and if we end up in a trade war with Canada and they cut off cheap electricity from Hydro Quebec, the cost will go way up. So you need a back up. Propane is a good choice if you also include a propane generator as your back up. Eventually battery back up will be a good choice but that seems too expensive at this point.
It is unfortunate that high quality mini splits are overpriced in the US if installed by an HVAC guy. I got quotes for $5-6,000 per unit and that did not include the 240v electric lines that would need to be installed. So instead, I purchased my own units for $2,200 each (including all lines, surge protector, brackets and electrical) and installed them myself (about 6-8 hours each including 240v electrical lines). I then paid $100 each to have a licensed HVAC neighbor to charge them up. If I had to hire professional HVAC and electricians to do the entire install, the cost would have been over $18,000 for the three units. The DIY units sold by Mr Cool, Perfect Aire and Blue Ridge are relatively easy to install but not as efficient in heating mode and not rated as low temperature. And you still need to run a 240 V electric line.
It's unlikely battery systems will be economical as a long-term backup power source in the near future, if ever. There just isn't enough energy storage available at reasonable cost. You'd be much better off with a generator for backup power if you expect outages of extended duration (more than a few hours or so). If you already have a heating oil system, you would be well served with a diesel generator which would likely run on the same fuel -- much of the time, what is sold as "heating oil" is just dyed (what is often called "off road") diesel fuel. Your fuel supplier will be able to tell you for sure what you have.
The downside to a diesel generator is they tend to be expensive. Propane generators need a very large propane tank to operate properly, so they aren't likely to be a good choice unless you already have a propane system in place. The nice part is that most natural gas fueled generators can be easily converted to run on propane, so you can use a "normal" residential standby generator system.
The last option would be a gasoline fueled generator. Most of those are portable units, so I'd recommend installing a "power inlet" if you go that route, which will greatly simplify connecting and using the generator when you need it (and it's much safer too!).
BTW, I doubt we'll see power shutoffs even if something does happen with Canada and the tarriffs. It's not easy for them (or us) to just "shut off" those large electric interconnections, since they are involved with system stability on both sides of the border. The US often provides power to Canada too, during system emergencies (i.e. something big on their side breaks, we send power to help them out while they fix it), or just for general operational reasons. Severing those connections would "island" the grid on either side of the border, which is a problem because they are supposed to be a single, synchronous, system. My guess here is that electric transfers would be exempted from any tarriffs due to the operational issues ON BOTH SIDES that would occur if those connections were to be interrupted. Even if the connection to Hydro Quebec that brings in cheap hydro power to the Northeast were to be shut down, there is capacity on the US side to deal with that, and I doubt you'd see significant price increases in the near term.
Thanks. I will look into a diesel generator. I am a little concerned that they are more likely to break down or fail to start if not used regularly. Also, diesel seems to produce too much pollution. Almost eveyone here has propane. I think the original poster does not have oil or propane so he can choose between the two.
Diesel generators are usually the most reliable, and tend to last MUCH longer than natural gas or gasoline generators. They don't like to be cold though, so you would want to look into a block heater to keep the unit warm during the winter for easier starting. Most permanently installed diesel generators will ship standard with a block heater (which is usually installed in the cooling system for the unit), otherwise Kim Hotstart units work well for the smaller generators you're likely to need for residential use (note that for me "big" generators are over a megawatt, because I mostly do commercial work :-)
Diesel generators are the most efficient in terms of converting fuel energy into electrical energy. This is especially true at lighter loads (less than 50% or so), where diesel generators may be around twice as efficient. Diesel doesn't produce more pollution here, since these are constant speed engines -- you might get a bit of soot in the exhaust when it starts, but then it's up to speed and runs pretty well. It's very different from the sooty black clouds you see from large trucks when they accelerate from a stop.
If you have natural gas or propane available, you will have lower emissions burning either of those types of fuels. The issue is that if you already have diesel fuel available, then diesel fuel is likely your best choice since you wouldn't need to install a new fuel system in that case.
Bill, do they make a block heater for a diesel unit that works off a 12 volt battery..... since I am assuming that I will need to use this when the electricity is already down?