shemmy | Posted in General Questions on

I’ve got a currently vented attic at my house (soffits + ridge vent).  Part of my attic is already finished by the builder, and there’s a door that leads to flat decking that’s already been insulated and air sealed into the unconditioned space.  The problem is, I have 2 hvac units here unfortunately – a heap pump for the 3rd floor space, and and a “standard” unit gas/ac unit feeding by 2nd floor space.  But yeah, they are both in the unconditioned vented attic sitting on some decking.  Since it’s already decked, I would like to be able to store a few things here as well.

The sloped sides of the roof here have an LP TechShield radiant barrier already.  This area faces North/South respectivly (top = north, bottom = south in the attachmet). The temp range was somewhere around 35 – 100-ish throughout the year, humidity all over the place as I’m in zone 4 (middle of NC).

I had the builder recommend someone to put in some insulation in the attic, and they did put r30 rockwool batts along the roof rafters after installing baffles that terminate up near the ridge. R30 is also along the ceiling plane at 9′, which is relatively narrow.  There’s still probaby a good 3-4′ of air to the ridge vent above this.  And they put r15 rockwool in the end-wall near the window.  See drawing for reference.  

I’ve watched this space for the last year after its been insulated, and it never really gets below I’d say 55 degrees (i keep temp/humidity/dew point sensors here with hard data), but it’s certainly not air sealed since it’s just batts in place.  The humidity is very well controlled in this area.  I think the hvacs here are marginally leaky, keeping it warm-ish in the winter (55-63-ish).  I also have a ventilating dehumidifier in this space connected to the 2nd floor AC unit, so that’s probably helping.

Anyway, the question I’ve mostly been concerned about is condensation.  It gets down sometimes to 10-15 farenheight here in the winter occasionally at night, even though the average temp in winter is somewhere around 38-40.  I’ve seen no evidence of condensation inside my little insulated bubble, but it’s hard to tell what’s happening outside or in the actual osb sheathing under my roof given the temp delta between inside my insulation bubble and outside it.  It is somewhat difficult to air seal this area due to all the ducting in the area.  

Roof is asphalt shingle with underlayment and then osb + radiant barrier.  From there, it’s 2×8 rafters on the interior.

Thoughts/concerns?

Blue = finished space
Pink = space insulated with r30 rockwool along roofline (with baffles) and r15 wall

The only reason I started thinking about this was I was showering one day and noticed condensation on my mirror.  Totally unrelated to my attic insulation per-se, but for whatever reason, I started thinking about the insulation I added last fall, and here we are!  Brains work in mysterious ways.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    BILL WICHERS | | #1

    If moisture gets up there, it will condense out onto any surfaces that are below the dew point. There is nothing you can really do about that, aside from conditioning the space. If you want to improve energy efficiency AND eliminate any condensation concerns, look into finishing your partially conditioned attic project by insulating the rafters up to code. You can do this with polyiso under the rafters, since you already have vent channels and mineral wool between the rafters. That's not the only way, but it's my preferred option. You then drywall over the polyiso.

    I'm guessing things are already built here, but those soffit vents should ideally be all the way out at the edge of the soffit, right up next to the fascia board. Having the soffit vent in the middle of the soffit is not idea, because you want that vent out as far away from the side of the house as possible so that it draws in the coolest possible air.

    Bill

  2. walta100 | | #2

    Understand what you have built is not code compliant and risky.

    You may get away with your semi conditioned attic. There is no way to predict when or if the wrong set of weather conditions will happen and make it rain in your attic.

    Walta

    1. shemmy | | #3

      What recommendations would you have for me to fix it? From my reading, an air and vapor retarder on the inside (warm side) could possibly address the air and vapor transmission? I wasn't looking to fully finish it with drywall and paint exactly (and that might be harder than I imagine due to the ducting).