Timberframe exterior enclosure with rigid foam

zachak | Posted in Energy Efficiency and Durability on

I have a timberframe shop under construction and need to finalize exterior insulation.

I’m in Southeast Alaska—technically Zone 7—but realistically much more like a Marine 4C of Seattle, Washington, just a little colder and a fair bit wetter.  Moisture is my biggest concern in a design.  Siding will get wet, even with 3′ overhangs.

For aesthetic reasons, I (and my customer) really don’t want to infill, even if it’s just part way in to the timber plane.

I’ve struggled with the most efficient way to build fairly efficient walls to the exterior of the timber plane.  2Xs can run top to bottom from plate beam to floor beam.  With wraparound porches, a deck ledger also needs to be incorporated.

I assume there needs to be at least a single layer of plywood with WRB, but we’ve also played with the design of plywood on both sides of the wall.  OSB just doesn’t stand up in our very wet maritime climate.

Walls don’t need to be super-insulated…this is a shop that will be unheated most of the year, with a wood stove as the sole source of heat off and on in the later fall through spring.  I was hoping for at least 3″ to 4 1/2″ of rigid insulation.

Customer already has red cedar vertical board and batten siding on hand, which makes it all a bit more difficult for drainage planes, but siding will be firred out for ventilation.

The good news is that the area has plenty of wind, which dries wood quickly, even moisture behind siding.  My own house has old growth board and batten siding over 100 years old with tar paper directly behind, and it’s still in good shape.

Below is our best effort at a partial infill design…but again, aesthetics are sure hoping for a fully exterior solution.

Any thoughts or schematics are MUCH appreciated.

Thank you.

Zach

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    Akos | | #1

    If you are installing sheathing, I would put the studs in normal direction. No point in grits, simpler to build on the ground and stand up a wall section. The exterior rigid option only needs 1 wrb, either under the rigid or over the rigid both works. With outie windows, the simples is over the rigid.

    The key to energy efficiency of these types of structures is air sealing, if the wind is not blowing through it, it doesn't take that much to quickly heat it up. Since you have sheathing, taping the seams there is the best place as it is not interrupted by the post and beams.

    1. zachak | | #2

      Thanks Akos.

      My apologies for not responding sooner...my notifications weren't getting through.

      Good points. Much appreciated. Still a lot for me to digest to make sure all is correct before building.