Martin Holladay, if you are out there, or etal:

Martin some time ago you posted a reply to Gary Steinfeld where you stated "you can use rigid foam to create a ventilation channel." I like this idea and would like to plan on using a foam ventilation channel in a cathedral ceiling application, followed by FG between the rafters and another layer of foam on the underside of the rafters. Some have suggested firmly that the vent channels be WELL air sealed.

My concern is that this method might trap any mositur which might get into the FG. Of course the goal would be to air seal the underside foam and the upper side so as to not have a moisture issue, BUT.....!

Martin since suggested that this method was ok and you are a GBA Advisor could you comment.

Thank you.

Asked by Bob Brown
Posted Sat, 03/09/2013 - 14:54
Edited Sat, 03/09/2013 - 17:07

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 1

Bob,
As you wrote, "Martin since suggested that this method was OK."

Martin still suggests that this method is OK.

If you use EPS or XPS foam to create the ventilation channel, and the foam is 1 inch thick (or less), it will be somewhat vapor-permeable and will allow some drying to the exterior in a pinch. I think everything will be fine.

Answered by Martin Holladay, GBA Advisor
Posted Sat, 03/09/2013 - 17:10

2.
Helpful? 0

A follow-up to Martin

I had been thinking of using 1 1/2 inches of foam for the shoots, but 1" would be fine. 1. Do you agree with air sealing the shoots?

2. What type of foam would you then recommend for the underside of the rafters and would you still add a "vapor barrier" (ie plastic) to the underside of that foam? Naturally tape seems on the foam.

Thank you again.

Answered by Bob Brown
Posted Sat, 03/09/2013 - 17:56
Edited Sat, 03/09/2013 - 18:05.

3.
Helpful? 0

Bob,
Q. "Do you agree with air sealing the shoots?"

A. Yes. More information here: How to Build an Insulated Cathedral Ceiling.

Q. "What type of foam would you then recommend for the underside of the rafters?"

A. Any type of rigid foam will work, but foil-faced polyiso is the most environmentally friendly foam, and is also the easiest to tape.

Q. "Would you still add a vapor barrier (i.e. plastic) to the underside of that foam?"

A. No. Foil-faced polyiso is already a vapor barrier. More information here: Do I Need a Vapor Retarder?

Answered by Martin Holladay, GBA Advisor
Posted Sun, 03/10/2013 - 06:31
Edited Sun, 03/10/2013 - 06:32.

Other Questions in Energy efficiency and durability

In Energy efficiency and durability | Asked by David Gregory | May 24, 13
In General questions | Asked by erik olofsson | May 22, 13
In General questions | Asked by Ben Hardy | May 23, 13
In Energy efficiency and durability | Asked by Ben Hardy | May 23, 13
In Green building techniques | Asked by Gordon B | May 23, 13
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!