Flash and Batt foam thickness

I'm in NJ climate zone 5 and have a project with an installed falsh and batt with 1" closed cell foam and Roxul batt in wood framing. I usually spec 2"+ but would like to avoid ripping everything apart and spraying more foam. Is there a chart/rule-of-thumb anywhere showing wtih of foam based on climate zone averages or any specific data to justify thickness besides doing a calc? This seems like a case where it would probably be ok but with a small chance for a big problem??

Asked by Michael Margulies
Posted Jan 25, 2013 11:33 AM ET
Edited Jan 25, 2013 11:35 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Michael,
Relax -- your walls should be fine.

The guidelines you are looking for can be found in either of these two articles:

Calculating the Minimum Thickness of Rigid Foam Sheathing (Look for the paragraph with the headline, "What about flash-and-batt jobs?")

Why Flash and Batt Makes Sense ("According to building scientist Joseph Lstiburek, flash-and-batt installations require at least 1 inch of spray foam in climate zone 5, 1 1⁄2 inch in zone 6, and 2 inches in zone 7.")

Answered by Martin Holladay
Posted Jan 25, 2013 11:40 AM ET

Other Questions in Energy efficiency and durability

Spray foam questions

In General questions | Asked by Stanger133 | May 20, 18

Is it worth creating a conditioned attic for my house?

In Energy efficiency and durability | Asked by CGFears | May 23, 18

Spray foam from crawlspace onto bottom of plank subfloor in Pacific NW?

In Energy efficiency and durability | Asked by Frasca | May 21, 18

Fasteners for concrete, brick, and CMUs

In General questions | Asked by Martin Holladay | May 23, 18

Vaulted / Cathedral Ceiling -- Unvented

In Green building techniques | Asked by user-7075735 | May 23, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!