Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin Dickson, MSME
Posted Nov 14, 2012 1:52 AM ET
Edited Nov 14, 2012 8:28 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by Martin Holladay
Posted Nov 14, 2012 7:15 AM ET

Other Questions in Building Code Questions

Insulating an attic-based minisplit indoor unit & ductwork

In Green building techniques | Asked by Brian Gray | May 26, 17

How does someone cancel subscription when there seems to be no way out??

In General questions | Asked by James Someone | May 27, 17

Understanding HRV Energy Use Calculations

In Energy efficiency and durability | Asked by Venkat Y | May 27, 17

How can I effectively resolve an issue of next door neighbor's cigarette smoke seeping into my apartment?

In Energy efficiency and durability | Asked by user-6855474 | May 26, 17

Vapor Barrier when using Excel II as Air Barrier

In Green products and materials | Asked by Thomas Kaempfen | May 27, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!