Helpful? 0

Over slab polystyrene foam board insulation and clay tiles

We are using polystyrene board insulation for an over slab application. Is 25 psi polystyrene foam board insulation adequate to support one layer 1/2 inch osb board, one layer of cement backer board topped with ceramic tile?

Asked by Tim Hatcher
Posted Thu, 03/14/2013 - 15:47

Tags:

5 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Tim,
Yes. More information here: Foam Under Footings.

Answered by Martin Holladay, GBA Advisor
Posted Fri, 03/15/2013 - 07:24

2.
Helpful? 0

Thanks Martin. This article addresses under slab insulation. I'm wondering about over slab EPS boards and the integrity of clay or ceramic tiles on top of 25 psi EPS.

Answered by Tim Hatcher
Posted Fri, 03/15/2013 - 17:32

3.
Helpful? 0

The rigidity of half-inch OSB on top of 25psi foam in full contact with a slab below is at least comparable to and probably BETTER than the flex of standard thickness OSB sub-flooring suspended on 16" o.c. joists. If the tile backer is rated for a standard subfloor, it's going to be good here, if...

It's important to stagger the seams of the foam & OSB, as well as the seams of the backer-board & OSB, since those will be the flex points with the highest pressure & deflection. If you had the seams all alighned directly over one another you would have maximal shear forces at the weakest point in the foam layer, and it could develp rockering compression and cracking over time. If the seams of the OSB are a foot away from those of the foam, and the seams of the backer at least 6" away from those of the OSB it will have very little "give" to it.

Answered by Dana Dorsett
Posted Fri, 03/15/2013 - 17:44

4.
Helpful? 0

Tim,

How do you plan to attach the foam, OSB, and cement backer board?

Answered by Ron Keagle
Posted Sat, 03/16/2013 - 12:40

5.
Helpful? 0

Tim,

Here is a Cork alternative. This standard grade cork is R4/inch, takes a lot of load and has been used successfully as "over slab insulation" for years. It allows a lot of latitude of what you put on top of it.

We've been developing a new informational website. it's not fully developed yet, but some technical specs are up: compression resistance, thicknesses, thermal conductivity, etc. www.thermacork.com

Cork heated floor.jpg
Answered by albert rooks
Posted Sun, 03/17/2013 - 23:02
Edited Sun, 03/17/2013 - 23:03.

Other Questions in Green building techniques

In General questions | Asked by erik olofsson | May 22, 13
In Energy efficiency and durability | Asked by lisa lockwood | May 20, 13
In General questions | Asked by Eric Mikkelsen | May 21, 13
In Green products and materials | Asked by JOSEPH POLAND | May 19, 13
In Energy efficiency and durability | Asked by Sal Lombardo | May 20, 13
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!