The SunRise Home.

I have been cruising this presentation by Thorsten Chlupp and wanted to see if anyone who might have actualy seen it, might have some comments.
http://passivehouse.us/passiveHouse/2010_Passive_House_Conference_Presen...

Capture 5.JPG51.16 KB
Asked by Lucas Durand - 7A
Posted Thu, 02/24/2011 - 10:23
Edited Fri, 02/25/2011 - 15:43

Tags:

66 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

My first impression is that the SunRise home would be not-so-affordable...
The quantities of materials used seem amazing to me...

The Bituthene... is that a standard detail for his FPSF foundations?
Is its primary purpose to provide a drainage plane or does it help secure the "wing" insulation to the vertical insulation?

Capture 2.JPG Capture 3.JPG
Answered by Lucas Durand - 7A
Posted Thu, 02/24/2011 - 10:26
Edited Thu, 02/24/2011 - 10:30.

2.
Helpful? 0

Unfortunately, the PDF presentation isn't in very high resolution...

Capture.JPG 1.JPG
Answered by Lucas Durand - 7A
Posted Thu, 02/24/2011 - 10:35

3.
Helpful? 0

I like Thorsten's attitude about making "ultra-tight" "simple".

Is the redish line I have high-lighted representative of the "continuous" air barrier?
Does anyone have specifics on what materials were used to make the air barrier?
How about specific air-sealing details - types of tape, gaskets, locations, special techniques?

Answered by Lucas Durand - 7A
Posted Thu, 02/24/2011 - 10:40

4.
Helpful? 0

What is going on here?

Capture.JPG
Answered by Lucas Durand - 7A
Posted Thu, 02/24/2011 - 11:10

5.
Helpful? 0

Are the corners of the window boxes taped only to the Tyvek?
Are the boxes also taped to the sheathing layer behind the Tyvek as well?
Is that tape or strips of ice&water shield?

Answered by Lucas Durand - 7A
Posted Thu, 02/24/2011 - 11:15

6.
Helpful? 0

Lucas,
I thought you would find the project interesting.

I started up a thread over at JLC
http://forums.jlconline.com/forums/showthread.php?t=55640
All I know is from observing the presentation.

I think the pressure boundary at the plywood makes a lot of sense.
It looks like the note says the plwood is taped...

check out the panel orientation and the sun shadows in the photos ;--)

Answered by John Brooks
Posted Thu, 02/24/2011 - 11:22

7.
Helpful? 0

John, I find it very interesting. Thanks.

I noticed the panels too. Crazy. I wonder what that 12000 Gal. R60 tank in the Sunset Roost home cost? They kinda loose me there...

Answered by Lucas Durand - 7A
Posted Thu, 02/24/2011 - 12:34

8.
Helpful? 0

John, it appears Thorsten is using some type of plywood gusset to create a type of Larsen truss over the plywood sheathing.
Do you know how these gussets are attached to the sheathing?
There appear to be little "stubs" nailed over the Tyvek... or do they project through the Tyvek?
Are the gussets nailed to the sides of the "stubs"?

Capture.JPG Capture2.JPG
Answered by Lucas Durand - 7A
Posted Thu, 02/24/2011 - 12:39

9.
Helpful? 0

Lucas,
My reverse engineering from the photos .....
platform framed with 2x4 ceiling joists on the upper level
walls & joists completely wrapped in plywood
plywood joints and intersections are taped
plywood covered with house wrap
then roof trusses AHW (After House Wrap)
then cleats are strapped on

not-so-different from an idea that I had been playing around with
except trusses are added above the Attic Floor Deck and
Larsen-like trusses are strapped to the walls

brooks.JPG
Answered by John Brooks
Posted Thu, 02/24/2011 - 18:47
Edited Thu, 02/24/2011 - 19:17.

10.
Helpful? 0

Lucas,
I noticed that they did not build it like their cross-section showed.
The 2x4 service core(ceiling joists)sit on top of the plate

2x4 on top.JPG
Answered by John Brooks
Posted Thu, 02/24/2011 - 19:51

11.
Helpful? 0

John, I am recosidering my own strategy now...
For continuity and simplicity, yours and Thorsten's details appear hard to beat.
"0.6 ACH_50 made simple"...
I think I will have to accept a not-quite-as-continuous approach with "air-tight" plywood.
The Riversong truss doesn't do plywood sheathing on the exterior of the inner stud wall...
Certain dyes have already been cast...

Answered by Lucas Durand - 7A
Posted Fri, 02/25/2011 - 10:36

12.
Helpful? 0

This is where I disagree with the "extremeness" of 0.6ACH50...
I don't think there is anything wrong with "extreme" airtightness as long as it is "simple".

Answered by Lucas Durand - 7A
Posted Fri, 02/25/2011 - 10:45

13.
Helpful? 0

Distantly related?

Noname.jpg Noname2.jpg
Answered by Lucas Durand - 7A
Posted Fri, 02/25/2011 - 10:46

14.
Helpful? 0

I think making the pressure boundary as simple as possible is the key thing.

The Wall and Ceiling pressure boundary is about 1/2" thick and it is virtually Continuous

It is very similar to Marc Rosenbaum's strategy ....

only there is a ventilated attic instead of a compact Roof

Answered by John Brooks
Posted Fri, 02/25/2011 - 11:27
Edited Fri, 02/25/2011 - 11:28.

15.
Helpful? 0

The ventilated attic is the "HAT"

When the roof cladding is replaced in the future...
The Air Barrier is not disturbed

Answered by John Brooks
Posted Fri, 02/25/2011 - 11:37

16.
Helpful? 0

Lucas
Interesting stuff...BTW you might want to check the spelling of Thorsten's last name in your OP...I believe it is Chlupp.

Answered by Garth Sproule 7B
Posted Fri, 02/25/2011 - 11:43

17.
Helpful? 0

Lucas,
can you explain your 3 comments in more detail?

Is it the not-so-continuous structure or the thermal layer that you will be "accepting"

ld.JPG
Answered by John Brooks
Posted Fri, 02/25/2011 - 11:48

18.
Helpful? 0

Thanks Garth.

Answered by Lucas Durand - 7A
Posted Fri, 02/25/2011 - 15:44

19.
Helpful? 0

can you explain your 3 comments in more detail?

John,
I had to get an engineer’s stamp to get a permit so I am committed to a Riversong style truss wall.
I haven’t been able to figure out how to locate a sheathing layer between the two rows of studs without getting away from the Riversong framing style.
With structural sheathing innermost, the rim joist becomes a “bump-out” in an otherwise continuous plane of “tightness”.

Consequences are added complexity.
Gaskets and “goo” instead of just tape.
Also, a service cavity is required if you want to minimize disruptions in air barrier continuity and keep services on the warm side – though maybe the latter is more of a cold climate thing…

I think having plywood at the exterior side of the inner studs makes the most sense.
For simplicity and because it creates an insulated service cavity on the warm side of the air barrier.

Just for the record, I still think the Riversong framing system is one of the best.
It just doesn’t “do” mid-wall sheathing is all.

Riversong truss.png Larsen truss.png
Answered by Lucas Durand - 7A
Posted Fri, 02/25/2011 - 15:50
Edited Fri, 02/25/2011 - 16:04.

20.
Helpful? 0

The service chases allow for quite a bit of interior renovation over time without having to disturb the air barrier.

Answered by John Semmelhack
Posted Fri, 02/25/2011 - 17:22

21.
Helpful? 0

Lucas, could you not use joist hangers to hang your floor joists on the inside face of the plywood/walls. That would solve your continuity barrier. I think it was the guys at 100khouse.com that used that detail on one build.

Answered by John O'Brien
Posted Sat, 02/26/2011 - 16:55

22.
Helpful? 0

Affordable is always relative. Since I paid for the project and it wasn't a funded research project I spend more than I wanted but less than some high taste homes we build for clients. And if I look at our outlook on energy prices it was actually cheap...

The SunRise home was for me an invaluable opportunity to push the limits, try out new concepts and be able to learn. Pretty much everything in the home is some sort of a prototype idea and with the help of thermal shutters on all windows it meets Passiv Haus in PHPP07 - which is no easy feat to achieve in a 14,000 HDD climate. Besides that it produces 100% of all its heating and DHW demand solely by either solar or a custom build masonry heater with integrated coils which are molded together in an integral energy system...which requires between 7 to 28 watts of electricity to move and distribute its energy/heat. There is no fossil fuel based heat source in the home - and we stay nice and toasty at 40 below and have not run out of hot water yet. It is simply amazing to see how efficient the home is - and how well the energy system works. And we started the system up under the worst conditions in the dead of winter in December. I see tremendous potential and already have the 3rd generation mapped out in my mind. Data loggers crunch away on the many sensors which have been placed throughout the different assemblies and parts of the many components which make up the home. The Cold Climate Research Center will monitor and crunch this data and analyze how these parts fair in reality.

Anyways, questions about the wall assembly: I wanted the performance of a REMOTE wall with all the goods I have learned to value from this wall system and replace the out insulation with a more renewable product - cellulose. EPS foam works very well, but it is a 100% petrol based product with high embodied energy. I named this variations the ARTIC wall, which is more or less a REMOTE wall insulated with cellulose and which is diffusion open to both directions and has no vapor barrier but a very airtight "diffusion" layer in form of air sealed and taped CDX plywood. At this point and time it is a Prototype wall assembly and I need to see more data from the sensors which have been placed throughout the wall sections before I am ready to claim this to be a good alternative wall assembly to REMOTE/PERSITS.
IMO the key in both assemblies is the placement of the airtightness layer within the assembly - where it can be continuous and most importantly - protected. If you place your ply/air/vapor layer on the inside frame face you just can't get there. Even if you did the best job (and hardest) to air seal you be surprised to see how fast this can deteriorate a few years with homeowners taking over. And you fight your installations of electrical, mechanical and plumbing - now, today and in the future. An installation layer is simply invaluable. Combine this with a fool proof pressure boundary and you got a system which just works. Traditional double walls can work well and create a very efficient home but also can have many problems build in. This is one of the reasons PERSITS was developed so long ago...

Why build a good house when you can build the best?

Happy Building, TC

PS: Lucas email me if you want a ARTIC wall detail, with a beta disclaimer at this point and time

Answered by Thorsten Chlupp
Posted Sun, 02/27/2011 - 01:12

23.
Helpful? 0

Thorsten,
I realize you may not want to open the door to 100 questions.

My primary questions are about joining the plywood pieces.
It looks like the plywood is in a sweet spot where it does not experience extreme temperatures.
Did you use Euro-tape (Siga) or other?

Was I right about your construction sequence?
Did you skin the "ceiling joists" with plywood and then install the roof structure(trusses)

From the photos it looks like you decided there was no need for the Housewrap at the attic floor?
Or is the housewrap just not visible because it is covered in dust?

floor.JPG
Answered by John Brooks
Posted Sun, 02/27/2011 - 07:49
Edited Sun, 02/27/2011 - 08:54.

24.
Helpful? 0

Thorsten, thanks very much for taking the time to comment on this thread.
I really appreciate the idea of "0.6 ACH_50 made simple".
I also appreciate your efforts to move to a less-foamy solution.

Like John I am also wondering what type of tape you chose to use at the seams of the CDX?
Is it the Grace/Vycor that is visible at the window boxes?

Thanks again Thorsten, and happy building to you too ;-)

Answered by Lucas Durand - 7A
Posted Sun, 02/27/2011 - 09:18

25.
Helpful? 0

All these questions about wall details when the most important part of the project is successful implementation of seasonal solar thermal storage. Hopefully you'll discuss this in greater detail in the future, Thorsten. We've been discussing this for an anchorage passivhaus for a year now.

Answered by mike eliason
Posted Sun, 02/27/2011 - 11:48

26.
Helpful? 0

But Mike, I already have a successful and time-tested solar storage system that meets my needs - 80 acres of boreal forest.

Answered by Lucas Durand - 7A
Posted Sun, 02/27/2011 - 14:09

27.
Helpful? 0

Lucas, could you not use joist hangers to hang your floor joists on the inside face of the plywood/walls.

John O'brien, I'm not sure this would work in my case.
It is an interesting idea though...

Answered by Lucas Durand - 7A
Posted Sun, 02/27/2011 - 22:35

28.
Helpful? 0

I would think that it would be no different using joist hangers through 1/2cdx, into the rim, then it would be to do the alternative.

Something like the attached. You could swing both an internal and external cdx air barrier unbroken with this.. (theoretically). I'd appreciate the builders telling me why this won't work. ;)

JoistHungDSW.jpg
Answered by John O'Brien
Posted Mon, 02/28/2011 - 08:21
Edited Mon, 02/28/2011 - 19:24.

29.
Helpful? 0

John O'brien,

Your sketch would probably work well and would allow one cavity of insulation rather than two. Riversong says this is an important advantage of his system. However it doesn't address what Thorsten says about the services going interior of the air barrier. He's got the air barrier plywood midway through the insulation and no issues with services that penetrate the AB. Unfortunately there's no perfect combination of features. When the plywood goes at the exterior of the inner frame, there are two cavities to dense pack, and it's not as easy to assemble a truss--but it is possible, as in Thorsten's project here.

Answered by TJ Elder
Posted Tue, 03/01/2011 - 01:37

30.
Helpful? 0

Window extension detail: the ply bucks are continuous and fastened to the main 2x6 framed opening, then standard flashing detail plus air sealed with 4"vycor tape. Tyvek is v cut at the header and overlaps the buck...pretty much your standard detail.
Foundation: Keeping this sort of foundation dry in our extreme cold climate (frost heave) is crucial - waterproofed in this manner you create a fool proof defense for your foundation...which is a core part of your building after all
Tapes: We mainly use Vykor and 3M...Euro tapes are nice but too expensive. As your tape is on your warm side and protected it is perfectly fine and I have never seen issues in all our testing...or the more the 50 REMOTE homes I have built over the years.
Ceiling: Correct, you build the platform - or your lid, air seal and detail and then roll your truss on the ceiling deck you created. The slide still had and older detail - for the sake of utility chasing it makes more sense to run the ceiling joist over the top plates so wiring can run right into the ceiling. I used Tyvek on the lid, it's just dust covered ...got to love cellulose!

Mike: I agree with you, interesting :-) I most likely will give a talk in ANC and Wasilla in April...email if you want to be in the loop. If you're coming up north I am happy to give you a tour. This isn't the best place to discuss renewable energy systems.

Thomas: You don't need to insulate the interior frame, which sometimes might be the easier/cheaper solution. I need a lot of insulation in my extreme cold climate - in a cold climate an outside blanket will do all you need it to do. It isn't about a perfect combination of features but what your ultimate goal is as far as performance and longevity of your structure you're trying to build goes. Your pressure boundary is the key to this question - and IMO and my humble experience worth any extra effort to get it right.

Answered by Thorsten Chlupp
Posted Tue, 03/01/2011 - 03:56

31.
Helpful? 0

Thomas, I left out the interior 2x2 strapping channel that would be the service layer. It would cover up the 2" of foam as well in the previous diagram I had.

Answered by John O'Brien
Posted Tue, 03/01/2011 - 08:48

32.
Helpful? 0

John O'Brien, I didn't mean to suggest that your detail wouldn't work.
Only that I'm not sure it would work in my case.
I'd have to look into it...
Anyway, I think the idea is interesting.

Answered by Lucas Durand - 7A
Posted Tue, 03/01/2011 - 10:34

33.
Helpful? 0

Thorsten,
I noticed that there is no blocking under the long edge plywood joints.
Did you use a Tongue&Groove plywood ... or is the tape holding the seam together?

I am also curious about the housewrap outboard of the ceiling plywood and the wall plywood.
Is this to enhance the Air control layer or protection from liquid water?

edge.JPG
Answered by John Brooks
Posted Mon, 03/07/2011 - 17:20

34.
Helpful? 0

Did you use a Tongue&Groove plywood ... or is the tape holding the seam together?

I was just at the lumber yard the other day and they had a 1/2" "t&g" plywood for roof sheathing applications they called "V-groove".
Previously, I had always believed that one needed to step up to 5/8" to get t&g...

Here it is - "Easy T&G Roof":
http://www.canply.org/english/products/easy_tg/easytgroof.htm

Answered by Lucas Durand - 7A
Posted Mon, 03/07/2011 - 19:07
Edited Mon, 03/07/2011 - 19:22.

35.
Helpful? 0

I thought it might be "helpful" to copy Thorsten Chlupp's definition of Out-Insulation here at the "SunRise Home" Thread:

Definition of Out-Insulation:
1. The pressure boundary or airtightness layer is placed on the outside of your structural sheeting between the framing and the exterior insulation layer. In the early days this layer was completely sealed with a 60 mil peel and stick rubber membrane, later your typical 6 mil poly vapor barrier was used or taped Tyvek. Taped and sealed CDX plywood works excellent and creates a diffusion open boundary which allows drying potential in both directions.
2. The exterior framing is now part of your conditioned space and is utilized as your utility chase - electrical, mechanical, and plumbing...which opens many more options on how you can run your utilities. It is your structural building core. It can be insulated if additional R-value is needed and the 1/3 to 2/3 insulation ratios in-between you pressure boundary is maintained...I actually think 40/60 is still a safe ratio.
3. The insulation is wrapped around the exterior of the structure and keeps everything warm and is protected with a weather barrier.
4. Vertical strapping attaches to the main structure with long fasteners or in form of a Larsen type truss design depending on the design and insulation used. This creates a rain screen and drainage plane - which promotes the equalization of the pressure outwards, which in turn ensures the wall assembly can dry to the outside. IMO this is very important if cellulose or mineral wool is used. If foam sheeting or spray foam is used as the exterior insulation this of course is a moot point...REMOTE walls can only dry to the inside in reality.
5. Siding of choice is attached to the strapping, which is plenty strong to support the weight...with engineer approval.
6. Roof assembly is separated with the same pressure boundary and built with a vented cold attic roof truss (with exterior access). The same basic physical principles of air flow and temperature differentials ensure pressure equalization and drying potential to the outside.
NOTE: The key difference of an outinsulation strategy is not only that insulation is placed on the outside of the core structure but also that your critical pressure boundary (or airtightness layer) is CONTINUOUS and PROTECTED from both directions. This layer will stay untouched and functional for the lifespan of the structure. From my experience drywall/gypsum/6 mil is just not a very durable material choice to handle a critical building function.
Summary: Insulation where it belongs - on the cold side, thermal bridge free construction, protected placement of your main defense of moisture, and easy to use utility chase now and in the future.
......
Answered by Thorsten Chlupp
Posted Sun, 03/06/2011 - 20:17

Answered by John Brooks
Posted Wed, 03/09/2011 - 07:37

36.
Helpful? 0

That V-groove ply would make for a pretty slick air barrier Lucas. Lock that together with some black death, plus some tape for good measure.

Answered by John O'Brien
Posted Wed, 03/09/2011 - 22:38

37.
Helpful? 0

John O, I think so too... I'm not sure how much extra "tightness" it'll give me but if anything the extra support along the seams should make for a more durable air barrier than with square edge... It's only an extra $300 on the whole project to go entirely with the "V-groove".

Answered by Lucas Durand - 7A
Posted Thu, 03/10/2011 - 13:11

38.
Helpful? 0

John B, thanks for reposting Thorsten's comments on this thread.

Answered by Lucas Durand - 7A
Posted Thu, 03/10/2011 - 13:13

39.
Helpful? 0

Still processing but after further review of the ARCTIC profile…

In my opinion, the most significant aspect of the ARCTIC profile is the location of the air barrier. It is in a sweet spot:
- Its location allows it to have the simplest pressure plane of any air barrier system - it is a cube and that is a good thing.
- Its location allows it to stay warm and therefore “dry” - no condensation.
- Its location allows it to stay protected for the life of the structure - no extra service cavity required.

In my opinion, secondary to the importance of the location of the AB, but outstanding never the less, are (among other things):
- The choice of a Larsen-style truss system to create “outsulation” - not-so-foamy insulation exterior to the air barrier that can be varied in thickness to adjust the “1/3 to 2/3 insulation ratios” to suit the climate.
- Climate appropriate permeability - the air barrier can do double duty as vapour retarder and still allows drying whichever way it needs to.

Considering the R values involved, this system is very “buildable”.

This system requires some compromises - like flat ceilings.

“Extreme tightness” is almost guaranteed with attention to details like window and door build-outs.

The “extreme tightness” and drying potential will likely have a strong impact on durability on both sides of the air barrier.

Using the same basic approach as ARCTIC and relative to the location of the air barrier, I wonder if a “1/2 to 1/2 insulation ratio would work best in mixed climates?

Using a slightly different approach from ARCTIC and relative to the location of the air barrier, I wonder if a “2/3 to 1/2 insulation ratio”, a sort of “inverse ARCTIC” would be best for cooling dominated climates.

1.jpg 3.jpg
Answered by Lucas Durand - 7A
Posted Thu, 03/10/2011 - 13:14
Edited Thu, 03/10/2011 - 16:19.

40.
Helpful? 0

Hmmm...
I had a "1/2 to 1/2 insulation ration" drawing to post but for some reason the image that appears on my post is not the same as the one as I uploaded...

What's up with that?

Answered by Lucas Durand - 7A
Posted Thu, 03/10/2011 - 13:20

41.
Helpful? 0

Lucas,
did you try to give your image a new name?

Glad to see you are still "thinking out loud"
Buildable is VERY important

Answered by John Brooks
Posted Thu, 03/10/2011 - 13:55

42.
Helpful? 0

I have mentioned this on another thread....
There is another advantage to the plywood attic deck....
It provides a safe "stage" for building"the roof "...stick frame or trusses.

A system like this allows blower door testing before drywall
which was not a feature of the traditional REMOTE

Answered by John Brooks
Posted Thu, 03/10/2011 - 14:12
Edited Thu, 03/10/2011 - 14:20.

43.
Helpful? 0

I understand the advantage of the deep-set and "overinsulated" windows for Thorsten's Climate and because of the very thick window frames.

In a not-so-extreme climate with not-so-thick window frames
I think an "outie" window(like Riversong's) would be much more BUILDABLE.

I can't help but notice when I look thru the SunRise slide presentation that the final casing for the windows is avoided until the very last minute.
This suggests that it might be very fussy and labor intensive

Answered by John Brooks
Posted Thu, 03/10/2011 - 14:30
Edited Thu, 03/10/2011 - 14:47.

44.
Helpful? 0

Lucas, looks like you grasped the concept and the important difference. There are a few more rather important characteristics which we hadn't even talked about...like the lambda value and decrement delay. I will email you my draft write up on the new wall soon, which will explain some of these characteristics. I like to go over some datasets before I send it, but you should see it in a few days. I say that, performance is incredible...I have not actively heated my house for 3 weeks now...if you check the weather channel for temperatures in Fairbanks Alaska you will see that it was mainly nice and sunny but still cold...with close to 30 below night temperatures. Nevertheless our indoor temperature maintains 68-70F by passive solar gain.

Roof deck/ceiling: I did not use T+G only standard CDX Plywood which we taped with 4" Vycor...it was plenty strong for what it was supposed to do. It surely makes running trusses safer, easier and faster. The ceiling does not have to be flat; we quite often do vaulted ceiling trusses for our clients. I used Tyvek in addition to the taped and sealed plywood mainly because I had a many people voice great concerns about building diffusion open wall system with cellulose in our extreme cold climate and an extra layer of protection with high permeability was the conservative part of me giving in. With the data we collect now I believe that was unnecessary.
The home is tight - final test with HRV system running on high came in at 0.48 ACH_50, the residual loss is accounted by some ventilation leakage from the HRV and the 6"make-up air (passively sealed with a cold air trap) and the 8" masonry heater chimney stack, which requires a slight opening in the closed damper position by code.

John B. - a standard REMOTE can be blower door tested the same before drywall - you HAVE to test before drywall or you missed your best window of opportunity.
Nothing fuzzy about the window detail...the only reason this happened late is because of glazing issues which we had, delaying the windows. I experimented with many different glassing variations which in the end caused the delay...your typical major pain. I know that you don't like the idea of placing the windows in the wall center where they belong, but in a heating climate this is really by far the better option - 20-22% increase in efficiency in your weakest part of your wall is very hard to argue against. The ARTIC wall detail makes the inset placement very easy and labor/cost wise I really don't see a difference...I understand that you don't like the looks - I hear that from clients quite often - as it is just not done normally and so seems odd at first. But this is to me really only a fashion versus function argument. You really, really want function on this part if you're in any way concerned about energy efficiency of your building...

Answered by Thorsten Chlupp
Posted Thu, 03/10/2011 - 16:07

45.
Helpful? 0

Rolling trusses made easy...

DSC_0642.jpg
Answered by Thorsten Chlupp
Posted Thu, 03/10/2011 - 16:14

46.
Helpful? 0

Thorsten, thanks very much for sharing.
It has given me a lot to think about.
SunRise home has been "grist for the mill" so to speak...
I'm looking forward to seeing further information.

I think you're really onto something here...
I agree with John B that buildability is very important.
The fact that this envelope can be made so tight with such relative ease is worth making a few compromises for.
I like "rolling trusses made easy" almost as much as I like "0.6ACH_50 made easy".

Answered by Lucas Durand - 7A
Posted Thu, 03/10/2011 - 16:29

47.
Helpful? 1

Thorsten,
Sorry about my misunderstanding of the standard REMOTE
I thought from looking at your JLC article that the ceiling air barrier was the Poly and that the Poly was put up at the same time as the drywall.

looking back at the article ...I see that I was wrong

The new method (ARCTIC)certainly lines up the layers in a way that was missing before.

Thanks for returning with more answers... I was afraid we were wearing you out ;--)

Answered by John Brooks
Posted Thu, 03/10/2011 - 16:44
Edited Thu, 03/10/2011 - 17:14.

48.
Helpful? 1

Of course build ability is VERY important. Don't matter if I can build the most efficient home on the planet if no one can afford it. I build homes for a living, that's how I feed my family and pay my bills. I have a very grand interest in Building Science and developing alternative means of heating our homes but at the end of the day I am a Builder and know how to swing a hammer.
Value engineering is a big part on any project I do...I really don't like to make things complicated or unnecessary expensive - and we spend a good amount of time perfecting details and figuring out best ways to keep costs down. On average I turn-key a home in 90 days - and we can do so because of teamwork, clear processes, quality control and efficiency. KISS rules...

John - don't you know it! No I idea how I always get sucked back over here...every time it seems I get in some silly argument which makes me sometimes wonder if I am from a different planet - gets old quickly...and I already have 5 jobs as it is.

Answered by Thorsten Chlupp
Posted Thu, 03/10/2011 - 18:07

49.
Helpful? 0

Thorsten,
Just to be clear... I admire your ARCTIC wall and Roof Deck Ceiling because it looks to be very BUILDABLE.

Answered by John Brooks
Posted Thu, 03/10/2011 - 18:17

50.
Helpful? 0

Another aspect of "buildability" that gets over-looked sometimes is that it tends to translate into lower energy methods.
"Walking" up large trusses on a deck as opposed to bringing in the boom truck for example.

I have put up large trusses by hand before. Looking at your photo Thorsten, I shake my head and wonder why anyone would want to do it another way.

Answered by Lucas Durand - 7A
Posted Thu, 03/10/2011 - 20:52

Other Questions in General questions

In General questions | Asked by Lisa MArtin | Apr 15, 14
In General questions | Asked by John Brooks | Nov 20, 10
In Mechanicals | Asked by Kent Jeffery | Apr 16, 14
In Green building techniques | Asked by Stacey Owens | Apr 17, 14
In Energy efficiency and durability | Asked by Dan Nehm | Apr 19, 14