What makes more sense, insulating crawl space vs. under the floor?

imzjustplayin | Posted in Green Building Techniques on

According to this page:http://energy.gov/energysaver/articles/where-insulate-home
there are about 3 ways of insulating the bottom of a house… If the house is built on grade, you insulate the sides of the slab and possibly underneath the slab.
If the house is built so that there is a crawl space, the crawl space can be of the ventilated type where the underfloor of the house is insulated with fiberglass batts or spray foam.
The final way is to make the crawl space into an unventilated crawl space, i.e. a “conditioned space” place a plastic sheets all around, make provisions for drainage around the foundation, either outside or inside for excess moisture, seal off everything, then have a light duty ventilation system for Radon, then insulate the foundation walls instead of insulating under the floor. The primary benefit of this supposedly is that you can use much more insulation around the foundation walls, and get more of the house envelop insulated for lower cost vs. just between the joists in the house.

So I guess my question is, the idea of turning the crawlspace into a “conditioned space”, is that really better than insulating underneath the floor, between the joists? I live in Northern California (SF Bay area) and the ground temperature isn’t all that warm, if anything a bit chilly. So if I insulate the foundation but not the ground itself, turning the crawlspace into a conditioned space, wouldn’t the cold from the earth seep into the house, making the house cold? Yes there is a plastic sheet so there shouldn’t be any air movement and while I should really being looking at this from the perspective that it’s the heat that is moving to a cold space, not the other way around, wouldn’t the same still apply? That the earth would absorb the heat from the conditioned space, making the place effectively colder?

I have an older house that I want to retrofit that has zero insulation in the floor and I’m trying to decide whether it’s a better idea to insulate the floor vs sealing off the crawl space and insulating the foundation instead.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    David,
    Here's a link to an article which will answer most of your questions: Building an Unvented Crawl Space.

  2. imzjustplayin | | #2

    Yeah I've read that article before but it's almost as if the only justification for having a non-ventilated crawl space was humidity problems causing the insulation to collapse. If there isn't a humidity problem then somehow it IS better to have a ventilated crawl space. What they don't seem to go into is the impact of the earth's temperature on the house. I know the ground temperature in the south is higher than it is in the north so it's a possibility that higher ground temperatures plus higher overall outdoor temperatures don't really matter.

    btw one of the hyperlinks in that article is dead, here is the updated hyperlink that works:
    http://www.homeenergy.org/show/article/nav/moistureproblems/id/776

  3. GBA Editor
    Martin Holladay | | #3

    Dave,
    Thanks very much for notifying me about the dead link, and for providing the updated link. I have corrected the link in the article.

    Since you live in California, which has a less humid climate than the Southeast, you can have a ventilated crawl space if you want -- as long as your climate is mild enough to keep your plumbing pipes from freezing.

    Of course, if your crawl space includes any ductwork, you will suffer a major energy penalty due to the fact that your ducts are outside of your conditioned space.

  4. davidmeiland | | #4

    Dave R, your question is partly an energy modeling question--is there more heat loss if you insulate the floor, or if you insulate the foundation walls? If you insulate the floor and vent the crawl, your delta T is from interior to exterior at the floor line, a straightorward boundary, easy to visualize. If you insulate the walls, your delta T is from interior to crawl, which is a combination of soil and concrete walls, which are exposed to soil at various depths AND to the exterior air. I've never seen anything definitive on the various heat loss scenarios, and where the efficiencies are (probably because I've never looked far), but I wish someone would fill me in here, because there are times when an insulated, sealed crawl seems a lot easier and probably better from an energy standpoint.

    My own house has an insulated floor over a 36" crawl. The joists are 2x8 and my insulator dense-packed them using canvex. I figure there's an average of about R-28, because the canvex billows quite a bit as it's packed. I have no ductwork and almost no supply piping in the crawl. There's nothing to think about unless we get an extended period in the teens.

    A client of mine has a house with a crawl that is essentially a short basement. The block walls are a bit more than 48" tall. It is bone dry even after extended heavy rain. It has interior stairs that are big enough to handle a 4x8 sheet. It has an electric furnace and a lot of uninsulated, leaky ductwork. We're going to seal the foundation vents and insulate the walls with rigid foam. It seems like a no-brainer compared to insulating the floor (losing regain of the duct losses), and trying to seal and insulate a maze of ductwork (that would have to be done with FG and foil scrim, or possibly SPF although I am not a big fan).

    So I guess in your case, the question is, what are the specifics? Do you have ductwork? Can you get rigid into the crawl without cutting it into small pieces? Do you have easy access to spray foam installers? Is your crawl space bone-dry or not? Do you need termite inspection gaps? Do you have potential radon? What is your budget?

  5. imzjustplayin | | #5

    I was mostly looking towards insulating the crawlspace because there is a lot of duct work and it's a very expansive area, over 4K square feet sort of a sprawling situation. I think there are humidity problems because there is insufficient drainage around the foundation due to plants being planted too close and so that is one thing that will need to be addressed regardless of the insulation situation. Also, due to the previous furnace and one of the water heaters in use, the crawl space is used as a fresh air intake so that likely would change if the crawlspace is sealed off. This house was built in '72 with zero underfloor insulation and while 2X8 or 2X10 (not sure, pretty deep though) was used in the construction, I can't help but be bothered by all the perforations in the house's conditioned space. Btw the house uses a stucco exterior so there is no way I can replace the siding without great expense. The house uses a heat pump for heating but due to the great expense of heating this place, it has been turned off completely in the mean time.

    I guess the question I have then is, if this were turned into a passive house, what would be done and what cost? Then the second question would be, what would be the logical way to insulate the house w/o excessive expense?

  6. GBA Editor
    Martin Holladay | | #6

    Dave R.
    Q. "If this were turned into a passive house, what would be done?"

    A. You would be in for an extremely expensive remodel, and the expense could never be justified by the anticipated energy savings.

    Q. "... and what cost?"

    A. At least $100,000.

    Q. "Then the second question would be, what would be the logical way to insulate the house w/o excessive expense?"

    A. Hire an energy auditor or home performance contractor certified by RESNET or BPI. Get an energy audit and ask the contractor for a list of cost-effective energy retrofit measures.

  7. imzjustplayin | | #7

    Does that mean passive houses are cost ineffective? I thought 10% increase in cost was pretty good for making a house a passive house. I mean what was the cost increase from going from '72 building codes in California to 2014 building codes? has to be more than a 10% increase right?

    Also your answer doesn't address which route one would go for insulating under the floor. I'd hope that a slab of concrete isn't a prerequisite.

  8. GBA Editor
    Martin Holladay | | #8

    Dave,
    Most Passivhaus buildings in North America have specifications that are not cost-effective. That said, some builders have succeeded in building new Passivhaus homes that are cash-flow neutral -- in other words, the additional mortgage costs associated with the incremental construction costs (compared to code-minimum construction) are balanced by energy savings.

    Here's a big caveat: the same claim can be made for many energy-efficient homes that don't meet the Passivhaus standard. In fact, it's usually possible to do even better (financially) if you ignore the Passivhaus standard and simply focus on the most cost-effective investments.

    When it comes to Passivhaus retrofits, I've never seen one in the U.S. that makes sense in terms of cost-effectiveness.

    Concerning your question about insulating your crawl space: I believe that it makes the most sense to create a sealed crawlspace with insulated crawl space walls, for a host of reasons. I haven't done a detailed energy modeling exercise, however; in any case, such energy modeling will differ in every climate zone. If you have strong reasons why you prefer to insulate your crawl space ceiling, go ahead.

  9. user-1156270252 | | #9

    I see these question were asked in 2013 now 2021 so maybe new information out there. I have been trying to do a lot of research on the questions asked and no one seems to have a good answer. Especially is you are going better than code. (Who wants to make a D, code minimum, and pass the test and not make an 'A' to do better.) Seen articles that a slab is the biggest source of energy loss because of the surface are that the floor has. They are using similar R values as the walls. It seems like you would want the same on the floor of the crawlspace.

    1. Expert Member
      MALCOLM TAYLOR | | #10

      CHDesign,

      "Seen articles that a slab is the biggest source of energy loss because of the surface are that the floor has. They are using similar R values as the walls. It seems like you would want the same on the floor of the crawlspace."

      The amount of insulation that makes sense in any building assembly depends in part on the temperature differential between the inside and the outside. The reason crawlspace floors are rarely insulated to the extent slabs on grade are is that the ground underneath them is in most climates quite warm. Even with slabs on grade I'd be very surprised if it ever made sense to insulate them to the levels of the exterior walls. The best way to determine how much insulation to use in either situation is of course to do energy modelling.

    2. Expert Member
      BILL WICHERS | | #11

      Sure, code minimum is like a D-, but it costs more to get to an A+. You have to balance the costs with the benefits. Dana once mentioned you could insulate the walls to R1,000,000, and it WOULD save energy, but it would NOT be economical (and I calculated that the walls would be well over a mile thick too). Practicality is another important design constraint here. What you want to do is to try to hit the "sweet spot", where you get the maximum benefit for a given cost. Where exactly this sweet spot is depends a little on your climate zone, your fuel sources, and also your own personal preferences for your build. The sweet spot isn't going to be some arbitrarily high number for anything though.

      In the case of a crawl space floor, you are probably down below the frost line. That means that slab is going to be something above freezing on the other side. If it's -20F "outside" on the exterior of your walls, the underside of that crawl space slab is still going to be up above freezing, so something higher than 32F -- 52 degrees warmer than the exterior of the walls in this case! That much reduced thermal differential means much reduced heat flow, and that means a much lower R value required to hit the "sweet spot" in terms of optimal insulation levels for that crawl space floor.

      Note that crawl space WALLS make sense to insulate up to close to the same level as the exterior walls of the living space, and that's because the see exterior side temperatures closed to the exterior side temperatures those "regular" walls see. As you go progressively deeper underground, you see increasing temperatures. This is why you sometimes see articles that say things like "the first two feet of the foundation are the most important to insulate", things like that. That is because the first part of the wall sees colder temperatures. Foundation walls are usually at least partially above grade at the top too, which means those ares see the SAME exterior side temperature as the living space walls.

      Slabs on grade are different, since they aren't "at depth", but they'll still lose less energy than the ceiling.

      It's always important to consider the specific application in question and not to just generalize any particular rule across an entire structure.

      Bill

      1. user-1156270252 | | #13

        I would agree with you. I am trying to find a good source that gives the climate zone and heat loss or cooling through the soil. If you compare the amount of surface area of the stem wall to the area of the floor of the crawlspace there is a big difference. With out crunching numbers it seem even though it is not a freeze concern, insulation would make a big difference on the floor. Now how much? How much is enough and how much is just throwing away money. https://www.greenbuildingadvisor.com/article/183793

  10. plumb_bob | | #12

    I would suggest that aiming for passive house standards will be extremely painful and expensive. Aiming for general improved efficiency and comfort through targeted retrofits will keep the budget reasonable.

    One of the main reasons for air sealing and insulating the exterior walls of the crawl vs the floor system, is the crawl effectively becomes part of the house. If done correctly the air should be warm and healthy and the space become usable.