Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin Dickson, MSME
Posted Wed, 11/14/2012 - 01:52
Edited Wed, 11/14/2012 - 08:28

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 11/14/2012 - 07:15

Other Questions in Building Code Questions

Insulation design

In GBA Pro help | Asked by Robert Brown | Oct 17, 14

Curbless shower with a PVC liner -- how to terminate the liner at the floor?

In General questions | Asked by john walls | Oct 19, 14

Rising power plant energy cost

In Energy efficiency and durability | Asked by Terry Lee | Oct 15, 14

Enclosed room on slab

In Energy efficiency and durability | Asked by Jason Schatz | Oct 16, 14

An outside, completely isolated, balcony column structure

In General questions | Asked by peter mare | Oct 20, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!