EPS over polyiso on reroof?

So based on everything thing I am reading should we be using R3 R4 or R5 for each inch of Polyiso since it decreases in performance as it gets colder. I seem to be seeing some variation in Answers. I am in zone 5 and was planning on putting 5 inches of Polyiso.(thinking that was R 30 Roughly but if is is only R 15 when coldest that is a problem) Now it seems like I would be better served with three inches of polyiso with EPS on top. I have access to 1.5 or 2.75 inch EPS. Would I still be OK with 3 inches of polyiso and 2.75 inch of EPS on top?

Asked by terry grube
Posted Aug 29, 2014 5:33 PM ET
Edited Aug 30, 2014 5:33 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Terry,
Q. "Would I still be OK with 3 inches of polyiso and 2.75 inch of EPS on top?"

A. Yes. The EPS will warm up the polyiso and improve its performance.

In your climate zone, an unvented hybrid cathedral ceiling only needs R-20 of rigid foam insulation above the roof sheathing. Your plan -- about R-18 of polyiso capped by R-11 of EPS -- will give you about R-29 of rigid foam.

Answered by Martin Holladay, GBA Advisor
Posted Aug 30, 2014 5:40 AM ET

Other Questions in Energy efficiency and durability

Can rigid insulation be safely used in the center of a double stud wall?

In Green building techniques | Asked by Jason Whitacre | Nov 30, 16

Insulating a wall that is half plaster/half drywall?

In General questions | Asked by Al Ciu | Dec 2, 16

Another crawl space in the Northwest

In Energy efficiency and durability | Asked by David Meyer | Nov 28, 16

How important is a thermal break between a house foundation and an attached garage foundation?

In Green building techniques | Asked by Eric Whetzel | Dec 2, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!