EPS over polyiso on reroof?

So based on everything thing I am reading should we be using R3 R4 or R5 for each inch of Polyiso since it decreases in performance as it gets colder. I seem to be seeing some variation in Answers. I am in zone 5 and was planning on putting 5 inches of Polyiso.(thinking that was R 30 Roughly but if is is only R 15 when coldest that is a problem) Now it seems like I would be better served with three inches of polyiso with EPS on top. I have access to 1.5 or 2.75 inch EPS. Would I still be OK with 3 inches of polyiso and 2.75 inch of EPS on top?

Asked by terry grube
Posted Aug 29, 2014 5:33 PM ET
Edited Aug 30, 2014 5:33 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
0 Helpful?

Terry,
Q. "Would I still be OK with 3 inches of polyiso and 2.75 inch of EPS on top?"

A. Yes. The EPS will warm up the polyiso and improve its performance.

In your climate zone, an unvented hybrid cathedral ceiling only needs R-20 of rigid foam insulation above the roof sheathing. Your plan -- about R-18 of polyiso capped by R-11 of EPS -- will give you about R-29 of rigid foam.

Answered by Martin Holladay, GBA Advisor
Posted Aug 30, 2014 5:40 AM ET

Other Questions in Energy efficiency and durability

Heat pump water heater for radiant floor heat?

In General questions | Asked by Clayton Hufford | Jan 31, 15

Code Required - Electric Resistance Heater

In Mechanicals | Asked by Peter L | Jan 31, 15

How do I keep my sheathing dry?

In Energy efficiency and durability | Asked by David Baerg | Jan 30, 15

Order of upgrades

In Energy efficiency and durability | Asked by Daniel Gillen | Jan 28, 15

How can I stop snow from blowing into my soffit vents and up the attic vent chutes?

In General questions | Asked by Lynn Braff | Jan 30, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!