Wondering if there are any drawbacks/issues with using cardboard ventilation baffles? We made our own baffles out of foam sheathing for the last two homes we built to create an air tight insulation cavity between rafters. Needless to say it is a very time consuming and costly process, especially with a few volume ceilings.

We just experimented making baffles out of a sheet of cardboard and we think we could create, install, and seal these cardboard baffles in a fraction of the time it would take with other materials.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Bruce,
    Plenty of people use cardboard ventilation baffles. You can buy them:

    J&R - Cardboard Attic Baffles

    Bafflo baffles

    As with any ventilation strategy, the usual warnings apply: pay attention to airtightness, and make sure that the R-value of your insulation is high enough. More information here: How to Build an Insulated Cathedral Ceiling.

  2. snfh | | #2

    Thanks Martin. I'm familiar with both manufacturers and many others. There are flaws in the designs of all these products and most are not long enough to be installed in a single pass. So, I plan to make my own as long as I can be assured that the cardboard itself poses no risk (moisture/mold) as long as it is properly installed.

  3. GBA Editor
    Martin Holladay | | #3

    Bruce,
    If you are installing cellulose, the question is simple: will the cardboard be stiff enough to resist the pressures induced by the blowing machine?

    If you are installing fiberglass batts, then the cardboard is certainly stiff enough -- but you still have all of the inherent disadvantages of fiberglass batts.

  4. snfh | | #4

    I am installing cellulose and will test cardboard on the next house. Our test chutes are fairly rigid (if stapled close to the crease of the flap) and seem like they will withstand the pressure of a blowing machine . I guess the only way to know for sure is to test it.

  5. mrgregpittman | | #5

    I found one of the article on the Yahoo! Voices that might help you to understand more

    http://voices.yahoo.com/how-install-choose-baffles-attic-1427873.html

  6. Foamer | | #6

    Bruce,
    I came across your question while browsing for a better baffle - a search that is ongoing. We have installed pretty much every baffle out there and I don't like any of them. Cardboard is adaptable and plenty strong at the time of install but does not hold up well over time. Styrofoam is too flimsy and require additional work to block the eaves. Site built systems are very labor intensive. I did find a product that installs like a cardboard baffle but is made of fluted plastic. If you can swallow the cost, this may be your best option (http://www.dciproducts.com/html/smartbaffle.htm).

  7. user-917856 | | #7

    Bruce,

    I saw these baffles at EEBA in 2006. They are recycled plastic, very durable (can't be torn) and they offer a "high energy" version for deeper attic insulation. Call them and see if you can get some free samples.

    http://www.brentwoodindustries.com/spg/building-products/index.aspx

  8. snfh | | #8

    Torsten,

    Thanks for the feedback. My experience is pretty much the same as yours. I wish I could see some 30-50 yr old cardboard baffles to see how they are holding up but that will probably never happen.
    I did order a box of the smartbaffles and experimented with them. They work for standard spacing and are a bit of a pain for non-standard spacing. Anyone could make smartbaffles with a sheet of corrugated plastic for less money.

  9. r5portals | | #9

    Here are photos of cardboard baffles at thirty years of service:
    https://drive.google.com/open?id=0Byj-qncyomXmRjhVcUN3QUtYVEU

    Perhaps coated cardboard lasts longer. I doubt it, where bare cardboard side exposed, may curl more. Manufacturers do not offer a service life guarantee.

    Let's emphasize plywood as the best solution. Where most bird block is like that in the photos, know tiny hole area demands placement in every bay.

  10. user-5946022 | | #10

    What about making rafter baffles out of 4x8 sheets of 1/2" polyiso the big box sells. These have foil on one side so with the foil face down they could also serve as a radiant barrier.

    Has anyone ever done this, and is the scored polyiso strong enough to resist both the force of blown cellulose and the raves of time (that photo of the 30 year old cardboard baffles is scary...) If so, other than the fabrication time, is there a downside? You could fabricate them so you get the full 2" depth or more that some articles advocate.

    1. Expert Member
      BILL WICHERS | | #11

      1/2” polyiso is used for this all the time. The foil side facing up helps as a radiant barrier to keep the attic a little cooler, but I wouldn’t use polyiso just for this. Facing the foil down doesn’t do anything if it will be pressed against some other type of insulation since a radiant barrier needs an air gap to work. Polyiso is rigid enough to spray insulation against unless you try to span something a lot more than the standard rafter spacing.

      Polyiso holds up pretty well. I just pulled out some in a renovation in part of my house that is about 40 years old. It is just like new except for the exposed polyiso on the edges being yellowed. It’s still rigid, in one piece, and insulating just fine.

      Bill

      1. user-5946022 | | #12

        Thanks for the reply. Did you insert a block into the rafters, glue something to the polyiso, or just score and bend it? I'm considering this solution over the expensive DCI Smartbaffle. It would get the full 2" of vent space.

        I'd put the reflective side down; per other articles here putting it up it gets dusty and eventually does not work. Only a small part of it would be in contact with the insulation under it - the rest could act as a nice radiant barrier

        Working in an existing condition so I'm trying to avoid as much in place work as possible; I'd like something I can just slide it in there and secure with a staple on each side. A baffle created by scoring polyiso relies on the foil side polyiso to hold the thing together - I'm concerned it would tear either from the cellulose pressure or over time.
        Taping the score does not seem like a good option as I presume the attic heat would eventually overcome any adhesive. Any easy way to fabricate these so they are sturdy and stay and work in attic is limited?

        I watched this video: https://www.finehomebuilding.com/2016/06/29/rigid-foam-vent-baffles. Thought I would use the same system but stop the scoring 4" short of the high end. I'd score that last 4" on the other side and fold that section the other direction to use as a staple flange.