Insufficiently thick exterior foam: Remove, increase, ignore?

Hi there,

I've been reading the articles on GBA about exterior foam and I think mine is too thin to keep the sheathing above the dew point. I'm wondering your opinions as to the best remedy. I'm assuming that removing or increasing the thickness will both be expensive. I believe my wall assembly is risky, but have no evidence it is actually a problem. Given that I'm wondering if the best course of action is to live with it. Here are the details:

- 2 x 4 walls
- .75" polyiso
- Plywood sheathing
- No rain screen
- Stud cavities filled with fiberglass batts
- No interior vapor barrier
- Climate zone 6 (Cabot, VT)

Greatly appreciate your thoughts.

Asked by Jeremiah Breer
Posted Mar 19, 2017 5:26 PM ET
Edited Mar 20, 2017 12:41 PM ET

Tags:

6 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Maybe Kohta will chime in hear, but he and John Straube gave a presentation at NESEA this month talking about moisture of course. I believe they were looking at CZ 6 with 50% indoor humidity and the worst scenario was a wall assembly that had rigid foam on the outside, but nowhere near enough. It allowed condensation to develop, but it hindered drying to the outside.

Answered by Jonathan Lawrence CZ 4A New Jersey
Posted Mar 19, 2017 6:01 PM ET

2.

Jeremiah,
Tough call -- but if it were my house, I'd probably do nothing. Just engage in "watchful waiting."

The lower your interior relative humidity during the winter, the lower your risk. So you might want to buy a few hygrometers. Operate your ventilation system to keep your winter interior RH at 30% or below.

When it's time for remodeling, inspect what's going on. Good luck.

-- Martin Holladay

Answered by Martin Holladay
Posted Mar 19, 2017 7:02 PM ET
Edited Mar 19, 2017 7:02 PM ET.

3.

- 2 x 4 walls
- .75" polyiso
- Plywood sheathing
- No rain screen
- Stud cavities filled with fiberglass batts
- No interior vapor barrier
- Climate zone 6 (Cabot, VT)

If the sheeting is on outside of the foam you should be OK. Your assembly looks a lot like the ZipR walls.
I looked at the ZipR wall and I do not recall seeing any climate zone rules.

If you want to be certain use an Inferred camera to find your coldest spot open up the wall and see if you find any mold.

Walta

Answered by Walter Ahlgrim
Posted Mar 19, 2017 10:23 PM ET

4.

Walter,
The rules for the minimum R-value of exterior rigid foam apply to Zip-R sheathing as well as to the walls built by Jeremiah Breer in Cabot, Vermont. For more information on these rules, see Calculating the Minimum Thickness of Rigid Foam Sheathing.

If your Zip-R sheathing has too low an R-value, or if Jeremiah's layer of rigid foam has too low an R-value, the interior face of the rigid foam won't stay warm enough during the winter to avoid condensation. You'll end up with beads of water or frost on the interior face of the rigid foam. This moisture can drip down and form puddles on the bottom plate. Eventually, you can get mold or rot on your bottom plate.

-- Martin Holladay

Answered by Martin Holladay
Posted Mar 20, 2017 6:22 AM ET

5.

The most important first step is to verify that the wallboard is air-tight, since air convection from the interior into the cavities moves a LOT more moisture in than vapor diffusion through standard interior latex paint. Chasing the leaks down with a blower door (or a large window fan, room by room) can start at any time. Use a decent long lasting flexible caulk (polyurethane caulks are good). You may have to pull some floor/window/ceiling trim to really nail it all in an aesthetic fashion.

The most susceptible walls will be those that get no or minimal sun, such as north facing walls or shaded walls. If possible, paint those walls with half-perm "vapor barrier latex primer", but wait at least until July/August to allow plenty of warm weather drying time for the sheathing. Half perm paint goes a long way toward limiting peak moisture, but it slows drying.

Answered by D Dorsett
Posted Mar 20, 2017 9:22 AM ET

6.

+1 on air sealing and low humidity. Also note that if you keep the interior at a lower air pressure than the exterior, air won't leak outward - even with never-perfect air sealing.

Answered by Jon R
Posted Mar 20, 2017 11:53 AM ET

Other Questions in Energy efficiency and durability

Drainwater heat recovery questions

In Mechanicals | Asked by Calum Wilde | Jun 26, 17

Does the insulation on this wall make sense?

In Green building techniques | Asked by user-6832947 | Jun 27, 17

What type of sealant?

In General questions | Asked by Tim R | Jun 27, 17

Concrete slab reinforcement: M100 vs. F100 fibers: finish and strength

In GBA Pro help | Asked by Mai Tai | Jun 25, 17

Baffles and blocking at eaves (retrofit)

In Energy efficiency and durability | Asked by Jeff Classen | Jun 26, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!