EPS over polyiso on reroof?

So based on everything thing I am reading should we be using R3 R4 or R5 for each inch of Polyiso since it decreases in performance as it gets colder. I seem to be seeing some variation in Answers. I am in zone 5 and was planning on putting 5 inches of Polyiso.(thinking that was R 30 Roughly but if is is only R 15 when coldest that is a problem) Now it seems like I would be better served with three inches of polyiso with EPS on top. I have access to 1.5 or 2.75 inch EPS. Would I still be OK with 3 inches of polyiso and 2.75 inch of EPS on top?

Asked by terry grube
Posted Fri, 08/29/2014 - 17:33
Edited Sat, 08/30/2014 - 05:33

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Terry,
Q. "Would I still be OK with 3 inches of polyiso and 2.75 inch of EPS on top?"

A. Yes. The EPS will warm up the polyiso and improve its performance.

In your climate zone, an unvented hybrid cathedral ceiling only needs R-20 of rigid foam insulation above the roof sheathing. Your plan -- about R-18 of polyiso capped by R-11 of EPS -- will give you about R-29 of rigid foam.

Answered by Martin Holladay, GBA Advisor
Posted Sat, 08/30/2014 - 05:40

Other Questions in Energy efficiency and durability

Is this furnace venting/leaking problem as bad as it looks?

In Mechanicals | Asked by Nathaniel G | Dec 20, 14

Wet OSB - how much water can it take?

In General questions | Asked by colleen1 runyen | Dec 17, 14

Polyiso for basement

In Green building techniques | Asked by sr kod | Dec 20, 14

Solar thermal systems for heating water

In Mechanicals | Asked by aj builder, Upstate NY Zone 6a | Dec 15, 14

Closed-cell spray foam on roof deck... shingle underlayment choice?

In General questions | Asked by Mark Helmrich | Dec 19, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!