Where should vapour barrier be in double basement wall?

Walkout basement in zone 4C (west coast) 2x6 framed exterior wall with r20 fiberglass batt insulation. To eliminate the 'step' (many houses have a finished shelf) of concrete foundation which comes up 2', client wants walls framed from floor to underside joist inside foundation to avoid the shelf, creating a space between the framed exterior wall and the new interior wall. Should the vapour barrier (6 mil plastic be relocated to inside of newly framed wall, and if so, should new wall be insulated? the full cavity be insulated? thanks, dan

Asked by dan nugent
Posted Mon, 04/21/2014 - 09:54

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Dan,
In Climate Zone 4, you definitely don't want to use an interior vapor barrier like 6-mil poly in your wall assembly. Fortunately, the building code does not require a vapor barrier in your wall. If you live in Canada, you may occasionally encounter a building inspector who wants to see an interior membrane of some kind. If you have a building inspector like that, you can install a "smart" vapor retarder like MemBrain.

For more information on this issue, see Do I Need a Vapor Retarder?

Answered by Martin Holladay, GBA Advisor
Posted Mon, 04/21/2014 - 10:10

Other Questions in General questions

In Energy efficiency and durability | Asked by david chinn | Jul 27, 14
In Energy efficiency and durability | Asked by Jeff Lever | Jul 29, 14
In Green building techniques | Asked by Keith Richtman | Jul 29, 14
In Plans Review | Asked by Joshua Wyatt | Jul 28, 14
In Mechanicals | Asked by Shawn Shumaker | Jul 28, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!