Gas Hot Water Tank Flue – Gap as it Passes through Roof Deck

Lindaloowho | Posted in General Questions on

Hi Everyone,

There is up to a 1/2” gap to the outdoors between the circumference of the water heater tank flue and the gasket going through the roof deck.

Can I caulk this with High Temp Caulk or is the gap there for a reason?

Thanks!
Linda

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    BILL WICHERS | | #1

    Is this gap in the thimble, as in you can see sky through the gap? That's a problem -- you don't want rain getting in, but you have to use a proper assembly here. If the "gap" is just insulation, then it's probably not a big enough gap -- you typically need at least a 1" gap to combustibles around the typical B vent vent pipe from a gas fired water heater.

    There is info in the link I posted in your previous question regarding the proper way to air seal around a vent pipe like this.

    Bill