Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin Dickson, MSME
Posted Nov 14, 2012 1:52 AM ET
Edited Nov 14, 2012 8:28 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by Martin Holladay, GBA Advisor
Posted Nov 14, 2012 7:15 AM ET

Other Questions in Building Code Questions

Need help with our ductwork decision

In Energy efficiency and durability | Asked by Blake Lasslett | Jul 29, 16

Double wall opening detail

In General questions | Asked by David Chapman | Jul 29, 16

Interior vapor barrier

In General questions | Asked by Phette Place | Jul 29, 16

Which way should the polyiso foil face when installing over drywall?

In Green building techniques | Asked by Michael Bluejay | Jul 30, 16

Insulating stud wall crawlspace with rigid foam

In Energy efficiency and durability | Asked by David Bump | Jul 29, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!