Flash and Batt foam thickness

I'm in NJ climate zone 5 and have a project with an installed falsh and batt with 1" closed cell foam and Roxul batt in wood framing. I usually spec 2"+ but would like to avoid ripping everything apart and spraying more foam. Is there a chart/rule-of-thumb anywhere showing wtih of foam based on climate zone averages or any specific data to justify thickness besides doing a calc? This seems like a case where it would probably be ok but with a small chance for a big problem??

Asked by Michael Margulies
Posted Jan 25, 2013 10:33 AM ET
Edited Jan 25, 2013 10:35 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
1 Helpful?

Michael,
Relax -- your walls should be fine.

The guidelines you are looking for can be found in either of these two articles:

Calculating the Minimum Thickness of Rigid Foam Sheathing (Look for the paragraph with the headline, "What about flash-and-batt jobs?")

Why Flash and Batt Makes Sense ("According to building scientist Joseph Lstiburek, flash-and-batt installations require at least 1 inch of spray foam in climate zone 5, 1 1⁄2 inch in zone 6, and 2 inches in zone 7.")

Answered by Martin Holladay, GBA Advisor
Posted Jan 25, 2013 10:40 AM ET

Other Questions in Energy efficiency and durability

Poly on interior wall

In Energy efficiency and durability | Asked by Nicholas C | Jan 31, 15

Does code require fireproof caulk around electrical boxes & light switches?

In Building Code Questions | Asked by Robert Hallenbeck | Jan 31, 15

Freeze risk for a heat pump water heater in an unconditioned garage

In Mechanicals | Asked by Nathaniel G | Jan 31, 15

How do I keep my sheathing dry?

In Energy efficiency and durability | Asked by David Baerg | Jan 30, 15

Adding A/C to 1918 built home

In Mechanicals | Asked by Brian Forney | Jan 31, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!