We are renovating a 900 sq. foot basement apartment in Beacon, NY (Hudson Valley - area code 12508). It's partly below grade, and pretty tight with new double pane windows.

We're thinking of putting in an ERV for ventilation since:
1) We think that having the availability of ventilation in the basement apartment is a good thing.
2) We've noticed a slight mustiness in there.

We just got the house and need to do the reno pretty quickly, so can't take things like RH across multiple seasons. We could test for air tightness, but it seems pretty tight upon inspection by our contractor.

We're leaning toward the ERV because:
1) There will be some energy savings (though from what I've read not a very big amount)
2) It seems to give a more conditioned air coming in than plain ventilation (e.g. somewhat warmer air in winter and cooler in summer than with straight ventilation).

We'll probably add some dehumidification with a portable unit if it turns out to be needed (the previous occupants said they did that in the summer, and that was all they needed - no AC). We may be able to hook it up to a drain to eliminate the need to empty the unit.

Any thoughts on the above?

How would the above compare to having a ventilating dehumidifier? I'm concerned that would bring in cold air in winter, hot air in summer when ventilating.

Pros/cons of each approach?

Thanks very much in advance,
Yaakov

Asked by Yaakov Weintraub
Posted May 15, 2014 6:54 AM ET
Edited May 15, 2014 8:46 AM ET

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Yaakov,
Ventilation and dehumidification are two different operations. If you operate a ventilation system during cold weather, the ventilation air will help reduce indoor humidity. If you operate a ventilation system during hot, humid weather, the outdoor air will raise the indoor humidity level and increase the load on your dehumidifier. So if you suspect that your basement is damp, you should be careful not to overventilate during the summer.

Ventilation needs for a 900-square-foot apartment will be quite low. If you go ahead with your plan to install an ERV, make sure that you verify the exhaust and supply airflow rates -- in other words, make sure that you commission the system -- so that you know your ventilation rate and adjust it to the level you want.

For more information, see Designing a Good Ventilation System.

Answered by Martin Holladay
Posted May 15, 2014 8:34 AM ET

2.

Thank you. The ERV we are considering has a fairly wide range of adjustments on both exhaust and supply airflow, and we can use those to commission the system. That's one reason we chose it. The guidelines on this seem to be difficult to figure out - there are standards, but they're not necessarily the best choice. The ventilation apparently depends a lot on the level of contaminants in the home. For a low emission home, it makes sense to follow or under-ventilate compared to the standards, while for a high emission home, it makes sense to over-ventilate compared to the standards. Is there an easy way to determine if this is a low-emission, or high-emission? I know that we are using low-emission products in all the renovation (e.g. no-formaldehyde flooring and zero VOC paint and finishes), but there is also pre-existing construction in there.

Answered by Yaakov Weintraub
Posted May 15, 2014 10:25 AM ET

Other Questions in GBA Pro help

How to keep pine siding from greying

In General questions | Asked by tech1234 | Jun 23, 18

Conventional heat pumps with mini-split low temp efficiency?

In Mechanicals | Asked by Mai Tai | Jun 22, 18

Bubble-wrap air space 2" below in-joist radiant floor heating

In Energy efficiency and durability | Asked by user-6765846 | Jun 23, 18

Fastening Exterior pine trim to an ICF home

In Green building techniques | Asked by Wayde | Jun 23, 18

Dirty electric from minisplit ductless heat and air conditioning

In General questions | Asked by Arleendv | May 30, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!