A few unvented crawl space questions

I am detailing an unvented 600 sq. ft. crawlspace that is 4' high. The exterior side of the concrete wall is insulated with 5" of EPS and has been damp-proofed.

My plan now is to insulate the floor with 3" EPS and cover with two layers of poly that will be mechanically fastened with horizontal battens and acoustic sealant to the side of the footing. to boost the R-value in the wall i will add 1.5" XPS and then build a stud wall to cover with gypsum wallboard.

My plan is to notch the XPS around the floor joists so that the xps comes into contact with the underside of the floor sheathing above. i would then do the same with the GWB. How does this detail sound?

Also, do i have the HRV supply/exhaust the crawl space? also, i put a section of 4" PVC pipe through the footing and tied it into the perforated footing drain. this perimeter drain eventually connects to solid pipe and drains to daylight. the idea was it would drain out any water trapped under the 'slab.' the plumber thinks i should close this off. should i?

thanks again, gba..

Asked by erik olofsson
Posted Jan 24, 2013 1:42 PM ET
Edited Jan 24, 2013 2:03 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Erik,
It sounds like your crawl space will have above-average details. In case you haven't seen it, there is an article on the topic here: Building an Unvented Crawl Space.

The question of whether or not you need some type of air exchange or ventilation in your crawl space is controversial. Code requirements call for a low-cfm exhaust fan in the crawl space rim joist or a forced-air register delivering hot air in the winter and cold air in the summer. Both options require the installation of a floor vent connecting the conditioned space upstairs with the crawl space below.

Some observers worry about contaminating the indoor air with radon and other undesirable gases present in the crawl space. If your local code allows, you might skip the fans for a year and monitor the humidity in the crawl space. If it's dry, you might be all set without the floor register and fans.

Answered by Martin Holladay
Posted Jan 24, 2013 2:00 PM ET

Other Questions in General questions

Anyone seen nail corrosion from Roxul?

In Green products and materials | Asked by Ryan Williamson | Jun 22, 17

Halogen-free electrical cable

In Green products and materials | Asked by Kathryn Oseen-Senda | Jun 23, 17

Rigid insulation beneath floor on shed

In Green building techniques | Asked by Allan Manley | Jun 22, 17

Closed-cell spray foam and XPS: green or not?

In Green products and materials | Asked by Brian Gray | May 7, 17

Dense-pack retrofit cellulose insulation for basement walls?

In Energy efficiency and durability | Asked by Phil Ray | Jun 22, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!