Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin Dickson, MSME
Posted Nov 14, 2012 1:52 AM ET
Edited Nov 14, 2012 8:28 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by Martin Holladay, GBA Advisor
Posted Nov 14, 2012 7:15 AM ET

Other Questions in Building Code Questions

Mitsubishi remote thermostat and warranty

In Green products and materials | Asked by Wayne Yamamoto | Sep 30, 16

Single versus double header for energy efficient framing.

In Green building techniques | Asked by John Ranson | Sep 30, 16

Most efficient use of 3/4" polyiso on exterior (polyiso is foil faced on both sides)

In Energy efficiency and durability | Asked by Victor Brown | Sep 29, 16

Minisplit Design for Whole House

In Mechanicals | Asked by Jimmy Black | Sep 29, 16

Basement – Best way to eliminate musty smell / mildew/ mold etc

In Green building techniques | Asked by D Moye | Sep 30, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!