Young, dumb and broke, we built the original part of our house (CZ6) on pressure treated piers over bare ground 35 years ago. The floor was insulated with R-19 fiberglass covered with OSB. A few years later we replaced the piers with a shallow concrete block perimeter wall. The exterior from footing to house sidewall was covered with an inch of poly iso protected by a layer of pressure treated plywood.

We covered the rough ground beneath the house with two layers of 6 mil plastic as best we could, but it is not sealed to the concrete block. Needless to say, the cold ground causes condensation on the plastic. We used to ventilate the crawlspace in summer, but now keep it sealed which seems dryer, but we still have condensation and a few black spots on the rather soft OSB.

I am looking for easy to implement solutions - there is only 18" to 3' headroom and lots of pipes and wires to work around. Could I add a layer of mineral wool on top of the plastic and add another layer of plastic sealed to the foundation wall? Mineral wool would be flexible enough to follow the contours (and cushion the rocks). Or am I better off removing the OSB and fiberglass and having the underside of the floors closed cell spray foamed? That doesn’t resolve the condensation, just adds a better barrier.

Are either of those a viable solution or do you have other suggestions?

Asked by Ron Rosen
Posted Jun 7, 2018 8:07 PM ET
Edited Jun 8, 2018 8:16 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Ron,
Start by reading this article: Building an Unvented Crawl Space.

There are several remedies you can take.

1. Check the grading at the perimeter of your house to make sure that the grade slopes away from the foundation on all four sides of the house.

2. Use a short shovel and a drywall bucket to lower the grade in the crawl space. The work isn't fun, but someone has to do it.

3. Insulate your crawl space walls.

4. Remove and dispose of the OSB on the crawl space ceiling, and the insulation between the floor joists.

As the article notes, you don't want to insulate your crawl space ceiling. You want to insulate your crawl space walls.

Answered by Martin Holladay
Posted Jun 8, 2018 5:52 AM ET
Edited Jun 8, 2018 5:59 AM ET.

Other Questions in General questions

Plumbing too close to edge of slab

In Project management | Asked by Hugh Stearns | Jun 18, 18

Do I need an HRV/ERV for a house built in 1947?

In Mechanicals | Asked by Will82 | Jun 14, 18

Building code requirements for stacked window headers, bracing, and stucco over foam

In Building Code Questions | Asked by Zane Bridgers | Jun 17, 18

Brick house insulation

In Green building techniques | Asked by Sebastian Smith | Dec 29, 17

HVAC duct size versus grille size

In Mechanicals | Asked by Richt1022 | Jun 18, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!