Duct location, unvented attics

In the Building Science America series unvented attics are recommended; "as long as they have airtight ceilings and the ductwork is not in unconditioned space". So how do you put in ductwork in conditioned space? I don't really want to use spf around the whole ductwork. Burying it in FG or cellulose doesn't keep it from causing condensation when it carries the air conditioning. Where is the ductwork to be placed?

Asked by Michael McKinley
Posted Sat, 11/24/2012 - 13:04

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Between floors in open web floor trusses.

Answered by John Semmelhack
Posted Sat, 11/24/2012 - 15:02

2.
Helpful? 0

Michael,
Here's an article that addresses your exact question: Keeping Ducts Indoors: Five ways to bring ducts inside a home’s conditioned space.

Answered by Martin Holladay, GBA Advisor
Posted Sat, 11/24/2012 - 16:05

3.
Helpful? 0

Is an unvented attic recommended if we have ducts in the attic, but we do not have air conditioning. We live near San Francisco so outdoor temps rarely exceed 80 deg F. Right now we have a rectangular house with a pitched roof and gable vents on either end. Given that heating energy is our biggest concern, should the attic be vented or unvented?

Answered by chris Y
Posted Sat, 11/24/2012 - 17:03

4.
Helpful? 0

Chris,
It always makes sense to keep your ductwork inside your home's conditioned space. It makes no difference whether the ducts are used for heating, or air conditioning, or both.

If your ducts are located in your attic, you want an unvented conditioned attic. Your heating system will perform better and will be more efficient if you have an unvented conditioned attic than if you have a vented attic.

Here is an article with more information: Creating a Conditioned Attic.

Answered by Martin Holladay, GBA Advisor
Posted Sun, 11/25/2012 - 07:03
Edited Sun, 11/25/2012 - 07:04.

Other Questions in Energy efficiency and durability

Thinking of going solar

In Green building techniques | Asked by Ron Davis | Sep 19, 14

Would Tyvek on top of rafters and under roof sheeeting meet R806.4 for non-vented attics?

In Building Code Questions | Asked by Elmo Saunders | Sep 22, 14

The differences between mass and insulation

In Green products and materials | Asked by Nathaniel G | Sep 15, 14

Help with basement design

In Green building techniques | Asked by leonid grossman | Sep 21, 14

Sealing gap between garage floor & drywall?

In Green building techniques | Asked by Robert Hallenbeck | Sep 20, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!