Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin Dickson, MSME
Posted Wed, 11/14/2012 - 00:52
Edited Wed, 11/14/2012 - 07:28

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 11/14/2012 - 06:15

Other Questions in Building Code Questions

Heat-pump water heater in conditioned space

In Mechanicals | Asked by Gerald Blycker | Nov 24, 14

Mid Roof Edge Vents / Ice Dams

In Energy efficiency and durability | Asked by Robert Eaton | Nov 23, 14

Does radiant heat recycle water

In Green building techniques | Asked by Celina Jones | Nov 22, 14

Designing a passive solar / net zero house in NC Mountains

In General questions | Asked by bill Moseley | Nov 23, 14

Help with Green Addition and hyrdonic heat demo

In Green building techniques | Asked by Michael McArdle | Nov 23, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!