SIPs Roof Replacement

I have an energy makeover project for a client with an older log home. Beyond the usual infiltration issues we need to repair/upgrade the roof.

Current: asphalt shingle, tar paper, OSB in fair shape -- some rot and rodent damage, but not past fixing.

One plan is to strip back to OSB, repair as needed, add tar paper, 4" SIP Nail board, More tar and paper and a standing-seam metal roof ready for PV.

Thoughts? Ideas? Criticisms?

Thanks
b

Asked by Bruce Glanville
Posted Wed, 01/04/2012 - 18:11
Edited Wed, 01/04/2012 - 19:03

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 1

Bruce,
Most 4-inch-thick SIPs have an R-value of R-15 or less. That's not much. What is the R-value of the existing roof assembly?

What's the climate?

For installation over an existing roof, you don't need SIPs. You can use nailbase, which has OSB on one side instead of two.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 01/04/2012 - 18:26

2.
Helpful? 0

Existing R value is 19. Nail base SIPS was the intention already. I am concerned mostly with moisture as we are in Mixed-Humid East Tennessee, climate Zone 4. My SIPS supplier says the paper at the old roof, new nail-base SIPS joint is to eliminate moisture collection at that juncture. They use a liberal application of DEGA Seal at the joints and a Tar based seal in the nail-base OSB joint under the final layer of tar paper.

Answered by Bruce Glanville
Posted Wed, 01/04/2012 - 19:10

3.
Helpful? 0

Bruce,
If the existing roof is insulated with fiberglass batts, my guess is that the roof assembly is performing at significantly less than R-19. That means that your final improved roof will have a total R-value no more than R-34 -- and probably more like R-25 or R-30.

What I'm saying is, more foam is better.

Answered by Martin Holladay, GBA Advisor
Posted Thu, 01/05/2012 - 09:21

Other Questions in Green building techniques

In Building Code Questions | Asked by michael maines | May 23, 12
In Energy efficiency and durability | Asked by Victor Burgos | May 23, 12
In Energy efficiency and durability | Asked by David Slade | May 21, 12
In General questions | Asked by Robert Hronek | May 23, 12
In General questions | Asked by Holger Herrmann | May 23, 12
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!