Duct-free bath fans?

Does anyone have experience with these?

Do they satisfy the IRC 2009 code for a powder room (just toilet & sink)?

http://www.westsidewholesale.com/duct-free-powered-air-freshener-bath-fa...

Asked by Kevin_in_Denver
Posted Nov 14, 2012 12:52 AM ET
Edited Nov 14, 2012 7:28 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

The 2009 IRC only requires bathroom exhaust fans if the bathroom lacks an operable window that measures at least 3 square feet.

Assuming that the bathroom lacks an operable window of the minimum size, the code requires the installation of an exhaust fan that moves at least 50 cfm. Furthermore, the code requires that "Ventilation air from the space shall be exhausted directly to the outside" -- which means that you can't use the recirculating fan that you linked to.

As usual, the building code in California differs from the 2009 IRC. Section 1203.4.2.1 of California's building code requires all bathrooms with a bathtub, shower, spa or similar fixtures to be ventilated by an exhaust fan.

Answered by user-756436
Posted Nov 14, 2012 6:15 AM ET

Other Questions in Building Code Questions

Need advice on insulating walls

In General questions | Asked by Martin Holladay | Feb 20, 17

National Fiber in Belchertown, Mass.

In Green products and materials | Asked by Scott Mangold | Feb 21, 17

Under tile electrical heating - Schluter Ditra Heat system 2017

In Green products and materials | Asked by Ryan Kennedy | Feb 20, 17

Whole House Ventilation

In General questions | Asked by N/A N/A | Feb 21, 17

Paint OSB subfloor to protect from rain during slow construction?

In General questions | Asked by Jeff Cooper | Feb 21, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!