Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin Dickson, MSME
Posted Wed, 11/14/2012 - 01:52
Edited Wed, 11/14/2012 - 08:28

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 11/14/2012 - 07:15

Other Questions in Building Code Questions

A very low addition...

In Energy efficiency and durability | Asked by ron letourneau | Oct 29, 14

Steel frame home insulation

In General questions | Asked by J B | Oct 28, 14

How to seal 4" EPS foam at slab edge (radon concerns)?

In GBA Pro help | Asked by e c | Oct 29, 14

Foundation Sealing Options?

In Energy efficiency and durability | Asked by Rob Shuman | Oct 30, 14

I am considering a double wall construction

In Energy efficiency and durability | Asked by Rick Fetter | Oct 30, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!