Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin Dickson, MSME
Posted Nov 14, 2012 12:52 AM ET
Edited Nov 14, 2012 7:28 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by Martin Holladay, GBA Advisor
Posted Nov 14, 2012 6:15 AM ET

Other Questions in Building Code Questions

Excessive Moisture in Minnesota

In Mechanicals | Asked by Z Lessin | Dec 10, 16

How do I get rid of A LARGE AMOUNT of attic moisture

In Mechanicals | Asked by Scott Hill | Dec 10, 16

I need insulation help in Baltimore

In Energy efficiency and durability | Asked by David Soderblom | Dec 10, 16

Lunos e2 ductless HRV system vs. ducted system

In Mechanicals | Asked by Courtney McCracken | Dec 8, 16

I recently had a metal roof installed on my house

In General questions | Asked by Linda DuBois | Dec 10, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!