Where can I find insulation performance curves?

BrucePPH | Posted in General Questions on

I have seen a performance curve for fiberglass insulation in the past but have not seen anything for other types of insulation. This curve plotted R-values vs. temperature. I’d like to compare the different materials side by side to better inform customers. If I remember correctly the fiberglass curve looked like a bell curve with its greatest value at 55 degrees. Does a comparison study exist?

Thanks

Bruce Chyka
Performance Plus Homes

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Bruce,
    I haven't seen such charts, but I know that Joe Lstiburek's Building Science Corp. has spent tens of thousands of dollars building a test facility to measure insulation performance at different temperatures to create just the curves you are talking about.

    They have run into a variety of technical problems, however, during the set-up process. Eventually they hope to publish their findings.

  2. Riversong | | #2

    Bruce,

    Fiberglass is almost unique among insulation materials in it's performance at different temperature differentials because it does little to restrict internal convection. The thermal conductivity of an insulating material changes little with temperature changes, but the increased delta-T causes a convective drive (stack effect) which will move air through air-permeable materials like spun glass fiber.

    For this reason, fiberglass performs poorly both at low ambient temperatures and at high ambient temperatures, in other words when thermal performance is most needed. This is particularly true of loose-fill attic insulation and less so with the newer, more dense batts and blown fiberglass.

  3. jklingel | | #3

    Bruce: I have seen, but can not find, said charts for cellulose and fiberglass batts, and the data was right on what Robert said. If I can find the *&^% file, I'll post it. Oak Ridge Labs, or someone.... did it. john

  4. Riversong | | #4

    Here's a Dupont document with some interesting temperature vs R-value curves for polyurethane foam, which is dependent on the boiling point of the refrigerant used as the blowing agent.

    http://www2.dupont.com/Formacel/en_US/assets/downloads/h54876.pdf