Oversizing a multi-zone inverter heat pump - does it matter?

I'm trying to figure out a strategy to heat a large one level house with many rooms, and it seems that a multi-zone mini split could give me the overall capacity I need with the greatest comfort. But I've also seen many warnings about oversizing and its ultimate effect on COP, which makes me a bit nervous.

Looking at the heat pump specs, though, I'm confused as to why there would be a problem. My heating contractors aren't necessarily heat pump engineers, so I'd like to run some thoughts by the contributors to see where I might be off base.

Looking at the lineup of Mitsubishi H2i unit submittal sheets, it seems that they all have about the same low end of the capacity range - roughly 7KBtu/h. So whether I pick a 48 or a 20, the unit can modulate down to the same level. I see no downside in sizing for max capacity, or am I missing something?

The indoor unit capacities are a bit more mysterious to me. If I have a 12K indoor unit, can it operate down to the 7K minimum from the outdoor unit? Or is the unit always at its max capacity for a given return air temp? And if two units call for heat, can the 7K be "split" between them?

Thanks

Asked by rk2
Posted Feb 11, 2018 12:09 PM ET

Tags:

9 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Correct, short run-time/oversizing is about minimum capacity - not maximum.

I'll speculate that the larger model would have a larger heat exchanger, making it more efficient. And a larger compressor - increasing compressor life for a give load. On the other hand, a larger compressor operating at the same 7KBtu/h may reduce pumping efficiency. For a similar price and minimum output, I'd get the larger outdoor unit.

Answered by Jon R
Posted Feb 11, 2018 1:39 PM ET
Edited Feb 12, 2018 10:56 AM ET.

2.

Thanks, Jon. So does the same go for the indoor units?

Answered by rk2
Posted Feb 11, 2018 9:07 PM ET

3.

I don't know, but my guess is that the indoor units can modulate down, but how far varies with the model. Splitting between units sounds logical.

Over-sizing max capacity of an indoor unit (with the same rated minimum output) should increase sensible efficiency but may slightly reduce latent cooling efficiency.

Answered by Jon R
Posted Feb 11, 2018 11:27 PM ET
Edited Feb 12, 2018 1:35 PM ET.

4.

RK2,
As far as I know, the control algorithms used by manufacturers of minisplits are proprietary and often opaque. Dana Dorsett may provide a more detailed answer.

Briefly, oversizing is never good. If you've done a good load calculation, use that calculation when sizing your unit. Don't oversize.

Here are some links to further discussions of these issues:

Are Seven Heads Better Than Three?

Tweaking Plans for a Minisplit System

With a multi-zone mini-split, does the indoor unit or the outdoor unit decide when to turn on?

What is minisplit short cycling? Turndown?

Minisplit efficiency - multiple single zone vs single multi-zone

How does efficiency in a mini-split vary over various operating levels?

Answered by Martin Holladay
Posted Feb 12, 2018 7:23 AM ET

5.

As general rules:

Oversizing cassettes & heads is bad, oversizing the compressor is worse.

The coils in an oversized system are bigger, and potentially higher efficiency if running continuously at low speed. But oversized coils also have marginally higher refrigerant volumes and oversized blowers, adding the start-up ramp energy use, making it LESS efficient when cycling on/off, even at the same minimum-modulation levels as a more appropriately sized unit.

Answered by Dana Dorsett
Posted Feb 12, 2018 12:22 PM ET

6.

Larger coils have been an obvious trend in producing more efficient outdoor units - despite their higher volume.

See below for "Oversizing VC heat pumps substantially decreases cooling and heating season energy consumption and peak demand. "

https://aceee.org/files/proceedings/2014/data/papers/1-371.pdf

Answered by Jon R
Posted Feb 12, 2018 1:30 PM ET

7.

Thanks for the answers, gentlemen. From all the reading is that the biggest contributor is still the minimum capacity floor, and that otherwise it's in the balance between startup energy use when cycling and backup heat use on too-cold days. Could be interesting to model that, but it seems it might be relevant only to edge cases.

I just noticed that in the case of the Mitsubishi MXZ series, there may be a simpler answer: the 36, 42, and 48KBtu/h units have the same compressor and refrigerant charge. So with my heat loss calc over 3 tons, I might as well upsize and lower my need for backup stage heat. Does make me wonder what justifies the cost difference on the units.

Answered by rk2
Posted Feb 12, 2018 3:33 PM ET

8.

* My takeaway from all the reading, I meant to say.

Answered by rk2
Posted Feb 12, 2018 3:33 PM ET

9.

One other related question: I was looking at page 29 of http://meus1.mylinkdrive.com/files/MXZ-4C36-5C42-8C48NAHZ_PAC-MKA30-50BC... which describes the MXZ capacity diagrams.

Unless I'm reading the graphs wrong, the COP of the unit *drops* as it operates below max capacity. At full power, it has 4420W producing 54KBtu/h for a COP of 3.75. At lowest it runs 0.12 capacity ratio but 0.23 power ratio for a COP of somewhere around 2.

Does that seem right? Or am I misunderstanding the specs?

EDIT: something doesn't seem right, because the graph doesn't correspond with the operating currents listed on the operational performance charts like https://nonul.mylinkdrive.com/files/M-Series_MXZ_Operational_Performance... that do show increased COP at lower capacity.

So I'll chalk this up to me missing something.

MXZcapacity.JPG
Answered by rk2
Posted Feb 12, 2018 4:15 PM ET
Edited Feb 12, 2018 5:32 PM ET.

Other Questions in General questions

Difficulty Finding a Modulating Multi-Zone ASHP

In Mechanicals | Asked by Jonathan Lawrence CZ 4A New Jersey | May 21, 18

Spray foam questions

In General questions | Asked by Stanger133 | May 20, 18

Water Testing After Pex Repipe

In Green products and materials | Asked by JohnZ99 | May 16, 18

Water heater pad

In Energy efficiency and durability | Asked by Norman Bunn | May 17, 18

exterior sheathing and insulation

In Energy efficiency and durability | Asked by cdgatti | May 21, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!