EPS over polyiso on reroof?

So based on everything thing I am reading should we be using R3 R4 or R5 for each inch of Polyiso since it decreases in performance as it gets colder. I seem to be seeing some variation in Answers. I am in zone 5 and was planning on putting 5 inches of Polyiso.(thinking that was R 30 Roughly but if is is only R 15 when coldest that is a problem) Now it seems like I would be better served with three inches of polyiso with EPS on top. I have access to 1.5 or 2.75 inch EPS. Would I still be OK with 3 inches of polyiso and 2.75 inch of EPS on top?

Asked by primitivelamps
Posted Aug 29, 2014 5:33 PM ET
Edited Aug 30, 2014 5:33 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Terry,
Q. "Would I still be OK with 3 inches of polyiso and 2.75 inch of EPS on top?"

A. Yes. The EPS will warm up the polyiso and improve its performance.

In your climate zone, an unvented hybrid cathedral ceiling only needs R-20 of rigid foam insulation above the roof sheathing. Your plan -- about R-18 of polyiso capped by R-11 of EPS -- will give you about R-29 of rigid foam.

Answered by user-756436
Posted Aug 30, 2014 5:40 AM ET

Other Questions in Energy efficiency and durability

Crawl space insulation

In Energy efficiency and durability | Asked by Barbara Rowland | Feb 27, 17

Can you plaster over spray on insulation?

In Interior design | Asked by N/A N/A | Feb 28, 17

Problem with moisture in attic and second-floor ceiling of unheated house

In General questions | Asked by John Oliver | Feb 27, 17

Casement windows?

In Green building techniques | Asked by N/A N/A | Feb 26, 17

Knee Wall Access Doors

In General questions | Asked by Jeff Towson | Feb 27, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!