GBA Logo horizontal Facebook LinkedIn Email Pinterest Twitter Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Audio Play Icon Headphones Icon Plus Icon Minus Icon Check Icon Print Icon Picture icon Single Arrow Icon Double Arrow Icon Hamburger Icon TV Icon Close Icon Sorted Hamburger/Search Icon

Community and Q&A

Minisplits and moisture removal effectiveness

David Jensen | Posted in Mechanicals on

Considering that the better variable refrigerant flow mini split heat pumps, sized properly, are designed to operate largely without cycling off, it would seem that they would offer superior latent load performance (moisture removal) over the typical cycling split system. Is that true in the real world? I’m specifically interested in performance in high humidity environments like here in central Florida.

Thanks.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. User avatar GBA Editor
    Martin Holladay | | #1

    David,
    In theory, your thesis makes sense. However, I'm not aware of any rigorous study that supports the thesis.

    There have been studies of air conditioner oversizing that failed to show that oversized air conditioners are less effective at moisture removal than right-sized units. The issue is complicated.

  2. User avatar Expert Member
    Dana Dorsett | | #2

    With continuous compressor operation you don't have the issue of condensation on the coils being re-evaporated and injected into the air the way oversized AC systems set up to run the air handler continuously while the compressor cycles on/off do.

    The sensible heat ratios of most mini-splits operating a at low speed is indeed quite a bit lower than most 1 & 2 stage split systems under low sensible load conditions, which is another way of saying they remove more moisture than the most common ducted systems. But that's not to say that they always remove ENOUGH moisture in those low sensible load conditions. A mini-split helps, but isn't necessarily the whole solution. Low sensible load houses will often need a separate dehumidifier to manage peak latent loads.

  3. Charlie Sullivan | | #3

    " Low sensible load houses will often need a separate dehumidifier to manage peak latent loads."

    Just to expand a bit on why this is important---a well insulated house in a hot, humid climate will have the same latent load as a poorly insulated house in the same climate, but will have a lower sensible load. So moisture removal becomes a bigger fraction of the HVAC system's job as the house gets better insulated.

  4. David Jensen | | #4

    "The sensible heat ratios of most mini-splits operating a at low speed is indeed quite a bit lower than most 1 & 2 stage split systems under low sensible load conditions, which is another way of saying they remove more moisture than the most common ducted systems"

    Is broad terms, is there typically a crossover point in high sensible and high latent load conditions where the typical oversized split system will outperform the mini-split on the latent load, assuming the mini-split is sized properly? I'm trying to determine if there is a performance down side to the mini splits or, if done right, they are better across the board, with the exception of greater temperature imbalance depending on the distance from the mini-split.

    Thanks so much for your insights

  5. User avatar GBA Editor
    Martin Holladay | | #5

    David,
    I don't think that there is any performance downside to minisplits -- certainly not when it comes to moisture removal. If you are trying to heat and cool your entire house with just one or two ductless minisplits, of course you have to consider the problem of temperature differences from room to room. But that's another issue.

  6. D Dorsett | | #6

    If undersized and running at max speed most the time the SHR would run on the high side, over 80%. If oversized and cycling all the time it's latent moisture handling won't be nearly as good as when it's modulating. It would have to be grossly mis-sized to fall much below the performance of a single-speed split system.

  7. User avatar
    Reid Baldwin | | #7

    I recall reading that some systems have a dehumidify mode in which the air flow rate is reduced but the compressor speed is unchanged such that the coils get colder. Is that effective? I can see that you would pull more moisture out of each ft^3 of air, but you would also remove more sensible heat from each ft^3 of air. Are these effects different enough in magnitude that the SHR changes markedly?

  8. D Dorsett | | #8

    Most mini-splits have a dehumidify mode that operates at a fixed rate, but only the Daikin Quaternity series operates in dehumidify mode without sensible cooling, and the only mini-split with a dehumidistat control:

    http://www.daikinac.com/content/residential/single-zone/quaternity/control-humidity/#control-humidity

  9. User avatar
    Jon R | | #9

    For the record, many mini-splits operating at less than 1/2 rated load (a common occurrence, even when perfectly sized) have little to no latent removal (humidity reduction), worse than a unit that cycles (turning off compressor and fan so that little re-evaporation occurs). Why - because the mini-split interior fan doesn't modulate down as far as the compressor, leading to excessive CFM/ton. Regarding dehumidify mode: in most cases, not a viable solution. But let's see some specs regarding part-load SHR, temperature control, etc.

    Plan on running a dehumidifier in any new house in a humid climate.

    Table 7: https://www.nrel.gov/docs/fy11osti/52175.pdf

  10. kjmass1 | | #10

    With just one of my 12K Fujitsu splits running 24/7 during peak humid summer months, I've yet to achieve the documented pints/hr. It keeps my 1800sf house at 72 no problem and certainly removes buckets of water and keeps humidity in the house under control, but take those numbers with a grain of salt. Dry mode might remove more but you lose temp control and it will just keep cooling.

  11. Aun Safe | | #11

    Just to add some anecdotal info to this thread, I have a Mitsubishi MUZ/MSZ-FH09 system, and it is so poor at moisture removal when operating at its lower capacities that I need a separate dehumidifier in the room.

    But once it ramps up to higher operating capacities on days that are 90+ degrees F, I can easily shut the dehumidifier off and the Mitsubishi keeps rel humidity in the room well below 50%.

  12. Expert Member
    Akos | | #12

    I just put a couple of books on top the mini split head, works great for reducing the air flow.

    Most modulating units have an coil temperature sensor and won't allow the coil to freeze up even if you restrict the airflow. Still more efficient than running a dedicated dehumidifier.

  13. aggierockdoc | | #13

    "Low sensible load houses will often need a separate dehumidifier to manage peak latent loads."

    I’m finding it hard to understand why this might be.

    My two premises are this:
    • A split AC system with a condenser outside and the evaporator inside can push both the latent heat of condensation and the condensate from the dehumidification process to the outside of the enclosure and process the interior air to give cooler, dryer air to the inside.
    • Yet a standard dehumidifier, where the process air passes first over the evaporator coil and then over the condenser, retains the latent heat of condensation within the enclosure.

    My conclusion is this:
    Having both a dehumidifier and AC running in the same enclosure means I have to spend more “energy-cash” in order to (1) run the AC to remove the sensible heat derived from both within the enclosure AND the dehumidifier (2) run the dehumidifier.
    My objective is to minimise energy usage and maximise system value:
    I’m happy to pay for value (ie good cost/benefit) in terms of achieving my goal ie keeping energy consumption down. (Energy costs are HUGE here – around 0.3 to 0.4 USD per kwh)

    My questions:
    What am I misunderstanding?
    What would you recommend in terms of an efficient HVAC configuration that delivers on low energy usage and high dehumidification capability with cooling a secondary nice to have?
    NB. I live in Costa Rica where dewpoints are at around 25C in the summer and around 18C in the winter. Ambient temperatures range from 22C to 35C in winter and 25C to 30C in summer. If I had a bumper sticker for all HVAC engineers here in Costa Rica, it would read “it’s the latent load, stupid”.

    1. User avatar
      Jon R | | #14

      Designers of AC units seem to optimize for specs, not real-world efficiency or comfort. So they use the wrong CFM/ton at many operating points. So while it would be more efficient if the AC removed the moisture, it often doesn't and one has to use a dehumidifier to be comfortable.

      You want a unit where CFM/ton goes down with decreasing load (decreasing SHR). Most go way up at low loads. Adding a fixed air flow restriction is similarly flawed.

      A Daikin Quaternity will do a better job. Would be interesting to know if it would pay for itself in CR.

      > objective is to minimise energy usage

      Air sealing/testing and insulation is always important and usually cost effective. Solar AC is interesting.

      1. aggierockdoc | | #17

        Jon, thank you for responding. It's really helpful to hear an expert confirm my hunch that AC unit design is pretty much sub-optimally configured for the climate in which I live. It baffles me that the manufacturers kind of ignore the needs of the 2 billion people who live within 15 degrees of the equator.
        On a technical note, I'm particularly intrigued by your comment about needing a unit where air flow (ie fan speed) vs power consumption (ie compressor activity) should decrease with a decreasing load. I'm trying to get my around that.
        If in my scenario we assume there is no sensible load... the load would only change if I lowered the humidistat... so am I right to conclude you are saying something like...
        even though I want the device to decrease the SHR as I decrease the humidity set point, most (?all?) devices are too stupid to do that?"

  14. fcserei | | #15

    My solution was to use a regular thermostat to cycle on/off a Pioneer mini split in Dry mode around the thermostat set temp. I'm in Delaware. I had no problem to keep 75F, 45-55 deg humidity inside this summer. Electric bills were surprisingly low too.

    1. johns3km | | #16

      I do something similar- using a Sensibo it’ll toggle between dry mode and high speed cool for hot days.

    2. aggierockdoc | | #18

      At 24C/75F, I'd have to get my woolly socks out...

      In dry mode does your Pioneer just reduce the fan speed to provide the lower SHR... ? or does it slow the compressor as well?

      NB. My ideal set point would be to get humidity a little below 60RH with max daytime interior temps of 26C - 28C (and have ceiling fans keep us comfortable). Anything below that in terms of RH or temperature would be $ in the bin.

      As Jon R alluded to I'm planning on using 50 to 100mm foam batts all around the house enclosure, sealed up with a vapour barrier so that we can choose to let the outside in on good days, or keep the outside out on bad ones. Construction starts in 2 weeks!

      1. fcserei | | #20

        In Dry mode the fan speed is even lower than the low speed for the heat/cool modes. The compressor seems to be modulating also. The ducted mini split temp for the dry mode is set to 73F at the unit, slightly below the actual target temp I'm looking to get in the room.
        The best thing is that this way it is a set and forget thing, I don't have to fiddle with the mini split during the day like when I tried with the unit's original controls only.

  15. Deleted | | #19

    Deleted