Flytrappist | Posted in Mechanicals on

Hey folks-
I’m an old contractor building a new house- hopefully my last!  I think I’ve decided on an HVAC system utilizing two separate, single-zone Fujitsu splits in a tight, well-insulated 1200 sf single-story home.  I’m doing a self-install, since I can’t find a knowledgeable contractor out here in the sticks.  Manual J says I’ve got 16400 BTU heat, and 17350 cooling in zone 3A with design temps of 21F and 94F, but I think my loads may be even less.  I like the idea of using two separate systems that will avoid modulation issues and overcooling in small rooms.

A call to Fujitsu Tech Line was confusing.  Tech said a 7K BTU slim ducted air handler and a 7K wall unit were “close enough”, for an 18K dual-zone system, but if I was using two single zone, 9K outdoor units, I should match two 9K BTU air handlers to them.  Never got a reason why the difference, and not convinced I received good advice…

I’m thinking 9K is going to be too much, but I also don’t want incompatibility probs, and doubt we will be happy going with a single-zone for the entire house.

So- can I slightly undersize the indoor units relative to the outdoor units or should I just listen to the Fujitsu tech and match indoor and outdoor?

Opinions?

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. joshdurston | | #1

    With multi splits there is a tolerance for over under matching indoor/outdoor units. Maybe as wide as 70-130%.

    But the min modulation will likely be lower with the 1:1 9k units even though their max output is higher.

    Only reason to go with the multi split would be to get a base pan heater if that’s important to you. Otherwise the 1:1 9k will outperform is basically every metric.

  2. kyle_r | | #2

    The 9k, 12k, and 18k Fujitsu slim duct units all have the same minimum outputs. If modulation is your concern could you not go with a single larger unit?

  3. Jon_R | | #3

    > can I slightly undersize the indoor units relative to the outdoor units
    What do you expect to gain by this?

    > should match two 9K BTU air handlers
    I didn't follow this either - you think that 2x9K = 18K is excessively oversized for a 17,350 Manual J?

    Do review the latent performance at low loads (almost always a major mini-split weak point).