Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin Dickson, MSME
Posted Nov 14, 2012 1:52 AM ET
Edited Nov 14, 2012 8:28 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by Martin Holladay
Posted Nov 14, 2012 7:15 AM ET

Other Questions in Building Code Questions

What is the best way to reduce heat gain in South facing garages?

In Energy efficiency and durability | Asked by pshyvers | Jul 22, 17

Foil faced rigid insulation

In General questions | Asked by pnjfksx | Jul 22, 17

Main stack venting

In Building Code Questions | Asked by Mike M | Jul 22, 17

Accessing a concealed duct unit

In General questions | Asked by Mark Walker | Jul 22, 17

Naive question on LEED certification

In General questions | Asked by Brian Gray | Jul 21, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!