When adding foam insulation to a roof assembly, is there any reason to bring it significantly past the exterior building line?

The assembly I am asking about is:
I joist rafters filled with dense pack cellulose/sheathing/4" polyiso/sheathing/waterproofing/metal roofing.
Is it ok to stop the foam layer at the building/insulation line to save material on the gable and eave overhangs?
Thanks

Asked by stefan straka
Posted Sat, 05/17/2014 - 17:22

Tags:

6 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Wouldn't that depend on how you intend to tie all that to the
wall assembly? The insulation layer should be as contiguous
as you can manage, I would assume. The typical roof/wall junction
is a squeeze area subject to a lot of thermal bridging, probably
not an area to skimp on.

You might want to delete your duplicate post [if that's
possible..] so answers accumulate in one place.

_H*

Answered by Hobbit _
Posted Sat, 05/17/2014 - 17:36

2.
Helpful? 0

Hobbit,
There shouldn't be much thermal bridging-the dense pack will cover the top plate and so at the exterior wall the insulation line would be a nearly continuos stack: wall insulation(cavity fill and exterior foam) then dense pack over the plate then foam over the first layer of roof sheathing.

You are getting at the heart of my question though. Is there any benefit (to mitigating thermal bridging or possible areas of condensation) to having insulation outside the building line that is not insulating the conditioned space directly

I'll try to delete the duplicate post, thanks.

Answered by stefan straka
Posted Sat, 05/17/2014 - 18:57
Edited Sat, 05/17/2014 - 19:17.

3.
Helpful? 0

Stefan,
In some climates, solar radiation on the south side of the building can heat the south-facing siding, and cause a pocket of warm air to form under the soffit on sunny days. This pocket of warm air can encourage snow on the roof to melt at the eaves, leading to ice damming. If you continue your rigid foam all the way to the eaves, the added insulation can reduce ice damming under these circumstances.

Of course, if you live in a climate where ice damming isn't an issue, this concern doesn't apply.

If you omit the rigid foam at the eaves and rakes, you still have to install shims to support the top layer of sheathing and roofing. It's usually simpler to just extend the rigid foam to the edges of the roof.

Answered by Martin Holladay, GBA Advisor
Posted Sun, 05/18/2014 - 06:43
Edited Sun, 05/18/2014 - 06:45.

4.
Helpful? 0

Thanks Martin.
I live in a Zone 4 climate north of Seattle, with little/no snow accumulation. The gable and eave overhangs are a bit more than 3', equaling about 35 extra sheets of foam at 2 layers. Financially/material use wise it makes sense for me to leave these out. So other than the ice dam concern, are there any other reasons to insulate this area?

Answered by stefan straka
Posted Sun, 05/18/2014 - 07:35

5.
Helpful? 0

Stefan,
Q. "So other than the ice dam concern, are there any other reasons to insulate this area?"

A. No.

Answered by Martin Holladay, GBA Advisor
Posted Sun, 05/18/2014 - 10:00

6.
Helpful? 0

Thanks for your help.

Answered by stefan straka
Posted Sun, 05/18/2014 - 10:31

Other Questions in Green building techniques

Half insulating stone basement

In Energy efficiency and durability | Asked by Geoffrey Cook | Oct 31, 14

Minimum R-values for exterior foam for 2x6 walls

In Energy efficiency and durability | Asked by Craig Steinman | Oct 30, 14

How to seal 4" EPS foam at slab edge (radon concerns)?

In GBA Pro help | Asked by e c | Oct 29, 14

Pipe leak in basement

In General questions | Asked by Andrew Sirianni | Oct 31, 14

Foam insulation question for 100-year-old brick home

In Green building techniques | Asked by Wes Leland | Oct 30, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!