Extra precautions on low-slope vented roof

Garajmahal | Posted in General Questions on

I’m building a shop-over-garage building in climate 6B, with 90 psf ground snow load. Due to some design constraints on height and cost, I’m not doing a fancy hot roof with vented overroof. Instead, it’s basic cathedral ceiling construction: sawn rafters with batt insulation; vapor membrane between finished ceiling and rafters; plywood deck, underlayment, and standing seam roof above rafters.

 

The roof is lower slope (mostly 2.25:12), but I’ve spent enough time with the CRREL papers/equations to convince myself I have sufficient venting. (https://www.poa.usace.army.mil/Portals/34/docs/engineering/MP5420,%20Ventilating%20Cathedral%20Ceiling%20to%20Prevent%20Problematic%20Icings%20at%20Their%20Eaves.pdf, https://www.poa.usace.army.mil/Portals/34/docs/engineering/MP-02-5778,%20Guidelines%20for%20Ventilating%20Attics%20and%20Cathedral%20Ceilings%20to%20Avoid%20Icings%20at%20Their%20Eaves.pdf)

 

I’m committed to doing a thorough air-sealing on the ceiling, and my interior design makes this fairly easy: simple roof with big open area, membrane will go up prior to interior wall construction, and very few penetrations. Of course I’m still worried, both about moisture control (even if I get the vapor barrier perfect, the roof could leak) and ice dams due to insufficient venting, and I have two lingering questions:

 

1. Should I use a smart barrier like Intello Plus? The biggest selling point (vapor-open in a humid summer) is irrelevant in my area where we have very arid summers (dew point 40-45F). I only worry about moisture in the winter.  If I have moisture issues in the winter, will drying to the inside (where inside might have a dew point of 45F) even be possible? For $1000 is it a good backup plan, or just a waste of money in my climate?

 

2. I’ll be using snow brakes and I expect the main roof ridge vent to be covered in snow for 3 months a year. I read https://www.greenbuildingadvisor.com/question/ridge-vents-being-blocked-by-snow, which suggests that it will still vent, but just perhaps not as much. The CRREL math indicates I need 7 in^2 per foot NFA of vent (per side), which isn’t insignificant. The one thing that came to mind is that the longitudinal open area of the ridge vent is somewhere in the neighborhood of 40 in^2, and I could open up downward vents on the underside of the gable overhangs at the ridge. This would add 80 in^2 of venting at the ridge, which is only a fraction of the 490 needed (35 feet of ridge over the conditioned space) and biased towards the sides of the roof. Is this worthwhile, or a waste of time?

-Mark

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. Expert Member
    MALCOLM TAYLOR | | #1

    Mark,

    I don't see any problems with your plan. 2.5/12 roofs perform fine if build diligently.

    1. I agree. Given your climate, a variable-perm vapour retarder doesn't add much that is useful. In a heating dominated climate the vapour drive is from inside to out.

    2. I would leave well enough alone, and rely on the eaves to ridge venting.

    Taking into account your desire not to complicate things too much, one option you might consider is to use a continuous membrane (like house-wrap) above your rafters instead on making baffles in each bay:
    https://www.greenbuildingadvisor.com/article/building-a-vaulted-high-performance-and-foam-free-roof-assembly
    https://www.finehomebuilding.com/2021/04/28/a-new-take-on-insulating-a-roof

  2. Garajmahal | | #2

    Thanks, Malcom. While most of my roof is 2.25:12, a smaller portion is approaching flat roof (0.6:12). Because the eave-to-vent distance is small (12 ft), the CRREL math says I'm still in the green on that portion of the roof, but part of me is worried that diligence wouldn't be enough. In the chance that water does manifest inside the roof assembly, I imagine it's possible to reverse the vapor drive, but the question being if it reverses strongly enough to do any good. Based on your response, I'm leaning towards no, and using poly sheet.

    I do enjoy the elegance of the assemblies you linked, but I'm planning on using mineral wool batt insulation. Due to building height concerns, I didn't want to furr up another 1-1/2". While unfortunately expensive, mineral wool has the thermal efficiency to let me downsize the rafters while maintaining a 1.75" airway. And AFAICT mineral wool batts are dimensionally rigid enough to eliminate the need for baffles (I live in a WUI, and I can't seem to find a suitable baffle material that is cheap, vapor-open and flame-resistant).

    1. Expert Member
      MALCOLM TAYLOR | | #3

      Mark,

      I'd make the same choices.

  3. gusfhb | | #4

    What is the roof surface going to be? The back of my current house is 2-2-1/2 and I went with EPDM because shingles had leaked for 40 years.

    1. Expert Member
      MALCOLM TAYLOR | | #5

      gusfhb,

      " it’s basic cathedral ceiling construction: sawn rafters with batt insulation; vapor membrane between finished ceiling and rafters; plywood deck, underlayment, and standing seam roof "

  4. gusfhb | | #6

    missed it

  5. Technical475_supply | | #7

    The lower the slope of the roof - the less the roof will vent. 2.25:12 is getting pretty low. Especially if covered with snow. As then there won't be much "heat" from the sun and practically stack effect (bc of the insulation) to drive ventilation to remove any unforseen moisture out. But having a way out is better than none.

    The benefit of having INTELLO Plus on the interior as you originally propose, is that you significantly reduce the amount of moisture you need to vent out.

    Vented attics in climate zones 6 and higher, have in general accumulated some condensation (and ice formation) on the inside of the sheathing depending on how well the ceiling was airsealed. It poorly airsealed, if the ridge vents were covered/slow to vent- the higher the chance for ice to form on the sheathing. And then in March the roof would appear to leak (it was just the ice melting on the inside of the sheathing).

    To prevent this - using a smart vapor retarder, and making the airtightness great. Will be good assurance. Don't forget to airseal your walls (or at least your top plates!) very well too, otherwise those stacks (your walls) might still cause a lot of moisture to end up in your roof).

    1. Expert Member
      MALCOLM TAYLOR | | #8

      457,

      Can you flesh out your explanation as to how a variable-perm membrane will reduce the moisture in the roof that needs removing more than than interior poly would? I understand your description of what goes on during cold weather, but not how substituting INTELLO would help.

  6. Technical475_supply | | #9

    The INTELLO will allow inward drying, even with dewpoints at 45F in summer. This is as the sun will shine on the roof and any unforsee moisture that accumulated in the roof is then pushed towards the smart vapor retarder. It will open up to 13 perms when this occurs. The poly will not do this. Additionally, the INTELLO as it is a system, is designed to be a airbarrier. The surface of the INTELLO received the tape well. Poly on the contrary is slick, hard to tape to and as a result making a durable airbarrier out of it, even when limiting the seams - is a challange/question.

    1. Expert Member
      MALCOLM TAYLOR | | #10

      457,

      Sorry I'm still confused. If the dew point is 45F during the summer in hot arid conditions, why would the roof need the ability to dry inwards? And during the winter when moisture may accumulate, the vapour-drive is outward, so there will be no drying to the inside through the Intello.

      I understand the benefit of a variable-perm membrane to avoid the problems an interior vapour-barrier can cause if the house is air-conditioned for prolonged periods, but I don't think there is a very convincing case for one here.

      Intello and tape is no more "part of a system" than poly and tape - and taping poly as an air-barrier has been done successfully for over 50 years.