Flash and Batt foam thickness

I'm in NJ climate zone 5 and have a project with an installed falsh and batt with 1" closed cell foam and Roxul batt in wood framing. I usually spec 2"+ but would like to avoid ripping everything apart and spraying more foam. Is there a chart/rule-of-thumb anywhere showing wtih of foam based on climate zone averages or any specific data to justify thickness besides doing a calc? This seems like a case where it would probably be ok but with a small chance for a big problem??

Asked by Michael Margulies
Posted Jan 25, 2013 10:33 AM ET
Edited Jan 25, 2013 10:35 AM ET


1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.

Relax -- your walls should be fine.

The guidelines you are looking for can be found in either of these two articles:

Calculating the Minimum Thickness of Rigid Foam Sheathing (Look for the paragraph with the headline, "What about flash-and-batt jobs?")

Why Flash and Batt Makes Sense ("According to building scientist Joseph Lstiburek, flash-and-batt installations require at least 1 inch of spray foam in climate zone 5, 1 1⁄2 inch in zone 6, and 2 inches in zone 7.")

Answered by Martin Holladay, GBA Advisor
Posted Jan 25, 2013 10:40 AM ET

Other Questions in Energy efficiency and durability

Recommendations for a small HRV

In Mechanicals | Asked by Carlo Giombi | Oct 12, 15

Two backdrafting appliances and dust — Do I need an HRV?

In Mechanicals | Asked by J Pritzen | Nov 26, 15

Best practices for HRV on a budget

In Energy efficiency and durability | Asked by Kail Zuschlag | Nov 29, 15

Adding foam board to ceiling rafters?

In Green building techniques | Asked by Donald Mendell | Nov 29, 15

Questions about insulating 1947 concrete block home in Florida

In General questions | Asked by Nathan Vaughn | Nov 29, 15
Register for a free account and join the conversation

Get a free account and join the conversation!
Become a GBA PRO!