New Construction Venting, 2:12 metal shed roof at wall?

Planning my new home construction. Modern design 2:12 metal standing seam shed roofs.
Zone 5/B dry R-38 minimum, I want more. + Can get 4' snow.

All 3 roofs will include TJI's running full length from eve to top. 5/8" CDX sheathing, 30# roofing felt with Gracy's Ice & water shield at eves.

Center great room/ kitchen (36' deep x 28' wide) will be18' high at front of house & 12' at rear, easiest to vent.

Both bedroom wing roofs will slope away from the center great room. They will both join onto the outside walls of the great room below its 2' overhanging roof.

My concern is venting this low slope to wall intersection. I have googled & found several designs that would work if a bunch of snow was not piled up on them.

I'm thinking of building 1.5" verticle vent chutes into the exterior of the walls up to the soffits.

Ideas?

Asked by james patrick
Posted Jan 23, 2013 3:41 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

James,
Choose one of the commercial products designed for venting shed roofs that die into walls -- or design an unvented roof.

For information on insulating an unvented cathedral roof, see How to Build an Insulated Cathedral Ceiling.

Answered by Martin Holladay, GBA Advisor
Posted Jan 23, 2013 4:33 PM ET

Other Questions in Energy efficiency and durability

The Smartphone Society

In Green building techniques | Asked by Grady Rosson | Jan 24, 17

IPhone7 Reports, Videos, Gossip and reviews

In Green building techniques | Asked by Virginia Wilhite | Jan 24, 17

Highlighting YOUR LOOK With Leather IPhone 3g Accessories

In Green building techniques | Asked by Maxie Broun | Jan 24, 17

The Realities Regarding A $50 Smartphone

In Green building techniques | Asked by Gretchen Bushell | Jan 24, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!